Anonymous Poster #1

Busbar Tap Off

03/17/2015 4:27 PM

Is it possible to have additional busbar tap off(90 kW load) to an existing 1000A 4P + Integral Earth Bus Bar with 1000A breaker having a connected load of 500 kW? Hoping to receive your answers immediately

Thank You and more power

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Busbar tap off

03/17/2015 4:43 PM

Depends on your voltage, the loads and how they operate effecting instantaneous current draw through the breaker and busbars. Doesn't look promising.

__________________
jack of all trades
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Busbar tap off

03/17/2015 5:38 PM

No!

Much more information is needed.

UL rating considerations, not to mention numerous code requirements.

I'd never suggest anything else to an anonymous poster!

No!

Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#3

Re: Busbar tap off

03/17/2015 5:54 PM

Only by receiving more information immediately, Bwana.

Why don't you ring the original panel builder immediately and find out immediately?

__________________
Good moaning!
Reply Score 1 for Good Answer
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#4

Re: Busbar tap off

03/17/2015 6:00 PM

Yes it is possible. It might not be advisable. It might violate your local codes. It might damage your equipment or kill someone, but with so little information, we don't have a snowballocks chance in ellhay of knowing.

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#5

Re: Busbar Tap Off

03/17/2015 6:52 PM

You need to supply muuuuuuch more information, preferably immediately as we may very well be holding up your site commissioning with our vague guesses to the limited information available. Currently the answer is NO, but could potentially be upgraded to possibly (with many conditions) if more information is supplied.

We're assuming you have checked your existing breaker curve(s) against your new load profile.

More information please.

__________________
jack of all trades
Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#6

Re: Busbar Tap Off

03/17/2015 7:06 PM

Possible? Yes

Good idea? Maybe not.

Adding any bus to an existing bus requires absolute knowledge of the bus loading, the amount of de-rating to the bus that can be applied based on the type(s) of load(s), if the bus was/is designed to accept an expansion bus, and whether the Original Equipment Manufacturer will approve of the expansion.

You must do a detailed power study on the switchgear/equipment before even considering the expansion.

If you are unsure of how to perform the study, it is imperative you find someone that is competent to perform the study either in-house or from outside your company.

Once the power study is complete you will have a much better understanding of what is possible then you need to contact the OEM and follow all of their recommendations to the letter.

Failure to follow all of the required/recommended steps will result in bus damage, equipment damage, and/or injury or death to personnel in the immediate vicinity.

Be safe and good luck.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Reply Score 1 for Good Answer
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#7
In reply to #6

Re: Busbar Tap Off

03/17/2015 7:17 PM

Thanks, I now have visions of the guy asking if it's ok to drill and tap his fully insulated bus bar system to create the tap off.

__________________
jack of all trades
Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#17
In reply to #7

Re: Busbar Tap Off

03/18/2015 9:18 AM

You're welcome!

It really does not matter if the bus is fully insulated or not as long as the correct procedures are followed in accordance with all OEM recommendations and all of the required bus parts including insulation are purchased/fabricated.

Nothing new here as this procedure is common throughout industry especially during site electrical upgrades and process improvement projects.

I have executed this procedure many times on insulated and non-insulated MCC and MV Switchgear bus with either an on-site OEM representative in control or by my supervising in-house technicians with the written guidance of the OEM.

However; I would never attempt doing it with without gathering all of the required DATA, purchasing the correct required parts, and obtaining written OEM permission with a detailed instruction set.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#8

Re: Busbar Tap Off

03/17/2015 8:04 PM

My favorite tap off.

Reply Score 1 for Good Answer
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#9

Re: Busbar Tap Off

03/17/2015 8:56 PM

The immediate answer is: No!

__________________
Common Sense Dictates
Reply
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#10

Re: Busbar Tap Off

03/17/2015 11:10 PM

Not very likely with your skill set.

Do you also anonymously post on WebMD about where to make the incision to perform an appendectomy?

