Shaft Current In VFD Operation - Insulation Bearing

08/07/2015 4:36 AM

We all know that the Motors applicable for VFD Operations - the Shaft Current is a problem affecting the Bearing and results in Bearing Failure.

When we installed a 30 HP VFD motor-drive system, the manufacturer advised to use INSULATED BEARING or a perfect Bearing Insulation even for 5 H.P. Motor.

If you open the link given below here, http://electrical-engineering-portal.com/benefits-and-potential-drawbacks-of-vsds

you will find a statement as

"Insulated non-drive-end bearings are recommended on all motors over 100 kilowatt (kW) output rating." which indicates Bearing Insulation is required for H.P of 100 and above".

I want to KNOW from the CR4 MEMBERS to share their knowledge and experience about this topic. Further what will happen if conventional bearinfs are used in VFD APPLICATION.

DHAYANANDHAN.S

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#1

Re: SHAFT CURRENT IN VFD OPERATION - INSULATION BEARING

08/07/2015 5:20 AM

Bearing damage can occur if the fast switching VFD IGBT circuitry produces stray currents in the rotor. When the load Z is higher than the line Z, then current is reflected back to the VFD causing quite high voltage spikes to be induced in the rotor and stator metal.

The resultant stray currents in the stator are not a large problem as it is solidly earthed - although they can damage insulation, but those in the rotor must find their way to earth, and this is usually via the bearings.

Resultant arcing at the ball/raceway contact points in the bearing cause abnormal wear and pitting and also degradation of the lubricant which dramatically reduces effective bearing life.

Bearings are designed to operate with a thin oil film between contact surfaces, but once the dielectric properties of that oil is compromised, then current will flow, burning the oil and pitting the metal surfaces.

One problem with the use only of insulated bearings is that the shaft voltages are not mitigated and can eventually find other paths to earth (an attached appliance which can then suffer bearing damage) or even damage the insulated motor bearings if no other path is available. Another problem is the contamination of the bearing insulation over time, allowing the currents to flow through them.

You can safely use uninsulated bearings where these VFD drives are in operation provided you give those stray currents a more attractive earth path than that of the bearings A shaft grounding ring (SGR) on the rotor shaft is such a method, and is generally a cheaper and more effective option than insulated bearings.

Some of these grounding rings employ microfibre contact technology which provides a much greater earth contact area, wears very little, and is more effective even than insulated bearings.

Best practice normally recommends combining insulated bearings and a grounding ring for motors over 100Hp.

Failure to use effective stray current and common mode voltage protection/earthing when employing VFDs can result in bearings achieving less than 1% of their expected service life

Register to Reply Good Answer (Score 3)
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#2
In reply to #1

Re: SHAFT CURRENT IN VFD OPERATION - INSULATION BEARING

08/07/2015 7:27 AM

Thank you Mr. spades for sharing your experience and advise on the subject.

Quite Intresting to me to learn "shaft grounding ring (SGR) on the rotor shaft"

Again thanks, a lot.

DHAYANANDHAN.S

Register to Reply
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#4
In reply to #1

Re: SHAFT CURRENT IN VFD OPERATION - INSULATION BEARING

08/07/2015 5:30 PM

Thanks for sharing this information.

Recently saw failure of bearing on 900L/sec pump running on VFD. The pump supplier(matched motor and pump combination) suggested the failure related to delay between purchase and install.

Failure was detected and forecast by vibration monitoring before significant other issues developed.

I will re-visit the failure investigation records and motor/pump design spec sheets to see whether this may have contributed.

__________________
Just an Engineer from the land down under.
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#3

Re: Shaft Current In VFD Operation - Insulation Bearing

08/07/2015 2:03 PM

In addition to what has already been stated I would add:

The bearing insulation must be capable of withstanding the highest level of induced voltage without suffering any leakage otherwise the bearing and/or the shaft will be damaged from arcing between the shaft and bearing contact surfaces.

If using the shaft grounding brush or braided shunt you must be sure that the shaft contact area as well as the brush/shunt material is cleaned regularly on an interval that prevents oxidation and/or other contamination from occurring and rendering the system inoperative.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#5

Re: Shaft Current In VFD Operation - Insulation Bearing

08/07/2015 10:45 PM

Thank you Mr.JRaef, for sharing your experience.

dhayanandhan.s

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#6

Re: Shaft Current In VFD Operation - Insulation Bearing

08/08/2015 3:20 AM

There was a fairly recent blog that covered all this in some excellent detail, I learnt a lot!

You should search on CR4 for that....and any others.....

Best of luck.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#7

Re: Shaft Current In VFD Operation - Insulation Bearing

08/08/2015 4:01 AM

you commented on my post of a few weeks ago, regarding EDM and VSD output harmonics

Medium Voltage Variable Speed Drive Harmonics

here's the link to follow

__________________
The square root of nothing is what you make it!
Register to Reply
Active Contributor

Join Date: Sep 2015
Posts: 12
#8

Re: Shaft Current In VFD Operation - Insulation Bearing

09/09/2015 9:29 PM

Yes, better use Insulated bearings in VFD motors. China bearing manufacturers are producing insulated bearings with very nice price, which will offer another choise for this very purpose. Can check www.ninestarbearing.com to learn more.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#9
In reply to #8

Re: Shaft Current In VFD Operation - Insulation Bearing

09/09/2015 9:53 PM

SPAM!!!

Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Andy Germany (1); brich (1); dhayanandhan (2); Just an Engineer (1); Lisa Chen (1); lyn (1); SHOCKHISCAN (1); spades (1)

Previous in Forum: Alternator   Next in Forum: Earth Leakage Relay

Advertisement