Induced Draft Counter Flow Cooling Tower Problem

07/07/2015 3:05 AM

Dear All,

We are facing a problem of High Cold water temperature from Induced draft counter flow cooling tower for 600 MW unit with CW Flow - 67500 m3/hr.

Actual parameters are as below:

Range - 10 C against design 10 C

CWT - 36 C against design 32 C

CT Airflow - As per design

Dry Bulb Temperature - 44 C against design 32.7 C

Wet Bulb Temperature - 27 C against design 28 C (As WBT is less than design, tower should perform as per design)

Humidity - 27 % against design 70 %

Please help me to identify possible causes of High Cold water temperature

Regards,

Gaurav

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Induced draft counter flow cooling tower problem

07/07/2015 5:02 AM

Tower too small.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 2)
2
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#2

Re: Induced draft counter flow cooling tower problem

07/07/2015 6:23 AM

This degradation seems to be caused by high input air temperature of 44C (11.3 C degrees higher than design), which leads to the cold water being 4 degrees higher. Doubtless due to the record breaking high temperatures in your area, which cause a reduction of the ability of the tower to cool the water down. The humidity is low, or the problem would be exacerbated.

The tower is too small at the extreme temperatures encountered lately. The only fix is a supplemental tower to be used on the bad days to give added cooling. Some of these links might offer suggestions

cooling tower degradation

__________________
Per Ardua Ad Astra
Register to Reply Good Answer (Score 2)
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#3

Re: Induced draft counter flow cooling tower problem

07/07/2015 7:09 AM

You don't mention the incoming temperature, if that is higher than design limits then you will get higher outlet temps.

You do say that the range of 10°C is within design parameters, so the tower is achieving the temperature reduction that it is designed to do, so the problem is most likely incoming temperature or total heat load.

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#4

Re: Induced Draft Counter Flow Cooling Tower Problem

07/07/2015 8:20 AM

it is working as designed, just stop hitting it with high inlet temps, DUH

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#5

Re: Induced Draft Counter Flow Cooling Tower Problem

07/07/2015 8:44 AM

Are you sure the direction of air flow for all fans is correct? If you have one or more fans running in the wrong direction, the temperature will be affected.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru
Engineering Fields - Mechanical Engineering -

Join Date: Sep 2009
Posts: 1651
Good Answers: 71
#6

Re: Induced Draft Counter Flow Cooling Tower Problem

07/07/2015 9:29 AM

Inspect your cooling tower fill also. It should be breaking the water into fine droplets. If you are getting pouring water you could try to add more fill or decrease flow.

I saw a problem once where the scrubber balls from the condenser were plugging the holes in the deck causing water to cascade over the side or stream out in thick columns that wouldn't break sufficiently.

I hope your operators are sufficient to ensure fan direction is correct, you might be able to change the pitch of the blades to get a bit more air flow, but if the weather is a temporary issue it would be better to leave them.

Drew K

__________________
Question: What is going on with the American's Government? Response: Who is John Galt?
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jun 2010
Location: Chennai India
Posts: 20
#7

Re: Induced Draft Counter Flow Cooling Tower Problem

07/07/2015 10:58 AM

Please check your fill it might have scaled and also check the air flow it may be reduced due to the choking of fills

__________________
enervac
Register to Reply
4
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#8

Re: Induced Draft Counter Flow Cooling Tower Problem

07/07/2015 1:31 PM

Dear Mr.gaurav sharma,

You have not mentioned no. of cells. You have told some parameters as per design.

You have also mentioned Wet Bulb Temperature - 27 C against design 28 C. A lower Wet-Bulb temp should give a better performance than the design value since the Cooling Tower Efficiency is given by the equation (Thot-Tcold)/(Thot -Twet)

You have also mentioned that the Actual Relative Humidity is 27% as against 70%, which should result in a better performance since lesser Relative Humidity Air will absorb more water vapour to reach to Saturation Level, thus removing more heat from the hot water.

But it is not so in your case. I suspect the air flow is disturbed and required quantity is not flowing. To check this pl. verify the following.

From design aspect - What is the MERKEL RATIO in the design and what is the actual ratio when you face the problem. In other terms what is the Design L/G ratio and actually observed. I have a doubt the Air flow is reduced may be due to blade angle change.

