5KV Megger Shows Continuous Variation In The Resistance Value.

08/13/2015 1:53 PM

I need to understand what is causing this phenomenon. the data is given below:

TimeResistance
1min17.4
4min34.8
10min15.8
14min43
20min10
24min28
29min8.7
30min5.65
34min9.5
36min16
40min8
43min6.5
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#1

Re: 5KV Megger shows Continuous variation in the resistance value.

08/13/2015 2:04 PM

Humidity?

Are you breathing anywhere near the test set up, or, is it completely isolated in a controlled environment?

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#2

Re: 5KV Megger shows Continuous variation in the resistance value.

08/13/2015 2:20 PM

It appears the PI value of the test is .90804?

Possible causes:

Loose test connection?

Poor quality or unstable power supply to test set?

Incorrect test voltage value?

Incorrect test procedure or test equipment for application?

Inductance? (Adjacent to HV and/or high current carrying conductors or cables?)

Capacitance? (Long length of cable(s)? Filter or PF capacitors connected?))

Surge arrestors and/or other protective devices still connected in the system when test voltage is applied?

Moisture in cable/equipment?

High resistance carbon fault(s)?

Leaking/failing conductor insulation?

Leaking/failing cable/equipment conductor termination?

Faulty/Failing test equipment/set?

Hope this gives you an idea where to look.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Score 1 for Good Answer
Participant

Join Date: Aug 2015
Posts: 3
#8
In reply to #2

Re: 5KV Megger shows Continuous variation in the resistance value.

08/14/2015 12:29 AM

It appears the PI value of the test is .90804? YES
Possible causes:
Loose test connection? NO
Poor quality or unstable power supply to test set? MAY be
Incorrect test voltage value? NO
Incorrect test procedure or test equipment for application? NO
Inductance? (Adjacent to HV and/or high current carrying conductors or cables?) YES
Capacitance? (Long length of cable(s)? Filter or PF capacitors connected?)) it is jus a jumper wire connecting two MV (11KV) panels of length 15 meter.
Surge arrestors and/or other protective devices still connected in the system when test voltage is applied? NO
Moisture in cable/equipment? if there is moisture in the cable how can we remove it besides both ends have been prepared with raychem heat shrink kits
High resistance carbon fault(s)? Its a brand new cable.
Leaking/failing conductor insulation? if its the case, dun u think the resistance value should be on the lower side instead of varying continuously.
Leaking/failing cable/equipment conductor termination? May be
Faulty/Failing test equipment/set? tested with two different megger sets.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#11
In reply to #8

Re: 5KV Megger shows Continuous variation in the resistance value.

08/14/2015 10:00 AM

Poor quality or unstable power supply to test set? MAY be

If the power supply to the test set is not stable the readings will not be consistent and will not be dependable. You must stabilize the test set power supply by using a constant voltage source such as a UPS but make sure the ground circuit is intact and functional whatever system is used.

Inductance? (Adjacent to HV and/or high current carrying conductors or cables?) YES

You may have to de-energize the other conductors in the area long enough to conduct the testing.

Leaking/failing conductor insulation? if its the case, dun u think the resistance value should be on the lower side instead of varying continuously.

If you examine your test results the numbers are cycling from low to high then back to low which is indicative of arcing occurring through weak insulation, water, or carbon left over from a fault. Improper terminations can also display this same pattern.

Leaking/failing cable/equipment conductor termination? May be

Is this new cable(s) or recently repaired cables?

Are the readings the same on all three phase conductors? If so; more than likely the cable terminations are either the wrong type for the cable, or they have been improperly installed.

It is very important that you determine what type of cable you are dealing with, get all pertinent information on the type of terminations and the correct procedure for installing the terminations onto the cable then inspect each and every termination to verify if everything is in order.

I have observed the same test pattern on cables that have semi-conductor layers which were not cut back far enough resulting in break-over arcing during testing and/or operation.

Knowing and following the cable manufacturer's specific instructions is critical to the operation and longevity of the cable(s) as well as the equipment it is attached to.

Is it old cable that has been in service for a long period of time and suddenly failed?

If so; You more than likely have water impingement (wet cable interior) and/or have suffered a fault which has left enough carbon at the fault site(s) to allow arcing to occur during testing.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Score 1 for Good Answer
Participant

Join Date: Aug 2015
Posts: 3
#12
In reply to #11

Re: 5KV Megger shows Continuous variation in the resistance value.

08/14/2015 11:23 AM

Thanks for providing the valuable inputs. i will definitely take these into consideration. one more thing i want to confirm is the PI test is meant for motors and generators and not for cables. here we are testing MV (11KV) cable before going for Hi-Pot test to ensure everything is okay.

Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#3

Re: 5KV Megger shows Continuous variation in the resistance value.

08/13/2015 3:41 PM

It was not specified, but if the device under test is a stator, it started out wet and is drying, you will get fluctuations as it dries.

Another question: Does the time represent a momentary test or the duration of each consecutive test?

__________________
CRTL-Z
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9913
Good Answers: 1141
#4

Re: 5KV Megger shows Continuous variation in the resistance value.

08/13/2015 4:13 PM

With resistance this high, a very tiny bit of leakage results in a large numerical variation. (10 GΩ in parallel with 35 GΩ gives 8 GΩ). So I think anything in the environment could give you this much variation. Is there any historical data you can look at? What is your requirement?

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5

Re: 5KV Megger Shows Continuous Variation In The Resistance Value.

08/13/2015 6:20 PM

I would say off hand a bad connection, high moisture, or varying temperature, but I would go by the lowest reading...I would review the testing procedure and check for proper methods first though....

https://www.instrumart.com/assets/Megger-insulationtester.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
4
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#6

Re: 5KV Megger Shows Continuous Variation In The Resistance Value.

08/13/2015 7:06 PM

I don't find that unusual at all. If you are meggering at 5 kV, the numbers can vary all over the place with just slight environmental changes. Don't even breathe on it. I see stuff like that all the time. In most cases we want to see values higher than some value like 1 Gig and we're happy.

You may need to use guards around the measured device to prevent surface charge migration from affecting your measurement. The manual that comes with your megger will explain this nicely.

Register to Reply Good Answer (Score 4)
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#7

Re: 5KV Megger Shows Continuous Variation In The Resistance Value.

08/13/2015 8:38 PM

5KV Megger measurement is sensitive even to small environmental variations and usable ONLY on equipment rated for this testing. Now assuming that this is your case, is your Megger instrument AND cabling verified to be in good working order, not to mention clean and dry as it should, and its batts in good shape? Because some 8:1 resistance ratio is a little odd, and no matter how bad some connection is or someone is breathing on it, it cannot produce that result, at this voltage, without you hearing the produced... sparks that is. S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#9

Re: 5KV Megger Shows Continuous Variation In The Resistance Value.

08/14/2015 3:10 AM

My first thought, as someone else here, is that you are breathing too close to the equipment......or someone is!!

My second thought is why worry? that is spectacularly high insulation values....!!!

In my day, seeing even 100 Meg Ohms would have been considered wonderful!!

I have to admit that I have never had a device (Megger) that could indicate even a single "GΩ" acurately, let alone the values you are looking at!!!

....don't times change!!!

I have never, even see a 5KV Megger by the way......

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#10
In reply to #9

Re: 5KV Megger Shows Continuous Variation In The Resistance Value.

08/14/2015 9:20 AM

They've been available (in hand-held models) for many years now, from Megger Corp. and other good test instrument manufacturers (AEMC, etc.). 10kVDC and 15kVDC meggers are not unusual these days. Many of them run off a handful of AA cells, and will give you several years of test usage from that set of batteries. Here are some example links:

http://megger.com/us/products/ProductDetailsBySubGroup.php?PSGC=I105&BS=I

http://www.aemc.com/

http://www.fluke.com/Fluke/tten/Insulation-Testers/Fluke-1555-1550C.htm?PID=69212

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#13

Re: 5KV Megger Shows Continuous Variation In The Resistance Value.

08/14/2015 2:24 PM

5kV is not a big problem but G-Ohms sure is of problem in measurement. Measurement cable insulation may be much lower.

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14

Re: 5KV Megger Shows Continuous Variation In The Resistance Value.

08/17/2015 4:52 PM

The thing that is causing the phenomenon is something called "worry". So stop doing that immediately.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#15
In reply to #14

Re: 5KV Megger Shows Continuous Variation In The Resistance Value.

08/19/2015 11:53 PM

Artefact in measurement is often like a discovery only to collapse one day and end up in worry.

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Register to Reply
Register to Reply 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

adils02 (2); Andy Germany (1); Brave Sir Robin (1); PeterT (1); PWSlack (1); Randall (1); Rixter (1); SHOCKHISCAN (2); Shyam (2); SimpleMind (1); SolarEagle (1); Unredundant (1)