I am doing total dc load calculations. I thing according to the total of max amp load will exceeds to the size (capacity of )battery provided (12 dc battery).
Without purchasing an extra battery, do you have any advice that helps me to keep this 12 dc battery enough for my whole dc load.
Re: when total dc load exceede to the size of batteries
07/18/2015 5:59 PM
How did you figure max amp load?
If your figures are correct, you must reduce the load.
07/18/2015 7:42 PM
when you say reduce the load, do you mean that if I have an electrical equipment required to be in the design, should I omit that equipment. I am not clear on this
07/18/2015 7:48 PM
the load, not the battery, what are you operating and for how long? 2 seconds, a day a week? what is your expected amp draw from this motor hear element, fan, whatever?
07/18/2015 7:53 PM
I am estimating number of hours which will be 24hrs because most of the loads might be used 24 hours except the light that no need them during day time, but only for 12 hours.
I am don't like to provide you the type of load, but this is for 24 hours load and all they are dc equipment. no ac involve. I am using 12v dc battery for this total load.
07/18/2015 7:55 PM
you're wasting our time, bye
Re: DC load exceeds battery capacity
07/18/2015 6:17 PM
Increase the efficiency of your load....
07/18/2015 6:36 PM
do you have any advice that helps me to keep this 12 dc battery enough for my whole dc load.?
No advice. Need additional batteries.
07/18/2015 6:52 PM
Please present some numbers.
07/18/2015 7:40 PM
ok, I will tell you what I did, and please correct me if I am wrong.
Total Amp Hour needed = (Total continues max amp load = 60 amp) + (10% of Largest intermittent amp load =1 amp)
then
20% of (total amp hour) =12.2 amp-hrs
12.2 + 61=74 amp-hrs
from this number I decide the batteries capacity. so I use 40% discharge as the limit
I have to choose the battery so it does not discharge below %50 of its capacity
so
74 amp-hrs/0.4 = 185 amp-hrs and from their I use a battery rated higher than this number
I think I am not clear above, but let me know because I am confused
07/18/2015 11:20 PM
That mostly makes sense. How did you arrive at the initial 60A of load?
07/19/2015 12:35 AM
60A is my total max load of all dc equipment that considered as continues only. manufacturer of that equipment provide a max power (divided Pmax by 12vdc) or provide max load on the device itself. Then I added all equipment's max load together.
07/19/2015 2:09 AM
That is reasonable also. However, one thing that may help you is that not all of this equipment might be demanding maximum load all the time. You should also consider non-concurrent loads, and diversity factors even for those loads that might be sometimes, but not always, active at once. Your local regulations may specify some of these numbers.
07/19/2015 2:07 PM
Assuming your rough estimate of 185 ah per hour to a 50% discharge point to be reasonable to run that for 24 hours you would need a 4440 AH battery bank or roughly 45 100ah 12 volt deep cycle batteries.
Now how do you plan to recharge them?
07/19/2015 2:36 PM
how are you arriving at a deep cycle battery at all with almost no parameters given at all?
07/19/2015 2:46 PM
The same way we always answer technical questions for the clueless. We assume at least a half dozen parameters from when we had to do something that resembles the original question and then come to a conclusion with no regards to cost. The fun part is that we never explain our assumptions.
07/19/2015 3:19 PM
The un-fun part is that most clueless (Anonymous Posters) do no research, or even a simple Google search before coming here to ask for an undeserved education on painfully simple subjects.
07/19/2015 4:57 PM
I read the whole thread.
His load is at most 60 amps on a 12 volt system. He figures a 20% safe overhead on that and wants to run it for up to 24 hours at a time without discharging the batteries below 50%.
The rest was just simple math.
07/19/2015 12:11 AM
you are assuming n motor starting load or CB motor drive?.
pnaban
Reply Score 1 for Off Topic
07/18/2015 7:13 PM
more info
07/18/2015 7:45 PM
What type of info to provide you. I provided some numbers above
07/19/2015 12:10 AM
The manufacturer usually has the AH rating on the battery, usually rated at 20 hrs....I would go with a deep discharge type...first you must determine your AH draw per hour...Let's say 4 amps...for 24 hrs would be 184 AH rating at 20 hrs....
H is the rated discharge time, in (hours).
C is the rated capacity at that discharge rate, in (Ampere-hours).
I is the actual discharge current, in (Amps).
k is the Peukert constant, (dimensionless).
t is the actual time to discharge the battery, in (hours).
To find the Peukert constant, we must have two different ratings from the manufacturer. Most manufacturers will give a 20 hour rate AH rating as the standard rating, and also a 10 hour rate and possibly a 100 hour rate. With two of these, you can figure out Peukert's number using the simple ( maniacal laughter) formula below.
n = Peukert's constant
C1 = Capacity at 1st rate
C2 = Capacity at 2nd rate
R1 = hour rate at 1st C rating
R2 = hour rate at 2nd C rating
Or, you can use our calculator and avoid a headache. Find it here.
http://www.batterystuff.com/kb/tools/calculator-sizing-a-battery-to-a-load.html
http://www.batterystuff.com/kb/tools/math-behind-the-magic.html
http://www.wholesalesolar.com/solar-information/deep-cycle-battery-info
Reply Good Answer (Score 4)
07/19/2015 12:31 AM
That "maniacally laughable" formula is pretty much the same as LMTD formulas used for heat exchange calculations. Some of the deep principles cross over multiple disciplines.
07/19/2015 11:53 AM
Excellent reply!
Good Answers: 42
07/19/2015 8:54 AM
See[for instance]:
http://www.smartgauge.co.uk/peukert2.html
https://en.wikipedia.org/wiki/Peukert%27s_law
http://planetcalc.com/2283/
http://www.ajdesigner.com/phpbatterylife/battery_life_peukert_number_time.php
Julius
Re: When Total DC Load Exceeds the Size of Batteries
07/20/2015 12:56 AM
Battery capacity SHOULD be sized to deliver the reqd. load. It is NOT the otherway round because battery is REQUIRED to deliver the load.
In your case, if you are unable to reduce the load, then battery BACKUP TIME for the given load WILL REDUCE.
07/20/2015 10:22 AM
a 20Ah battery capacity is rated at 87.5% depletion. You need to up your battery capacity. Check the datasheets on your battery. It will show you a curve of what your battery voltage will be at the rated discharge time. At 87.5% for a sealed lead acid battery at a dishcarge rate of .2C you should be about 10.5 VDC. For NiCAD, NIMH or other dry cell rechargables it is around 10 VDC. At a higher discharge rate like .4C or .5C (C=battery capacity) your battery voltage gets worse on a variable scale.
Also, depleting your battery to 50% or lower will seriously decrease the life of your battery and will require longer charge times which, if they aren't met you will have trouble even getting a usable 12V our of your battery.
Conclusion, redo your calculations based on 87.5% battery capacity. Either increase your capacity or add batteries.