Grounding!

03/29/2015 8:02 AM

Dear All,

I've recently watched one of Mike Holt's videos regarding grounding and it surprised me. I was a nice video, though. I had in mind that the current always goes to the ground which I believe now is incorrect. It goes to the source. Then what about the lightning striking the earth?

I don't see why an electrode would be necessary for a generator? Only a cable from genset to panel board would suffice to trip the C.B in case of a fault?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#1

Re: Grounding!

03/29/2015 9:50 AM

No circuit breaker I know of can handle a direct lightning strike. A direct strike can easily produce millions of amperes of current from the millions of volts of potential between cloud and ground. The only thing good about a direct lightning strike is that it is not hard to find what has been damaged. An indirect lightning strike is another thing. Most of the time the induced currents generated by the EMP (Electro Magnetic Pulse) of lightning are small and relatively brief enough that no damage occurs at all. It also helps that the magnitude of the pulse field linearly decreases with the square of the distance from the direct strike. For locations that it is likely for lightning to strike a structure a separate earthing contact from the power distribution is usually required.

The grounding electrode at a generator is needed for the exact same reason as the secondary of the downstream transformer should have a grounded electrode. I circuit breaker attached to a source can only detect a ground fault downstream if the source is grounded. This gets far more complicated with long distance, multiple power source and load conditions of the power grid even though the general principles are the same.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 3)
Associate

Join Date: Jan 2015
Posts: 46
#2
In reply to #1

Re: Grounding!

03/29/2015 9:59 AM

Thanks for your response. I have two questions which I hope you will answer:

i. If current always tries to go back to the source, where does the current from lightning go?

ii. I really don't get why do we even use grounding electrode (leave lightning for the sake of argument ). I mean, we can use bare copper from the secondary of the transformer to the panel without bothering for the electrode. The fault current will travel from the fault back to the Panel via this copper conductor and trip the breaker. Please explain.

Really appreciate your help.

Register to Reply
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#3
In reply to #2

Re: Grounding!

03/29/2015 11:20 AM

i: The other half of the closed path loop of current path is the much larger path of the distributed capacitor of cloud to ground that the arc is not travelling.

ii: It depends on the wiring convention of your local wiring codes. The NFPA codes for most of the US require power distribution to be earthed and for permanent conductive building structure (metallic plumbing and structural steel) to be separately earthed from power distribution. The NFPA codes recognize that some installations require isolated returns or phases instead of neutral wires. By convention, the definition of a neutral conductor requires a connection to earth. This earth connection wire must only carry fault currents when they happen. A return wire need not be connected to earth.

My point here is that there is no Physics reason for turning return wires into neutral wires by connecting them to earth. However, when electrical wiring fails the installed infrastructure needs a wiring convention followed to attempt the safe mitigation of a fault. These codes came about by methodical studies of disasters where property and lives have been lost. From time to time these codes are reviewed in a tedious process.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 2)
Associate

Join Date: Jan 2015
Posts: 46
#7
In reply to #3

Re: Grounding!

03/30/2015 1:37 AM

Thank you very much! You've been most helpful!

Register to Reply
2
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#6
In reply to #2

Re: Grounding!

03/29/2015 10:46 PM

Query #1 has been pretty well answered, so I will dwell on #2.

The conductor (call it B) that you refer to as going from the panel (frame of panel I guess you mean) to the transformer would indeed provide protection against live conductor faults to the panel frame or to any other exposed metal that is connected to B, but consider other possibilities where the live conductor comes into contact with structural metal (or any other metal) that is not connected to B. All of that metal is now at live potential (it could be the entire building) and no protective equipment will trip.

If someone concurrently touches that metal and the frame of the switchboard or other B connected devices they will complete the fault circuit and receive a possibly fatal shock. An installed RCD could operate to reduce the shock severity. Connecting that B conductor to common ground by means of a stake will reduce the possibility of unearthed structure and provide a return path for the fault current, and protective devices will operate more reliably and without waiting for someone's body to complete the fault path.

Now consider another possibility:- Resident #1 and #2 live next door to each other or even in the next street or suburb.

Conductor B to resident #1's property is open circuit, he doesn't have an installed RCD, he has a kettle the outer frame of which is live, so, while every item of resident #1's equipment is connected to his internal B conductor, they are not connected to the main B and so their exposed metal frames are effectively at full line potential. His protective devices do not operate to isolate the circuits, and he is unaware of any faults and indeed suffers no ill effects, everything works as it should. The kettle is sitting on the sink which now comes to line potential.

Resident #2 next door (who does have an installed RCD) is about to boil her kettle and as she holds the kettle and grabs the tap handle, the fault current from next door travels through the copper pipes to her tap and through her body to her kettle which IS effectively connected to B. She receives a potentially fatal shock. Her RCD registers no imbalance and does not open to protect her.

The earth stake would have prevented this from occurring by providing an earth reference for resident #1's fault current. Even if his individual earth connection was invalid, the fault current would have been shunted to earth via the copper pipes, operating his protective devices and thus causing no shock to #2

There are numerous other valid reasons for connecting one live conductor to earth but that should be enough to illustrate some safety factors involved.

Register to Reply Good Answer (Score 2)
Associate

Join Date: Jan 2015
Posts: 46
#8
In reply to #6

Re: Grounding!

03/30/2015 1:39 AM

Thanks for the detailed explanation.

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#12
In reply to #2

Re: Grounding!

03/30/2015 9:27 AM

The reason for the electrode is two-fold;

1. Provide an alternate ground return path through the earth should the transmission conductor be damaged or severed.

2. To limit and/or eliminate exposure to differences in potential between equipment, power lines and cables, and the structure and/or earth.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru

Join Date: Apr 2011
Posts: 8006
Good Answers: 286
#5
In reply to #1

Re: Grounding!

03/29/2015 9:11 PM

Good comment Redfred. The numbers for current and potential are a little off though. Current was overstated and potential was understated....so that kind of evens out.

Peak current of the average cloud to ground lightning strike is around 30 kiloamps. 99% are below something like 200 kiloamps.

Potential, cloud to ground immediately prior to a strike is typically around 100 mega volts or greater.

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#4

Re: Grounding!

03/29/2015 5:55 PM

The purpose of an earth/ground conductor in a distribution system is to operate the circuit protective device and disconnect the fault so as to avoid fire and electrocution.

Lightning is not a distribution. It is a weather feature. The purpose of the earth/ground conductor is to operate a preferred discharge path, thereby protecting adjacent structures against strike, thereby avoiding fire and electrocution.

At least, that's what it should say in your textbook.

__________________
Good moaning!
Register to Reply
Associate

Join Date: Jan 2015
Posts: 46
#9
In reply to #4

Re: Grounding!

03/30/2015 1:42 AM

haha... when I see a comment from Crabtree, I am sure there would be a sensible answer but with pun. I really don't mind it because you do try to help! Thanks!

Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#10

Re: Grounding!

03/30/2015 2:03 AM

neutral-ground bonding establishes a reference (zero) level for the phase current, for ex., when we say 120v we mean 120v to ground as a reference. without neutral-ground bonding, the neutral floats. lightning can damage sensitive electronics because it raises the ground reference voltage level.

__________________
BSEE but always learning
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#11

Re: Grounding!

03/30/2015 4:25 AM

If you are really interested in lightning strikes and the distribution network, there are a lot of surprises for most people here:-

why-does-lightning-strike-from-the-ground-up?

To prevent lightning entering the normal distribution system, you first need to shield your distribution system as well as you can,

Which is why on overland supply cables, the upper cable(s) are usually the grounding connections, they tend to "intercept" the strikes before the phases are struck. Not always but mostly...

They are also usually connected at each mast to a ground pit or similar......to prevent the high voltage/current needing to travel long distances before an earth connection is "met".

Just how often masts are earthed does depend on local code and how often strikes are measured in that region....someone else here can possibly give far better detail about this than I can.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2007
Posts: 719
Good Answers: 25
#13

Re: Grounding!

03/30/2015 6:11 PM

Strange you should refer to the neighbour Spades, this happened to us.

The family complained of shocks from the sink and taps!! I thought unbelievable.

Not only was all our electrics well earthed, but also the copper pipes and water.

A meter showed it correct 115v to earth from the sink/ taps/ all pipework in the house.
(half the 230v normal UK supply)

This was from the neighbour's connection (about 200 yard away) He denied it.
However the utility company also had to accept it when they did a voltmeter test.

They cleared it at the neighbour's house, and I installed 6mm cable and earth spikes to everything.

jt.

Fact of Life - after every Monday and Tuesday, even the calendar says W T F

Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

1capybara (1); Andy Germany (1); Crabtree (1); jt (1); magnetic_flux (4); redfred (2); SHOCKHISCAN (1); spades (1); truth is not a compromise (1)

Previous in Forum: Geared Motor Overload Setting   Next in Forum: Important Exercise

Advertisement