RCCB - Nuisance Tripping - Lighting Circuits (Wet Area Service)

07/19/2015 7:32 AM

There is nuisance tripping (RCCB TRIPS) occur in our landscape lighting circuits. Existing RCCB is 40 amps 100ma which connected to dimmer panel(3phase). Inside the dimmer there are 12 circuits which is connected to LED lights through 10A individual breaker and each breaker have load of 10 to 15 lights. RCCB trips only, when we switch on all together by dimmer keypad. If we switch on individual breaker there is no tripping.

Alo please be informed that landscape is very wet and cable (weather proof cable) directly laid on soil. So kindly advice which type of solution will be better to solve the same.

1. Replacing 100mA RCCB with 300mA RCCB

2. Splitting the load from one RCCB to 4 RCCBs (Each RCCB with 3 Circuits)

3. Replacing RCCB with an ELR + CBCT

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#1

Re: RCCB - Nuisance Tripping - Lighting Circuits (Wet Area Serves)

07/19/2015 11:08 AM

Do an insulation test on cables outgoing from RCCB

__________________
pnaban
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: RCCB - Nuisance Tripping - Lighting Circuits (Wet Area Serves)

07/19/2015 1:00 PM

"10 to 15 lights" or 10 to 15 strings of lights.

Have you measured amp draw of each circuit? Total load?

What have you done, so far?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: RCCB - Nuisance Tripping - Lighting Circuits (Wet Area Serves)

07/19/2015 2:27 PM

From the information presented, there would appear to be a problem with the dimmer. Rectify it before re-energising.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: RCCB - Nuisance Tripping - Lighting Circuits (Wet Area Serves)

07/19/2015 2:42 PM

Use an extermination service to get rid of the gophers.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 258
Good Answers: 2
#5

Re: RCCB - Nuisance Tripping - Lighting Circuits (Wet Area Service)

07/19/2015 11:47 PM

Most of the LED fixtures have AC tyo DC conversion circuits with an electrolytic capacitor. All capacitors act as short circuit until it gets fully charged. Time cosntant depends on the circuit. Hence if all circuits are to be switched on simultaneously, the intial charging current will be high and may be the cause for your RCCB tripping. Reducing number of LED fixtures per RCCB will certainly help. You could also buy slower response RCCBs- which can withstand short time surges.

Register to Reply
Guru

Join Date: Dec 2010
Location: 1° North Singapore
Posts: 568
Good Answers: 17
#6

Re: RCCB - Nuisance Tripping - Lighting Circuits (Wet Area Service)

07/21/2015 10:52 AM

Your problem looks very much like due to turn on surge, as XYZ has pointed. It does not look like it has anything to do with earth leakage , so your solution 1 & 3 are out. Solution 2 may work as it reduces the turn on surge.

__________________
Sharing knowledge is one thing that defies basic arithmetic logic --- the more you share, the more you get!
Register to Reply
Participant

Join Date: Nov 2008
Posts: 4
#7

Re: RCCB - Nuisance Tripping - Lighting Circuits (Wet Area Service)

07/22/2015 3:14 AM

Thanks for your comments. I insisted our people to replace the RCCB by ECR with CBCT. I will update you the same once it done.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#8
In reply to #7

Re: RCCB - Nuisance Tripping - Lighting Circuits (Wet Area Service)

07/22/2015 3:18 AM

Please also update us on the gophers.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#9
In reply to #7

Re: RCCB - Nuisance Tripping - Lighting Circuits (Wet Area Service)

07/25/2015 4:53 AM

CBCT+ELR is RCCB. Solution-2 reduces the no. of lights in each circuit and thus the inrush current when switched-on.

100mA RCCB is important for human safety and any attempt to increase the leakage current rating or add a delay will make the system unsafe and you are risking electrocution.

__________________
Raghunath
Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

bravo88 (1); lyn (1); pnaban (1); PWSlack (1); raghun (1); Tornado (2); trajeshkannan (1); xyz (1)

Previous in Forum: When Total DC Load Exceeds the Size of Batteries   Next in Forum: Power Backup For Home Server?

Advertisement