Insulation Co-ordination of Power Transformer

06/29/2015 7:40 AM

Dear All,

We are doing a project in Eastern Europe, in which a Non-uniform insulated Power Transformer of 10MVA capacity is used.The SLD shows that a disconnect switch is provided in the Neutral bushing-Ground of the 10MVA Power transformer. The reason (assumed) is to operate the system either grounded or ungrounded. Surge Arrester is also provided at the Neutral bushing.

The basic insulation level (BIL) shown in the drawings are:

Impulse Voltage:

a) HV - 550 kVp

b) HV (Neutral) -95 kVp

c) LV - 75 kVp

Power Frequency Voltage:

a) HV - 230 kVrms

b) HV (Neutral) -38 kVrms

c) LV - 28 kVrms.

My questions are,

1. Can Non-uniform insulated transformers be used without Neutral Grounding? (Ungrounded).

2. Assuming the system is ungrounded, what will happen if one phase is faulted (Single line to ground fault)? Does the Power Frequency Voltage of HV (Neutral) is enough?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: Insulation co-ordination of Power Transformer

06/29/2015 7:55 AM

The reason you need a neutral-to-ground connection is that the transformer secondary may be in parallel with other sources of power, and a single connection prevents currents circulating in the neutral otherwise. The circuit protective devices will still work just fine.

__________________
Good moaning!
Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#2

Re: Insulation co-ordination of Power Transformer

06/29/2015 9:33 AM

This worries me in multiple ways on the same topic. People who do not know or understand the power distribution rules for a region should not be allowed to touch any of it, let alone get a contract to do this kind of work.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #2

Re: Insulation co-ordination of Power Transformer

06/29/2015 11:33 AM

Don't worry. The poster is Anonymous. :-$

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#5
In reply to #4

Re: Insulation co-ordination of Power Transformer

06/29/2015 12:15 PM

Clearly for a good reason.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Insulation co-ordination of Power Transformer

06/29/2015 9:47 AM

<...We are doing a project...>

Consult an Electrical Engineer within the organisation, to organise mentoring.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#6

Re: Insulation Co-ordination of Power Transformer

06/29/2015 1:58 PM

I agree with PWSlack: Consult an Electrical Engineer specialist in this field.

I am not a specialist in this field. In my opinion you have to consult the manufacturer.

However, I know two standards recommending the impulse test requirement and procedure:

IEEE 32/1972/1990 ch.5.2.1 Impulse Tests (see definition in Section 13).

and IEC 60076-3/2000 ch.7.4.3 Neutral terminal not directly earthed.

__________________
Julius
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7

Re: Insulation Co-ordination of Power Transformer

06/29/2015 7:19 PM

If there are no codes, specifications, regulations, inspecting agencies, safety requirements, insurance companies underwriting the loss of life and property associated with this project in "Eastern Europe", then don't worry, be happy.

Forge ahead with blind abandon!

I'd leave the country PRIOR to commissioning of the project, if at all possible.

For the record, I don't have a clue.

Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#8

Re: Insulation Co-ordination of Power Transformer

06/30/2015 9:42 AM

1. Can Non-uniform insulated transformers be used without Neutral Grounding? (Ungrounded). Yes if the OEM design allows it. Contact the OEM.

2. Assuming the system is ungrounded, what will happen if one phase is faulted (Single line to ground fault)? Does the Power Frequency Voltage of HV (Neutral) is enough? Nothing. This method is used regularly in order to adapt system protection relay schemes for ungrounded 3 phase systems. However, if a second phase should go to ground there can be catastrophic damage experienced by the transformer.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#9

Re: Insulation Co-ordination of Power Transformer

07/03/2015 8:56 AM

You have star connected 132kV winding with non-uniform insulation. Neutral may be isolated from ground using disconnecting switch but still the surge arrester will earth the neutral in case of over voltage appearing at the neutral terminal. This is my understanding and hope it is correct.

With the system as above, the 132kV winding is not designed for earth isolated operation.

In case the disconnecting switch is kept open, the surge arrester will have to protect the winding insulation closer to neutral by conducting the overvoltage to earth, when there is an single phase to earth fault elsewhere in 132kV system. This is the case if the transformer has source on the LV side.

If the subject transformer is at the load end, stepping down the grid voltage to supply loads downstream, there shouldn't be a problem of overvoltage and no issue in operating the transformer 132kV winding neutral unearthed.

__________________
Raghunath
Reply
Anonymous Poster #1
#10
In reply to #9

Re: Insulation Co-ordination of Power Transformer

07/06/2015 4:00 AM

Dear Sir,

Thank your for your reply.

In case the disconnecting switch is kept open, the surge arrester will have to protect the winding insulation closer to neutral by conducting the overvoltage to earth, when there is an single phase to earth fault elsewhere in 132kV system. This is the case if the transformer has source on the LV side.

What happens if Line to ground fault occurs at the 132kV in actual?

If the subject transformer is at the load end, stepping down the grid voltage to supply loads downstream, there shouldn't be a problem of overvoltage and no issue in operating the transformer 132kV winding neutral unearthed.

Why there will not be a problem, for the transformer at the load end?

Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#11
In reply to #10

Re: Insulation Co-ordination of Power Transformer

07/25/2015 4:09 AM

When there is line-to-ground fault in 132kV system eslewhere (such as OHL or Cable feeder upstream), the current tries to circulate through the transformer neutral, provided the transformer has source(s) connected on its secondary. If the DSis open and thus current circulation is blocked, the neutral assumes voltage with reference to ground that is close to phase-to-ground voltage of the system. Since the transformer is non-uniformly insulated, the transformer neutral is unlikely to withstand this voltage stress and transformer may fail.

If the subject transformer is at the load end, the transformer neutral doesn't form part of earth fault loop for circulation of currents (instead the transformer at the source end will take that role) and hence would be safe.

__________________
Raghunath
Reply Score 1 for Good Answer
Reply to Forum Thread 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (1); Anonymous Poster (1); Crabtree (1); lyn (1); PWSlack (2); raghun (2); redfred (2); SHOCKHISCAN (1)

Previous in Forum: Datasheet for IC LCKH   Next in Forum: Problem with Twin Line Servomotor Controller with Hiperface Encoder

Advertisement