Single Phase Pump vs Three Phase Pump

07/17/2015 4:45 AM

Pump performance is determined by head and flow rate. If source of power supply (single phase or three phase) is not a matter. What would be the best pump selection (single phase or three phase) ? What the advantages ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: May 2013
Posts: 66
#1

Re: Single Phase Pump vs Three Phase Pump

07/17/2015 5:15 AM

Thanks

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2
In reply to #1

Re: Single Phase Pump vs Three Phase Pump

07/17/2015 5:18 AM

Learn how to use a search engine.

Register to Reply
Guru
Technical Fields - Project Managers & Project Engineers - New Member

Join Date: Jun 2014
Posts: 623
Good Answers: 33
#3

Re: Single Phase Pump vs Three Phase Pump

07/17/2015 7:41 AM

Three phase will have more economical operating costs over time. With pumps, this is extremely important. A pumps operating costs over time far outweigh the initial capital investment of the pump.

3 phase, with the highest voltage available will draw the fewest Amps, Amps are what you pay for ALL the time, if you reduce the amp draw, you reduce the overall cost of the pump over the lifetime of the pump.

__________________
Hey Isaac, catch! ...oops, that's gonna leave a mark...
Register to Reply Score 1 for Off Topic
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#5
In reply to #3

Re: Single Phase Pump vs Three Phase Pump

07/17/2015 8:56 AM

No... you pay for power... power is watts. So... 1000 watts is still 1000 watts whether single phase or 3 phase.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7
In reply to #5

Re: Single Phase Pump vs Three Phase Pump

07/17/2015 9:40 AM

True that "watts is watts", but if the three phase motor is more efficient than a single phase motor delivering the same power output, you'll use less watts.

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#11
In reply to #7

Re: Single Phase Pump vs Three Phase Pump

07/17/2015 10:27 AM

Agreed... using less watts is always a good thing.

But... if two motors, one single phase and the other 3 phase, had the exact same ratings (efficiency, power factor etc.) and were both 5hp, the cost to operate is identical for both motors.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#12
In reply to #7

Re: Single Phase Pump vs Three Phase Pump

07/17/2015 10:53 AM

So what about us guys who like to run our three phase motors on single phase just to go against the grain?

Register to Reply Score 1 for Off Topic
Guru
Technical Fields - Project Managers & Project Engineers - New Member

Join Date: Jun 2014
Posts: 623
Good Answers: 33
#8
In reply to #5

Re: Single Phase Pump vs Three Phase Pump

07/17/2015 9:46 AM

wattwät/nounnoun: watt; plural noun: watts; symbol: W The SI unit of power, equivalent to one joule per second, corresponding to the power in an electric circuit in which the potential difference is one volt and the current one ampere.
Of course we pay for power, but the FLA on a 5hp motor on 3 phase with 460 volts is 7.6 amps.
And the same motor on single phase with 120 volts will draw 56 amps FLA.
So which would you rather pay for on a pump that may run 24/7 for a municipal water tower?

__________________
Hey Isaac, catch! ...oops, that's gonna leave a mark...
Register to Reply Score 2 for Off Topic
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#10
In reply to #8

Re: Single Phase Pump vs Three Phase Pump

07/17/2015 10:08 AM

If you discount the efficiencies of the motors and the nature of the power delivery system... there ARE NO savings in using a three phase source over a single phase source. Horsepower is horsepower whether from a single phase or 3 phase source.

The difference is in how that power is delivered.

Don't believe me... do the math.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#14
In reply to #10

Re: Single Phase Pump vs Three Phase Pump

07/17/2015 12:42 PM

Hello North:

You're not considering the extra cost of a start winding, centrifugal sw. and start capacitors, all of them subject to failure, and in my experience, much sooner than the run windings.

The 3 PH motor is the simplest of the motors, and as I said before, creates its own starting torque, no need for anything that will be of no use while running, exept in the case of start-run capacitors, but that is just one type of single phase starting method.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#17
In reply to #14

Re: Single Phase Pump vs Three Phase Pump

07/17/2015 12:55 PM

Agreed... I am only considering the energy consumed by the motors themselves. My comments on this are based on the comment, from Massey, that a 3 phase motor consumes less energy (if everything else is equal) than a single phase motor of the same size. Period...

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#18
In reply to #17

Re: Single Phase Pump vs Three Phase Pump

07/17/2015 1:18 PM

Remember,

This question is from the same guy who brought us:

Operating at 230V

Circuit Breaker

Phase Rotation and other questions of an elementary nature.

It seems clear that all this discussion is being squandered on someone who does not understand electrical theory or codes.

