VFD Damage

04/30/2015 11:59 AM

VFDs on a 480 Volt system, where matrix passive filters have been applied, are being damaged when power is re-established after very short power interruption (i.e. high voltage system reclosing). This is occurring to VFD circuits that are operating at the time of the outage and even those where the respective motors are not energized. Why?

Register to Reply
Pathfinder Tags: VFD operational experience
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster #1
#1

Re: VFD damage

04/30/2015 12:24 PM

Dont buy cheap Christmas Crackers...

Register to Reply
3
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#2

Re: VFD damage

04/30/2015 1:20 PM

Is this a new issue?

If yes;

I would check all equipment grounds, electrical ground grid, and device ground connections. (Make sure all are at less than 1 ohm resistance.)

If the circuit has surge protection, check that all SA are sized as per factory equipment voltage protection requirements and that none are open or too high impedance.

Check and verify all RLC filer noise bleed off circuit components are within factory OEM specifications and verify their connections to ground. (Look for a shorted or open capacitor and/or resistor and/or inductor and/or diode.)

If all of the above are correct and in good order; Use a voltage recorder with harmonic distortion detection capability to measure the peak voltage when the interruption(s) occur. This will identify if the VFD units are being subjected to voltage surges that are higher than allowed by design and also identify any harmonics that are being generated by the voltage pulse.

It is very possible that the equipment is experiencing a voltage doubling or tripling effect due to one or more RLC filter failure.

If it is an ongoing, existing problem;

The filter(s) is/are not adequate for the application or the installation is incorrect/faulty.

Good luck and stay safe!

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Good Answer (Score 3)
Participant

Join Date: Apr 2015
Posts: 3
#4
In reply to #2

Re: VFD damage

04/30/2015 4:51 PM

What I neglected to mention that may also have a bearing and may contribute to a better understanding of the problem is that the damage was caused not only to the VFDs that were energized (motors running) but also to those whose motors were not running.

Register to Reply
Power-User

Join Date: Aug 2008
Location: Melbourne, Australia
Posts: 476
Good Answers: 32
#5
In reply to #4

Re: VFD damage

04/30/2015 11:29 PM

When a short supply interruption occurs the VFD "soft-start" pre-charge system may not get switched out. The result would be a massive current surge when the supply comes back on (as the DC Bus capacitors are re-charged from the supply without any current limitation). The only way I can see to stop this effect would be to ensure that, when the supply is interrupted, it is enforced for a MINIMUM time - enough time for the pre-charge system in the VFDs to kick out.

Just a thought...

VFD manufactures usually indicate the maximum supply current that should be available:

EG

- Suitable for use on a circuit capable of delivering not more than 5000 rms symmetrical amperes, 480 V maximum, when protected by fuses.

- Suitable for use on a circuit capable of delivering not more than 50000 rms symmetrical amperes, 480 V maximum, when protected by CC, J, T or R class fuses.

__________________
johny451
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: VFD Damage

04/30/2015 2:50 PM

Please use the telephone to discuss the problem with the equipment manufacturer(s), then report back.

<subscribes>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#6

Re: VFD Damage

05/01/2015 3:47 AM

Could the HV reclosers create harmonics not filters by your RLC filters?

If possible, measure the odd harmonics.

__________________
BSEE but always learning
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#7

Re: VFD Damage

05/01/2015 4:48 AM

It might be a problem caused by the power coming back, while the VFD is in the process of "shutting down" as a name to use.

The electronics are in some areas still getting power from capacitors that have not lost their charge, but the overall control is gone. Inductors are shooting high voltages around as the power is dropped....

This can cause damage as parts are simply going "wild" as a word to use.

What could possibly prevent this to a degree, is some sort of breaker (I don't know the right name!), that drops off when no voltage is available...so the device cannot power up while still powering down! If power gos, it remains gone!! You need to go and reset them before powering up again.

This will probably prevent most problems, but possibly not all.....powering down such units while still operating, is bound to cause possible problems still from time to time.

Maybe the manufacturer needs to address such possible problems with a better design, stopping transients from entering sensitive electronics....

I would contact various manufacturers and ask how they handle uncontrolled power downs, or power "Hiccups".

Firstly, you need to fix the problem at the source (the power drop) and eventually possibly buy better quality VFD units that can handle that better as well......

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Participant

Join Date: Apr 2015
Posts: 3
#8

Re: VFD Damage

05/01/2015 12:17 PM

Me again. Thank you all for your responses. We are getting more info from the field all the time and no doubt we will be zeroing in on the solution as soon as we have identified the source of the problem. Another piece to the puzzle is that the motors controlled by VFDs but have not been fitted with passive filters that are connected to the low voltage busses have not suffered any damage. Also the damage that has occurred to the damaged VFDs has been to the IGBTs (at the output end) as well as the diodes of the uncontrolled rectifier (yes, the VFDs are the PWM type) - in other words, the damage has been pervasive.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#9

Re: VFD Damage

05/01/2015 12:39 PM

There is a long story as to why damage like this can happen, the end of which comes down to this anyway. You must have more impedance on the INPUT side of the VFDs. People often focus on the output filters to help protect the motors, which is fine, but neglect the input side simply because they may not be concerned about harmonics. Input reactors do little for harmonic mitigation, so people tend to leave them out, missing out on the OTHER more important benefit they bring, input impedance. It comes down to a combination of what was said earlier in this thread, but for different reasons. I'm on my iPad right now and this forum doesn't like Safari so it's too hard to do the long version, but if you want this to stop happening, go get line reactors for your drives.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#10

Re: VFD Damage

05/02/2015 2:30 AM

AndyGermany said "What could possibly prevent this to a degree, is some sort of breaker (I don't know the right name!), that drops off when no voltage is available...so the device cannot power up while still powering down! If power gos, it remains gone!! You need to go and reset them before powering up again."

Can i suggest a breaker controlled by a low-v or differential-v relay, or both.

__________________
BSEE but always learning
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#11
In reply to #10

Re: VFD Damage

05/02/2015 4:03 AM

I "feel" that such a breaker as you mentioned, would reduce the problems significantly.

As I see it, you feel possibly the same way?

Possibly not fix all the problems, but close to at a guess.....certainly a relatively cheap alternative, easily installed.

If the problems are (hopefully) reduced by at least 80% (or more as I believe they will be!) it would be very positive...

But till such a device is installed, we will not know!!

Guessing is simply not good enough!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

1capybara (2); Andy Germany (2); Anonymous Poster (1); CanukJake (2); Johny451 (1); JRaef (1); PWSlack (1); SHOCKHISCAN (1)

Previous in Forum: Big Capacity Motor Drawing Extra Current Than Small Rating   Next in Forum: Networked ESD Testing System

Advertisement