Running A 11KW 2 Pole Inverter Duty Motor At Low Speed

08/10/2015 7:34 AM

Dear Friends;

We have 11KW, 2pole, 400V inverter duty motor working at a take up conveyor of a single facer unit of a Corrugator machine. A separate cooling fan is with the motor. Normally motor works within 1700-2300rpm. For some reasons, we want to run the motor at 300-450rpm for some days. Kindly suggest if it is okay to run a 2pole motor at low speed? Normally motor current remains at 60%.

__________________
Don't assume any thing, always check/ask and clear yourself
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#1

Re: Running A 11KW 2 Pole Inverter Duty Motor At Low Speed

08/10/2015 9:25 AM

I don't see any real issues with the speed reduction but I do have a few questions:

  • What is the motor RPM on the data plate?
  • Is the motor overheating?
  • Is the inverter overheating?
  • Is this a common practice of using the motor VFD to switch from ~2000 RPM to ~ 325 RPM?

Good luck

Bryan

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Running A 11KW 2 Pole Inverter Duty Motor At Low Speed

08/10/2015 1:31 PM

Well, it says in the title that it is 2 pole, then 400V which implies 50Hz, so the synchronous speed would be 3000RPM, slip speed probably around 2750.

With a separately cooled motor, I see no issue whatsoever. That's exactly what VFDs are for.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: Running A 11KW 2 Pole Inverter Duty Motor At Low Speed

08/10/2015 7:54 PM

And even more so, that is what the separate cooling fan is for.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Mar 2011
Location: oz
Posts: 252
Good Answers: 10
#4

Re: Running A 11KW 2 Pole Inverter Duty Motor At Low Speed

08/10/2015 11:10 PM

You may need to see you data sheets regarding torque for that motor, 300rpm about 5Hz may not be able to deliver the same torque at 50Hz.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5
In reply to #4

Re: Running A 11KW 2 Pole Inverter Duty Motor At Low Speed

08/10/2015 11:26 PM

Good point; on a conveyor, full (or nearly full) torque will be needed even at low speed. Some motors and VFDs can do that, but not all.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Nov 2011
Location: NASA-Glenn Research Center, Cleveland Ohio
Posts: 389
Good Answers: 17
#6
In reply to #5

Re: Running A 11KW 2 Pole Inverter Duty Motor At Low Speed

08/11/2015 8:47 AM

use a two speed transmission to slow down speed when needed.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7
In reply to #6

Re: Running A 11KW 2 Pole Inverter Duty Motor At Low Speed

08/11/2015 8:54 AM

Maybe, or maybe not.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

eltech (1); JRaef (1); Original_Macgyver (1); setlock77 (1); Tornado (3)

Previous in Forum: Bypass Arrangement for Busbars in Substation   Next in Forum: Optimum Binary Signal One Can Transmit on a 1 Hz Frequency

Advertisement