<unsubscribe>

Register to Reply
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#13
In reply to #3

Re: Single Phase Pump vs Three Phase Pump

07/17/2015 12:33 PM

I'm surprised you were rated off topic, specially regarding the first paragraph of your post, I agree with you, and I would only add that a 3PH pump doesn't require an extra starting device to create a rotating magnetic field and starting torque; the rotating magnetic field is inherent to the 3 phases' 120 electrical degree shift.

No capacitors to dry out.

No charred or worn centrifugal sw. contacts

No starting problems whatsoever, as long as the motor is properly rated and not burn't.

Here's a GA for you pal !

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Guru
Technical Fields - Project Managers & Project Engineers - New Member

Join Date: Jun 2014
Posts: 623
Good Answers: 33
#16
In reply to #13

Re: Single Phase Pump vs Three Phase Pump

07/17/2015 12:48 PM

Thanks Yahlasit.

__________________
Hey Isaac, catch! ...oops, that's gonna leave a mark...
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#4

Re: Single Phase Pump vs Three Phase Pump

07/17/2015 8:20 AM

Make sure you are connected or have access to a (3) phase grid

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#6

Re: Single Phase Pump vs Three Phase Pump

07/17/2015 9:02 AM

It depends on the application and whether there are power demand and/or minimum power usage stipulations from the power supplier.

For applications 5HP and under there are minimal to no savings realized by using 3 phase equipment.

If the pump is a stand-alone application that will not be operating more than 50% of the time the standby and demand power charges can easily offset any possible savings realized and in most cases over a long period of time will cause the cost of 3 phase power service to far exceed the cost of using single phase power.

As far as the cost of rewinding and maintaining a 3 phase or single phase motor is concerned there is little to no difference on motors rated at 5HP and less.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#21
In reply to #6

Re: Single Phase Pump vs Three Phase Pump

07/18/2015 7:20 AM

I don't understand all of that. Can you elaborate?

What are standby power charges? I believe peak demand power charges are based on max power in any 30-minute period, so as JRaef said in #10 starting peaks are unlikely to affect it. How do these charges differ for 1 and 3 phase?

I assume OP has both systems available, clearly the figures might be different if he was deciding which system to install.

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#9

Re: Single Phase Pump vs Three Phase Pump

07/17/2015 10:06 AM

You cannot ASSume that 3 phase motors are more efficient, some single phase motors have equal or even better efficiency than equivalent 3 phase versions. The only thing that matters in that regard is the rated efficiency as stated by the motor mfr, if you believe it (bottom feeders are known to cheat).

So as others have said, you do NOT pay for amps, you pay for watts, and watts are watts regardless of phases. As to demand charges, most utilities use a sliding demand window anyway, so a brief peak of starting current has almost no effect the overall demand charges. Only in the most extreme cases do utilities charge for what is called "instantaneous" deman. Yet because a rare few do, the suppliers of mitigating technologies pounce upon this to over exaggerate the benefits of their technologies in mitigating it. There may be other perfectly legitimate reasons to soft start motors, but contrary to popular belief, demand charge mitigation is almost never one of them.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#15

Re: Single Phase Pump vs Three Phase Pump

07/17/2015 12:48 PM

We will just have to couple a single and three phase motor face to face and see who wins.

__________________
CRTL-Z
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#19

Re: Single Phase Pump vs Three Phase Pump

07/17/2015 11:02 PM

Dear Mr. cckla,

Single Phase Motor means higher current for the same power and hence wire/conductor size will be bigger than the 3 phase, Voltage drop will be Higher, Starting Current will be further high. Starting device - like capacitor connected - fault means you cannot start the motor since the single phase motor cannot start on its own. since the Torque is REVERSED INSTANTLY DEPENDING UPON THE FREQUENCY. As mentioned motor is costlier.

Three phase means, especially Star connected (where the Line Current = Phase Current), conductor/cable size required will be smaller, Voltage drop is Smaller, Starting current will be relatively lesser than Singl Phase Current. TORQUE REVERSAL DOES NOT OCCUR.

DHAYANANDHAN.S

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#20

Re: Single Phase Pump vs Three Phase Pump

07/18/2015 5:00 AM

If you have 3-phase supply available I see next to no reason not to use it, for reasons given in #14 by Yahlasit, and others.

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#22

Re: Single Phase Pump vs Three Phase Pump

07/19/2015 3:03 PM

If three-phase power is not available, the great advantage of a single-phase pump is that it will work on a single phase supply.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#23
In reply to #22

Re: Single Phase Pump vs Three Phase Pump

07/19/2015 5:19 PM

Single phase will work on a 3 phase also, just drop a leg

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#24
In reply to #23

Re: Single Phase Pump vs Three Phase Pump

07/22/2015 10:14 AM

But 3-phase won't work on a 1-phase supply . Not unless he installs an inverter, which might not be a bad idea.

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#25
In reply to #24

Re: Single Phase Pump vs Three Phase Pump

07/22/2015 10:25 AM

correct'o mundo

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply