Bypass Arrangement for Busbars in Substation

08/09/2015 11:10 PM

Hello sirs,

I was referring to double bus systems and main and transfer bus systems. I came to conclusion that bypass arrangement exists in main and transfer bus systems so that supply from line side can be transferred to feeder side.

Does bypass arrangement also exists in double bus systems?

Regards,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Bypass arrangement for busbars in substation.

08/09/2015 11:20 PM

Both paragraphs are equally amazing.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#2

Re: Bypass arrangement for busbars in substation.

08/10/2015 2:09 AM

2 things, 1) 'Hello sirs,' your insulting to the fine knowledgeable women that also enjoy this forum, 2) Illiterate drivel on your part

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Reply Score 1 for Off Topic
2
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Bypass arrangement for busbars in substation.

08/10/2015 2:23 AM

Refer to Google.

" bypass arrangement in double bus systems"

Reply Good Answer (Score 2)
2
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#4

Re: Bypass Arrangement For Busbars In Substation.

08/10/2015 9:21 AM

Yes, a double bus system can be configured with a bypass or a bus tie connection and/or multiple switching arrangements.

Normally this configuration is used to allow connection of two separately fed buss systems together so that when loss of power to either occurs, the tie breaker closes so that all critical power to the process is not lost.

In some cases the two busses are left connected together at all times to share or balance total load during normal operation and the tie breaker trips open only when required to prevent overloading of either bus feeder.

There are standard tripping and transfer electrical control schemes which are required in order to prevent tying the two busses together unless correct synchronization is present or one of the buses has lost power.

In a nutshell; It is possible to install whatever bus configuration needed to meet a process needs as long as the correct tie breaker control scheme is implemented to protect all of the breakers, all busses, and the equipment being serviced.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Reply Good Answer (Score 2)