Anonymous Poster #1

Energy Measurement

06/23/2015 11:14 AM

We have two station bus A&Bof 6.6kV each bus fed with a station transformer saperately and both buses are connected with tie breakers at both buses for inter connectio in case of any station transformer fails. All tie feedres are mounted with energy meters at both the end. My question is when tie feeder energy meter running when sending the power from A to B are receiving power from B to A

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Energy measurement

06/23/2015 11:19 AM

Please rephrase the question, as its meaning is unclear.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#2

Re: Energy measurement

06/23/2015 11:37 AM

I pick C

Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: Energy measurement

06/23/2015 12:01 PM

The energy meters are probably bidirectional, and are reading the same either way...check the model #'s and contact the supplier for spec info....You might have the wrong meters for your application....

http://www.powerlogic.com/product.cfm/c_id/1/sc_id/6/p_id/23

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#4

Re: Energy Measurement

06/23/2015 1:10 PM

I choose "E" None of the above.

I know there is a question in there somewhere?

Can someone translate please?

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Reply
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5

Re: Energy Measurement

06/23/2015 1:20 PM

I believe AP is worried about whether he is being double billed if power flows between the feeders when the tie bus is closed. There should be no problem if meters are bidirectional and the instrumentation transformers' polarities are correctly connected, if not then better hire a competent engineer to work with the utility to straighten things out.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply Good Answer (Score 2)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: Energy Measurement

06/23/2015 8:18 PM

42

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#7

Re: Energy Measurement

06/23/2015 11:55 PM

for metering purpose polarity of CTs are not a matter, it will measure the disregard the direction of current, so when the bus tie is closed the bus energy meter will read the power of bus which the transformer is not connected, i hope there is only one bus tie, what do u mean by all tie feeders?

Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#8
In reply to #7

Re: Energy Measurement

06/24/2015 12:50 AM

"...polarity of CTs are not a matter...", absolutely wrong, the direction of the current through a CT determines its phase relationship with the voltage and whether the power is flowing into or out of a circuit. Incorrect wiring is a common problem, along with improper ratio/meter constants, for energy metering and billing problems/disputes.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply Score 1 for Good Answer
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#9
In reply to #8

Re: Energy Measurement

06/25/2015 1:30 AM

You're running hot here mate. Didn't give you a GA for this one even though it's right on the money. A little of topic but not worth an OT rating. Already gave you a GA for your last comment which covered it.

Wish OP all the best.

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#10
In reply to #8

Re: Energy Measurement

06/29/2015 12:51 AM

dear sir,

i mean in this system v r talking abt bus tie ct only, it has to measure the bus current only when, ie when bus tie is on, only one incomer will be in closed condition so it will measure the power of the bus which the incomer is not connected

Reply
Participant

Join Date: Jan 2015
Posts: 2
#11

Re: Energy Measurement

06/29/2015 10:34 AM

Energy meters have no directions meaning its only voltage and currents which are -ve and on top of that energy has no -ve sign.So it will read in both the directions..

Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#12
In reply to #11

Re: Energy Measurement

06/29/2015 2:44 PM

You cannot make those statements without knowledge of the meter. Depending upon the requirements of the local utility company some energy meters have a ratcheting mechanism that will only allow the meter to record energy flowing to the customer, not from the customer to the utility.

Energy does indeed have direction, it flows from the source to the consumer. If it didn't have direction how else would you get credit when your solar system was producing excess energy and putting it into the network? Meter polarity is very important and must not be ignored if you are to expect proper billing.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#13
In reply to #12

Re: Energy Measurement

07/05/2015 3:49 AM

Energy is not a vector is what I think is meant but just because it's not a vector doesn't mean it can't be added and subtracted.Getting the meter sensor polaritites around the same way will make sure that the energy's exit or ingress is correctly reported on a mter.

I think you are right about the meters only recording energy that's sold and not creditting donor sources. The whole grid connect issue again. Utilities don't really want your energy.

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#14
In reply to #13

Re: Energy Measurement

07/05/2015 2:46 PM

Correct, energy is the dot product (scalar multiplication) of two vectors and results in a scalar quantity; however, scalar quantities have a sign (+ or -) associated with them, otherwise why would we need the absolute value function.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#15
In reply to #14

Re: Energy Measurement

07/06/2015 7:07 AM

Then there's the story of the ATS connected on the wrong side of the meter.

Burning diesel and spinning the billing consumption meter.

Still better than the one that lit up the whole street........

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply
Reply to Forum Thread 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Demonicious (1); Fredski (1); JRaef (1); Original_Macgyver (1); PWSlack (1); RAMConsult (4); roykav (2); SolarEagle (1); Wal (3)

Previous in Forum: Earthing of Building with Basement   Next in Forum: Breaker Size

Advertisement