Directional Power Element

06/22/2015 8:23 AM

Dear CR4 Members.

How to test the Directional power element in Generator protection relay.

What should the connection setup, parameters & observation?

Thanks,

Register to Reply
Pathfinder Tags: Directional Power Element.
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#1

Re: Directional Power Element.

06/22/2015 10:17 AM

What? If you are concerned about direction, then you must be talking about a multiphase generator. (Yes or No?)

If that is the case, then are you not more concerned with the direction of the load? I mean, is it possible for the generator to be started in the wrong direction?

There are several phase sensitive protection relays on the market. Many of them include other features such as phase loss detection, under-voltage, and/or over-voltage detection. The connection setup comes with the product on a sheet of paper inside the box. You might have to buy a relay base for it to plug into because it is intended to be replaceable. If this is what you are looking for, help us a little so we can help you.

Otherwise, it is all guesswork.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Associate

Join Date: Apr 2013
Posts: 26
#3
In reply to #1

Re: Directional Power Element.

06/23/2015 5:04 AM

NoturOrdinaryJoe.

Case is that,

we have a generator protection relay installed in generator control panel.During the testing of reverse power function of the protection relay, facing problem & need guide line to that, what is the right way to test this function in a sense of test connections, setting parameters & Simulation?

Thanks,

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #3

Re: Directional Power Element.

06/23/2015 10:21 AM

See #2 below.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Directional Power Element.

06/22/2015 1:14 PM

If the procedure is not in the manual that arrived with the equipment, then the first step is a telephone discussion with the equipment manufacturer.

Do let the forum know how it went, as it may well be useful to others.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#4

Re: Directional Power Element

06/23/2015 9:18 AM

http://www.usbr.gov/power/data/fist/fist3_8/vol3-8.pdf

Above is a link that should explain the procedure well enough to get a grasp on the procedure.

You need to obtain the OEM setup manual for the particular relay being tested and follow the test procedure outline in order to be successful as different relays have different setup & test procedures.

You must have a functional test set that is compatible with the relay being tested.

If reading the test procedure in the relay manual does not make sense or testing does not yield the results you expect, then you must contact the relay manufacturer for directions.

Good luck & stay safe.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Score 1 for Good Answer
Register to Reply 5 comments

"Almost" Good Answers: