Induction Voltage

06/12/2015 1:11 PM

In our refinery plant,we face the issue of motor auto start,transformer(especially having long control cables) trip etc due to induction voltage on control cables.This might be due to poor installation methods that might have followed.Have anybody encounteered such problems ever?Please share with me & what remedial actions one have taken.Thanks in advance.

__________________
"Know something about everything and everything about something"
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#1

Re: Induction Voltage

06/12/2015 2:06 PM

I assume the control wires are twisted pair, perhaps with shields? Shielded is better, costs more $$ though. You might have insulation corrosion that allows one leg to touch the metal conduit - sure to make problems. How old is the installation now?

__________________
Per Ardua Ad Astra
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#2

Re: Induction Voltage

06/12/2015 2:53 PM

Why do you think that it is triping do to induction on the control cables? Is this a new problem or has it been happening since day one of use? What in the installation methods lead you to believe that maybe the cause? How long are these runs of cable? What is the control wire functions? Types of controls? Wiring Diagram? Voltages?

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Induction Voltage

06/13/2015 12:08 AM

Why do you think that, "transformer(especially having long control cables) trip etc due to induction voltage on control cables."

The remedial action I would take is to engage an engineer who can determine the real cause of tripping and remediate it.

Control cables do not carry high voltage/amperage. They just tell other things what to do.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#4

Re: Induction Voltage

06/13/2015 4:34 AM

In certain circumstances, long control cables in AC actuated control circuits may prevent the disconnection of contactors due to the cable capacitance present. Even if the command contacts are open, the coil current can still flow due to the cable capacitance so that the contactor remains in the On position if sufficient sealing current is present. The effect of cable capacitance depends on the design of the control current circuit.See [for instance]:

http://www.moeller.net/binary/ver_techpapers/ver949en.pdf

__________________
Julius
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#5

Re: Induction Voltage

06/13/2015 9:55 AM

I had a turnkey startup for a standby generator for a new nursing home. I noticed the control wiring sharing the same conduit with the block heater circuit. I notified the engineer, who got the plans out and saw that the plans called for a separate conduit run. I don't know what the remedial action was, because I left when the engineer blew up. I think it might have had something to do with the conduit runs entering the new foundation below grade level.

__________________
CRTL-Z
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#6

Re: Induction Voltage

06/14/2015 9:36 PM

Dear Mr.giri,

You have not mentioned whether the power cable and control cable is fixed side by side.

If so it is to be seperated by a minimum distance of 1 Metre or the control cable should be shielded. You have also not mentioned the type of cable used. Replacing the existing control cable with a shielded type will be costly. Hence seperate them so as to have 1 Metre distance.

Pl. inform this Forum how the problem is solved.

DHAYANANDHAN.S

Register to Reply Score 1 for Good Answer
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (1); aurizon (1); dhayanandhan (1); lyn (1); ozzb (1); Unredundant (1)