we found in one of our project NC proximity limit switch used for ESD valves open /close indication . When tagret come against the respective sensor voltage increases 4 to 7 volt as well as the digital contact become 1- 0 respectivley . so fail safe action could not be achived if sensor wire break condition . To achive fail safe aspect vendor used opposite switch i mean OPEN switch used for close indication when valve closed . same for reverse also . So physcially when valve is open the valve cam against the close sensor . in this case . valve not closed 100% dcs shows close indication . I just want to discus about this . we are having dip switch adjustment provision in barrier and its dual barrier .

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#1

Re: Normally Closed Proximity Switch

02/06/2015 8:21 AM

Looks like you've totally analyzed this situation. There is a question here somewhere????

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply Score 1 for Good Answer
Associate

Join Date: Nov 2010
Posts: 30
#3
In reply to #1

Re: Normally Closed Proximity Switch

02/06/2015 2:08 PM

Its adjusted max to the desired level of closing and opening , When valve is open we have taken close limit switch for open indication . As we know our standard method is when vale open ZLH become 1 and ZLL is 0 ( NO switch ). here we have NC switch so close switch become 1 to 0 and open switch ll become 0 to 1 . this case we are considering two switche status . Our issue is during vale open as i said ZLL is 0 and ZLH is 1 . Momently valve is physcially closed but ZLL wire is broken as it is already 0 and ZLH also become 0 usually mismatch alarm will be generated If close status is used for activating a Emergency depressureization system nothing is going to happen . I need a solution for this with using same switch .

Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#5
In reply to #3

Re: Normally Closed Proximity Switch

02/06/2015 11:43 PM

Trying to get my head around your explanation and requirements, but if it is simply that you need the open condition to output a 0 instead of a 1, then consider using a NOT gate to invert that signal. Any competent electronics tech could build you one quite easily if they know the circuit parameters.

Register to Reply Score 1 for Good Answer
Associate

Join Date: Nov 2010
Posts: 30
#6
In reply to #5

Re: Normally Closed Proximity Switch

02/07/2015 1:07 AM
Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#2

Re: Normally Closed Proximity Switch

02/06/2015 9:22 AM

Can you adjust the switch to only react to "100% closing"?

__________________
CRTL-Z
Register to Reply
Power-User
Hobbies - Musician - New Member

Join Date: Dec 2014
Posts: 418
Good Answers: 3
#4

Re: Normally Closed Proximity Switch

02/06/2015 9:56 PM

Consider inter phasing with some signal conditioners. It's just a logic (not, yes) conversion

__________________
"When I thought I exceeded to be wise but wisdom was far from me" -King Solomon
Register to Reply
Guru

Join Date: Dec 2010
Location: North West England
Posts: 1170
Good Answers: 153
#7

Re: Normally Closed Proximity Switch

02/07/2015 6:54 AM

Attempting fail safe operation with a single NC switch at each end is doomed to failure. Replace switches at both ends with change over contacts. Use the NO at each end for position indication. Wire both NCs in series and create an "intermediate" signal. Provide indicators for all three signals so the plant operator and maintenance can see what is happening. Feed all three signals into an Exclusive OR circuit so if you get no signal (broken wire) or two at once (shorted wire) you know you are in fault mode. You will need to add a pulse delay to cater for the brief interruption during switch changeover. Add a timer to the intermediate signal set to just longer than the time needed for the valve to change status. If the timer trips the valve has stopped/slowed due to an obstruction in the half way position which should trigger a separate fault mode. Set back the limits from the extreme at each end so they trip early, then add delays so the actuator continues to drive the valve onto it's seat. Setting a limit right on the cusp risks the possibility of not tripping and causing a false positive alarm condition. Alarm signals should be latched and only reset after a competent person has ascertained the reason for the fault and resolved the problem. Alarms should be divided into categories of warning, serious and critical. Warning can in most circumstances allow the plant to continue running and leaves decisions about shut down to a trained operator.. Serious should shut down the plant in a controlled manner. Critical should generate an Emergency Stop shutdown. Data logging of all alarms is a good idea. In complex plants one fault can cause other parts of the system to behave erratically. Being able to check which fault was logged first saves a lot of time when diagnosing problems.

Register to Reply Score 1 for Good Answer
Associate

Join Date: Nov 2010
Posts: 30
#8
In reply to #7

Re: Normally Closed Proximity Switch

02/07/2015 12:00 PM

Please to be noted that its not a mechanical micro limit switch . It is normally closed proximity switch . Here i have attached the present logic and proposed logic to be implemented .

Register to Reply
Guru

Join Date: Dec 2010
Location: North West England
Posts: 1170
Good Answers: 153
#9
In reply to #8

Re: Normally Closed Proximity Switch

02/07/2015 1:30 PM

Proximity switches can and do fail high as well as fail low. If cables are damaged a short circuit is just as likely as an open circuit. When the valve is in transit from open to closed or closed to open you are not even looking for a failure, but this is the commonest time for a failure to occur. Fail safe operation implies guarding against all possible failure modes, not just the ones you choose. I never suggested that the limits should not be proximity switches, just that the proximity switches that you currently have installed are inadequate.

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#10

Re: Normally Closed Proximity Switch

02/09/2015 2:49 PM

Stick a travel timer on the valve. If it hasn't changed state by [time] after asking it to move, then you've got a failure, so alarm.

__________________
Good moaning!
Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#11

Re: Normally Closed Proximity Switch

02/13/2015 11:50 AM

Actually it sounds like all you need is a pull up resistor that is held to ground when you want the value to be zero. When it is 1, the pull up resistor is redundant and does not do anything.

By putting a pull up resistor on the output side of the circuit, it provides a signal when there should be none due to a broken cable. Make sense?

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Register to Reply 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Crabtree (1); jhhassociates (2); Kulas (1); NotUrOrdinaryJoe (1); Orson (3); Phys (1); spades (1); Unredundant (1)

Previous in Forum: Valve Character   Next in Forum: Galvanic Isolation For Transmitters

Advertisement