Again Cos Fi

03/18/2015 2:29 PM

Why el. power suppliers demand from consumers to keep cos fi at the rather low level - 0.96 ? Why not, let say - 0.99 ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: again cos fi

03/18/2015 2:44 PM

Because it isn't worth the effort for the additional 0.03.

__________________
Good moaning!
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: again cos fi

03/18/2015 2:55 PM

To expensive to do so with too little gain achieved.

This is one of those times when the Engineers and Accountants are in agreement.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: again cos fi

03/18/2015 3:55 PM

Economics....

..."The demand charge is more complicated. It's typically based on the peak kW demand over a given 15-min, 30-min, or 60-min interval during the month, which is nominally multiplied by the demand charge rate ($/kW).

Penalties for low PF - typically anything less than .95 - have become increasingly common. Most utilities use one of the following two common formulas for determining the billed demand when PF is lower than 0.95 lagging:

KWBilled = kWActual x (0.95/PF)

or

KWBilled = kWActual x (1 + 0.95 - PF)

Both of these formulas are applied only when PF is less than .95 lagging. Otherwise, the billed demand is the same as the actual demand.

The difference between the amount paid for the billed demand and the amount that would be paid for the actual demand is often termed the PF penalty. This quantity, calculated using the following formula, is generally responsible for the bulk of the justification for PF correction:"....

..." Most of the economic justification for PF correction will come from eliminating penalty fees on your utility bills. Reducing energy losses can contribute to the justification, but contrary to manufacturer claims, it's generally insufficient by itself to justify the cost of installing correction. Some manufacturers boast their products can yield energy savings as high as 10%, but it's typically only possible to reduce average kW demand by .5% to 1.5%. "...

http://ecmweb.com/content/inside-pq-0

http://www.michaelsenergy.com/industrial-energy-briefs-2/miscellaneous/power-factor-correction/

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#8
In reply to #3

Re: again cos fi

03/20/2015 5:39 AM

PF correction yields $avings even if there are no penalties if you operate your own generators. Fuel savings.....

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: again cos fi

03/18/2015 4:19 PM

The concept is called the "Law of Diminishing Returns". It just means that to go from .8 PF to .95 PF is relatively inexpensive for the gains made in the big picture of things. But going from .95 to .99 becomes exponentially more expensive and the benefits of doing so are exponentially fewer at the same time.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#7
In reply to #4

Re: again cos fi

03/19/2015 1:44 PM

Why "expensive" - capacitive load losses are not large indeed, aint they ?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: Again Cos Fi

03/18/2015 10:27 PM

Moreover, if you go "overboard" into a leading PF, some instabilities can occur.

BTW, the Greek letter is "phi", not "fi".

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#6
In reply to #5

Re: Again Cos Fi

03/19/2015 1:29 PM

"Phi" is not 1 but 3 latin letters, neither Greek.

To be above 0.96 is also not allowed. Now it is 0.98, the target being 0.96. If I drive it with capacitors to 1 and then to the leading 0.96 what instabilities can occur ?

Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#9

Re: Again Cos Fi

03/25/2015 9:51 AM

The suppliers put that out there is the minimum power factor for complex (combined resistive and reactive loading at an industrial facility), not the maximum. If a facility has enough capacitor banks to shift their local power factor back up to 0.99, then I am not sure the power supplier would mind at all. The power companies like to provide MW, not so much MVARS. MW are easier to transmit at lower loss factor (I suppose) than are MVARS at a low power factor. Usually the Pf limitation may only apply during peak demand time when HVAC loads are highest on the grid. I am sure the power suppliers have less problem with reactive loads being higher at times when the grid is off peak demand (typically at night).

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Crabtree (1); jack of all trades (1); James Stewart (1); JRaef (1); SolarEagle (1); Tornado (1); Wal (1); Yuri B. (2)

Previous in Forum: AC/AC Converter For Naval Application   Next in Forum: Time Delay Relays

Advertisement