What is the power absorbed by the Fan Motor(s) - it should be loaded to 80% and more. If less, the Air flow is reduced.

Pl. read the subject from the following links and you may find a solution for your problem.

DHAYANANDHAN.S

https://www.google.ca/search?q=cooling+tower+degradation&oq=cooling+tower+degradation&aqs=chrome..69i57.11662j0j8&sourceid=chrome&es_sm=93&ie=UTF-8

http://www.google.co.in/url?sa=t&rct=j&q=&esrc=s&source=web&cd=4&cad=rja&uact=8&ved=0CDEQFjAD&url=http%3A%2F%2Fclasses.engineering.wustl.edu%2Fche473%2Fhandouts%2Fcooling%2520tower%2520performance.pdf&ei=JgKcVd62GOHfmgXvsIG4BA&usg=AFQjCNG7yg3qRNw2JxnKMx3KLO2M88OyvA&bvm=bv.96952980,d.dGY

https://books.google.ca/books?id=6j5nuvAd44QC&pg=PA378&lpg=PA378&dq=cooling+tower+degradation&source=bl&ots=HHBQK_aj_R&sig=8z_S323lArxigoFI4GwfAOJUOYA&hl=en&sa=X&ei=rgScVeu4LObGmAXuyIPQAw&ved=0CFcQ6AEwBQ#v=onepage&q=cooling%20tower%20degradation&f=false

http://www.google.co.in/url?sa=t&rct=j&q=&esrc=s&source=web&cd=13&cad=rja&uact=8&ved=0CGIQFjAM&url=http%3A%2F%2Fnaabzist.com%2Fpdf%2FCooling%2520Tower%2520Thermal%2520Design%2520Manual.pdf&ei=JgKcVd62GOHfmgXvsIG4BA&usg=AFQjCNE8SS278wJjZ1nrh4 YxP3GrHE0Qnw&bvm=bv.96952980,d.dGY

http://www.google.co.in/url?sa=t&rct=j&q=&esrc=s&source=web&cd=12&cad=rja&uact=8&ved=0CCIQFjABOAo&url=http%3A%2F%2Fwww.kgogroup.com%2Fwp-content%2Fuploads%2FCooling-Tower-Basics-and-Common-Misconceptions1.pdf&ei=kwacVY2LBsTGuATmi4PYCg&usg=AFQjCNHJkoxBWUZwUtQoxvwwbl3uXqAbWA&bvm=bv.96952980,d.dGY

http://www.google.ca/url?sa=t&rct=j&q=&esrc=s&source=web&cd=14&cad=rja&uact=8&ved=0CD0QFjADOAo&url=http%3A%2F%2Fwww.ijsrp.org%2Fresearch_paper_feb2012%2Fijsrp-feb-2012-33.pdf&ei=VwWcVfuFOoilmQWn-4ioAw&usg=AFQjCNHWJuGH1dYqbnh4VcIaVA0SGcinCQ&bvm=bv.96952980,d.dGY

http://www.google.ca/url?sa=t&rct=j&q=&esrc=s&source=web&cd=16&cad=rja&uact=8&ved=0CEcQFjAFOAo&url=http%3A%2F%2Fxa.yimg.com%2Fkq%2Fgroups%2F10603698%2F137609219%2Fname%2FNDCT&ei=VwWcVfuFOoilmQWn-4ioAw&usg=AFQjCNH3dCxmNjOAQqFgPANskPaOy2c01Q&bvm=bv.96952980,d.dGY

Register to Reply Good Answer (Score 4)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9

Re: Induced Draft Counter Flow Cooling Tower Problem

06/23/2023 7:34 AM

What does <...High...> actually mean (rhetorical question - NNTR)?

The water temperature can never go lower than the wet-bulb temperature of the air passing through it, for it is this that determines whether any evaporation takes place. With the given figures, if the wet-bulb is <...27 C...>, then that is the minimum achievable cooling water supply temperature, and in practice it will be a bit warmer than that.

If cooler heat transfer fluid temperatures are required, then a refrigeration loop is needed downstream of the tower to provide those temperatures, and that's all there is to it.

If in doubt, consult a qualified Heating, Ventilation and Air Conditioning Engineer.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

aurizon (1); dhayanandhan (1); Drew K (1); enervac (1); Fredski (1); PWSlack (1); SHOCKHISCAN (1); spades (1); Tornado (1)