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Good Answer (Score 2)
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#19
In reply to #10

Re: Busbar Tap Off

03/18/2015 9:23 AM

If he did, looks like he's got a Darwin Award coming, hope the awards committe has his address, or rather the address of his next-of-kin.

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#11

Re: Busbar Tap Off

03/17/2015 11:47 PM

Dollars to donuts, it's 415 volts, but it would be better to have it actually stated.

What is the largest motor to be started, and what loads are concurrent at the time?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#12

Re: Busbar Tap Off

03/18/2015 12:36 AM

Depends on voltage,for one factor.

13,200 volts 3 phase at 1000 amps can be divided many ways by adding a switch

and appropriate breakers.

I have seen 13200 dividied across up to 20 switches,each feeding a department in a large manufacturing plant.

The next step down from there is usually 7200volts,then 4160,volts,then either 600v,480v,etc.

You phrasing of the question indicates that you have a very limited knowledge of

electrical systems.

For the safety and welfare of all concerned,please refer this job to a qualified and

experienced engineer of contractor.

IMMEDIATELY!

Your company and next of kin will have a lot less grief if you do.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#13

Re: Busbar Tap Off

03/18/2015 1:34 AM

contact manufacturer

__________________
pnaban
Reply
Participant

Join Date: Mar 2015
Posts: 1
#14

Re: Busbar Tap Off

03/18/2015 2:25 AM

This could be possible if its possible to size for the diversified load after applying diversity factor. local regulations should mention something about this.

Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#15

Re: Busbar Tap Off

03/18/2015 3:02 AM

Where the load is located,near bottom,top or middle of the run. If near bottom, if you can't connect tap off, connect the load to MSB. If near top, fix an adaptor & CB at top.In between if there a tapoff with extra capacity connect to it. You should give details of all tap-offs,locations & new one for a good answer.

__________________
pnaban
Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#16

Re: Busbar Tap Off

03/18/2015 5:11 AM

Anything is possible. Whether or not it is both wise and safe is quite another matter, however, that feature does not appear in the question.

The application is all. In order to determine the correct way forward, a good option is to hire a qualified Electrical Engineer locally to carry out the detailed design requirements. That way, instead of using an anonymous forum and having no come-back when something goes wrong, at lease there is some measure of warranty and accountability.

Good luck with the project.

<unsubscribes>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#18

Re: Busbar Tap Off

03/18/2015 9:21 AM

[ begin Rod Serling Voice ]

You are traveling through another dimension, a dimension not only of Snark and Satire, but of Sarcasm. A journey to a wondrous land who boundaries are that of Contempt. Your next stop, the Anonymous Question Zone.

[ end Rod Serling Voice ]

Seriously, why do we get people like this showing up? I understand they're in WAY over their head, and they don't want their boss to realize their lack of skills and knowledge, but these short posts, with the core question only, none of the ancillary information that would allow for an intelligent answer, only make me afraid of the countries that would allow such people to stay in these positions.

By advice to AP#1 is as follows:

You are playing with things beyond your comprehension. If you make a mistake, people, possibly many people, will DIE! Resign from the project and find a job better suited to your real skills. You will save lives by leaving that project and letting the company hire someone who understands the dangers involved.

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Reply Score 1 for Good Answer
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#20

Re: Busbar Tap Off

03/18/2015 10:19 AM

The general answer to your question is "YES", bus bars can be tapped. We often use high temperature silver solder and brazing flux. However, the devil is in the details which you have not provided.

Reply
Reply to Forum Thread 20 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

a.amer (1); adreasler (2); Brave Sir Robin (1); Crabtree (1); HiTekRedNek (1); IdeaSmith (1); jack of all trades (3); lyn (2); pnaban (2); PWSlack (1); redfred (1); SHOCKHISCAN (2); Tornado (1); welderman (1)

Previous in Forum: Grading Capacitor   Next in Forum: ACS 800 Tripping Without Any Indication

Advertisement