Surge Arrester for HV Cable Protection

02/05/2015 4:01 AM

What would be the maximum length of HV cable that can be used without surge arrester protection in the panel.?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Surge Arrester for HV Cable Protection

02/05/2015 5:40 AM

It may well depend upon the style and construction of the cable, the method of installation, the voltage applied to it and the relevant national electrical standards, none of which can be seen from here.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Sep 2009
Location: INDIA
Posts: 92
#2
In reply to #1

Re: Surge Arrester for HV Cable Protection

02/06/2015 2:43 AM

If it is directly buried 3.3kV cables.

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#3

Re: Surge Arrester for HV Cable Protection

02/07/2015 4:42 AM

In my opinion, if the cable is entirely buried then no lightning interference would be expected. Against breaker switching transient as the maximum voltage expected is 6*3.3*SQRT(2)=28 kV, I think the cable insulation could withstand this.

According IEC 60502-2 18.2.4 Impulse test- the sample test has to withstand 60 kV.

If the cable terminations are located on a steel pole I think you need an arrester at entrance and no arrester on the exit end. If the pole is a wooden pole I think at the maximum distance of 10 m you will need another arrester.

__________________
Julius
Register to Reply
Commentator

Join Date: Sep 2009
Location: INDIA
Posts: 92
#4
In reply to #3

Re: Surge Arrester for HV Cable Protection

02/10/2015 1:09 AM

I have a length of 10km

Register to Reply