Earthing of Building with Basement

06/23/2015 12:38 AM

we gave to do earthing of building consisting of Testing equipment.

building having basement of depth -6 .5 mtr.

at what depth we have to put / lay earthing conductor ?

either below -7.5 mtr, or laying earthing conductor -1 mtr outside the foundation and can we connect basement reinforcement

Can we implement this to achieve this earthing solution ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: Earthing of Building with Basement

06/23/2015 9:23 AM

Wow. Carving a 6.5 meter deep basement out of solid granite must be expensive. Drainage must be awkward. At least you will not have to contend with lava flows or coffer dams to hold back the tide.

I wonder what the local regulations say about earth conductors. You'll probably have to run a separate cable into the lagoon for a sea ground.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Earthing of Building with Basement

06/23/2015 10:18 AM

Consult a qualified Electrical Engineer locally, who will design the earthing requirements based upon the appropriate national electrical codes: in the UK, for example, BS7671; in India IS3053; etc., etc.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#3

Re: Earthing of Building with Basement

06/24/2015 12:25 AM

First of all I agree with PWSlack. In USA NEC[for instance] states:

[NEC 2014 Art.250.52 Grounding Electrodes. (A) Electrodes Permitted for Grounding. (3) Concrete-Encased Electrode.]

"Metallic components shall be encased by at least 50 mm (2 in.) of concrete and shall be located horizontally within that portion of a concrete foundation or footing that is in direct contact with the earth or within vertical foundations or structural components or members that are in direct contact with the earth."

See also [for instance] NECA 331/2009 Ch. 3.4 Concrete-Encased Electrodes[Ufer Grounds]

National Electrical Contractors Association

Building and Service Entrance Grounding and Bonding

https://www.necanet.org/store/product/neca-331-2009-standard-for-building-and-service-entrance-grounding-and-bonding-(ansi)-Standard

__________________
Julius
Register to Reply
Participant

Join Date: Feb 2013
Posts: 4
#4

Re: Earthing of Building with Basement

06/24/2015 10:23 AM

A comprehensive soil resistance test must be performed to conclude the effectiveness of the proposed earthing system. It maybe as simple as can be. But consider how good of a grounding system is required. What is the building with a basement going to be used for? In the electrical industry, one should consider the use of current prior to breaking ground.

Register to Reply
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#5

Re: Earthing of Building with Basement

06/24/2015 10:57 AM

The placement of the Building's main electrical and mechanical grounding system should be physically deep enough to achieve and meet the minimum ground resistance required, as defined by the local electrical code.. Must also be Mechanically sound, strong to maintain its safe grounding integrity..

__________________
vsar
Register to Reply
Register to Reply 5 comments