Power Transformer Loading

07/15/2015 7:27 AM

Dear experts,

How long a oil cooled, oil forced transformer can be fully loaded?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Power Transformer loading

07/15/2015 8:02 AM

Presumably forever, but there are some real-life limits on duration such that nothing really lasts quite that long.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Power Transformer Loading

07/15/2015 9:54 AM

Until it fails.

Maybe you should try asking people who make them.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5
In reply to #2

Re: Power Transformer Loading

07/15/2015 5:40 PM

Or, until it falls off the truck.

Now, that's just being too cute.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: Power Transformer Loading

07/15/2015 1:25 PM

14 hrs per day....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4

Re: Power Transformer Loading

07/15/2015 3:56 PM

From your previous questions it sounds like you work at a thermal power plant. It also sounds like you really are not qualified to do so.

I am not going to offer advice to someone I think is doing something very dangerous and outside what they are qualified to do, ESPECIALLY if they got themselves responsible for the management or maintenance of a thermal power plant, which appears to be the case here.

Hire a competent Engineer. A multi million dollar, multi-megawatt power plant is not a toy!

__________________
jack of all trades
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#6

Re: Power Transformer Loading

07/16/2015 1:23 AM

ask manufacturer. consider continuous continuous and cycling loads and harmonics

__________________
pnaban
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7

Re: Power Transformer Loading

07/16/2015 12:45 PM

Indefinitely. This question may be answered by transformer manufacturers over the telephone!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#8

Re: Power Transformer Loading

07/16/2015 6:05 PM

Read what it says on the rating plate on the side of the transfo. It should state the standard to which it was made & ratings without & with pump. Better still, refer to the documentation with the transfo and the standard to which it was designed.

Normally, ratings are continuous for certain ambient and temperature rise conditions.

Register to Reply Score 1 for Good Answer
Member

Join Date: Feb 2015
Posts: 7
#9

Re: Power Transformer Loading

07/17/2015 1:25 AM

I am having two 45MVA Unit transformers & one 50MVA station transformer.My total load is approximately 45MVA. I would like to know how much spare capacity i have. That's why I am asking how long a oil forced transformer can be fully loaded?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#10
In reply to #9

Re: Power Transformer Loading

07/17/2015 1:39 AM

Looks like 45 (or even 95) MVA spare capacity. Jeez, you must be fully loaded with money. Or Johnnie Walker.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#11
In reply to #9

Re: Power Transformer Loading

07/17/2015 6:31 AM

A single line diagram would help.... my impression is that you have 2 "45MVA" generators & One common station transfo 50 MVA. Your load on the 50 MVA transfo would be 45 MVA?

Typically each genset would run half the hours, but the 50 MVA would always be loaded.

So the genset transfos use up their life at half the rate of the 50 MVA.

A transfo fully loaded to its standard will last 10s of years ON AVERAGE.

A "rule of thumb" is that an extra 8 Celsius insulation temperature will halve its life.

So the extra 5 MVA of the 50MVA may be so that its service life can be expected to be similar to the "half-timer" generator transfos.

Also, if this kit is not new, pushing the ratings could be disastrous.

CR4 posters will not wish to give you bad advise because of lack of knowledge of the circumstances.

Register to Reply Score 1 for Good Answer
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#12
In reply to #9

Re: Power Transformer Loading

07/19/2015 3:42 PM

Based on your previous posts this is a theoretical question (and not homework) right, not a real thermal power plant you are personally responsible for? Your language implies that it is the latter, but this could just be a language barrier confusion on our part.

The answer to this question will help us determine if you are just trying to improve your knowledge of a subject or if you are doing something.........else.

The way you have posted it REALLY looks like you are responsible for operating a thermal power plant but are not qualified to do so. To say this is unsafe and illegal is somewhat of an understatement.

__________________
jack of all trades
Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#13
In reply to #12

Re: Power Transformer Loading

07/19/2015 4:26 PM

It's India. That don't matter.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#14
In reply to #13

Re: Power Transformer Loading

07/19/2015 5:00 PM

Although some countries may be more lax with their legal and safety standards (and I am NOT mentioning any names here) it still matters regardless of where you are in the world.

A disaster resulting in a loss of income or life is a very effective equaliser.

__________________
jack of all trades
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#15
In reply to #14

Re: Power Transformer Loading

07/19/2015 6:22 PM

My emoticon inserter doesn't work, so it's hard to convey satire/parody/irony.

Perhaps the best answer to the OP is, longer than I can!

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#16
In reply to #15

Re: Power Transformer Loading

07/19/2015 6:46 PM

Mine's been broken for a while (also why I don't post pictures anymore). Try right click over the top and copy paste, that works for me.

Alternatively, go old school ;)

__________________
jack of all trades
Register to Reply
Register to Reply 16 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments: