240V Residential Circuit into 347 Baseboard Heater

08/27/2015 10:34 AM

Wondering if this is possible?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#1

Re: 240V Residential Circuit into 347 Baseboard Heater

08/27/2015 11:42 AM

No!

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: 240V Residential Circuit into 347 Baseboard Heater

08/27/2015 12:20 PM

This might be possible, but some rewiring and/or redesign of the safety and resistance factor of the elements might be necessary....a qualified electrician could make it work but it might cost more than just buying a new heater designed for the voltage present....then again it might be a simple fix...it all depends on the design of the heater...

http://electrical-engineering-portal.com/resistive-heating-explained-in-details

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Participant

Join Date: Aug 2015
Posts: 2
#3
In reply to #2

Re: 240V Residential Circuit into 347 Baseboard Heater

08/27/2015 12:38 PM

Thanks. i will look at the configeration and see what it looks like.

Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#9
In reply to #3

Re: 240V Residential Circuit into 347 Baseboard Heater

08/28/2015 1:18 AM

What exactly is a "347 Baseboard Heater" Do you mean a baseboard heater designed for operation from 347 Volts? (That seems to be what all the other posts have assumed) I've not come across 347 Volts as a standard voltage, but of course there are lots of places I haven't visited.

Or is this a heater with two elements in a 3, 4 ratio to give a total of 7?

Or is 347 a model number?

Or something else?

More specific information will usually lead to a more appropriate answer.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#11
In reply to #9

Re: 240V Residential Circuit into 347 Baseboard Heater

08/28/2015 9:37 AM

347 Volts is common for baseboard heaters. Don't ask me why.

I think the rating is 277-347V, among other more common voltages.

Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#13
In reply to #11

Re: 240V Residential Circuit into 347 Baseboard Heater

08/28/2015 10:44 AM

Thanks. All of my industrial experience has been with 480 Volt systems or lower. 347 V* √3 = 601 V, so one leg of a 600 V 3Ø system to neutral would produce that voltage.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#15
In reply to #9

Re: 240V Residential Circuit into 347 Baseboard Heater

08/31/2015 1:47 PM

In Canada 600Y/347 V is a common three phase voltage. It is very common for 347 V to be used for lighting in large industrial facilities and for baseboard heaters in large apartment buildings.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#19
In reply to #15

Re: 240V Residential Circuit into 347 Baseboard Heater

09/01/2015 12:46 AM

Thanks! Obviously I had not experienced that system... Now I know!

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#4

Re: 240V Residential Circuit into 347 Baseboard Heater

08/27/2015 12:42 PM

Yes it will work but at about half power.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7
In reply to #4

Re: 240V Residential Circuit into 347 Baseboard Heater

08/27/2015 3:58 PM

While I ignore you most of the time (ignorance is bliss) I'm with you on this one.

Nof60 has a point about nameplate information and money grabbing insurance companies and their lawyers.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: 240V Residential Circuit into 347 Baseboard Heater

08/27/2015 1:38 PM

Follow the instructions that came with it.

If in doubt, consult a qualified Electrician. Make sure the installation is documented for domestic insurance reasons.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#6

Re: 240V Residential Circuit into 347 Baseboard Heater

08/27/2015 3:19 PM

As a safety regulator I must point out that...

While doing as you have asked will produce heat (as TCMTech pointed out at a reduced output rate), there is a possible legal aspect that may impact you in a negative fashion (think insurance) should something happen.

Electrical equipment is certified to function at specific voltages. If this heater is not certified to work on a 240V source, using it on a 240V source would be against the code in both Canada and the US. Just enough of a reason for an insurance carrier to refuse a claim.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Good Answer (Score 2)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#8
In reply to #6

Re: 240V Residential Circuit into 347 Baseboard Heater

08/27/2015 7:06 PM

I'm curious to know what bona fide safety issue would occur from running a heater at less than rated voltage.

Of course, lawyers and insurance companies can readily confabulate phony issues.

And also, of course, motors are different, because subnormal voltage can lead to overcurrent.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#10
In reply to #8

Re: 240V Residential Circuit into 347 Baseboard Heater

08/28/2015 9:22 AM

If there are any safety mechanisms in the heater and they require the full voltage to trip, it may not trip if there is some sort of electrical fault.

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#16
In reply to #8

Re: 240V Residential Circuit into 347 Baseboard Heater

08/31/2015 1:51 PM

Tornado... I did not say there was a safety issue, only a possible legal one. As an inspector I would have to fail this installation unless the unit had a slash voltage rating of 347/240 V.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#17
In reply to #16

Re: 240V Residential Circuit into 347 Baseboard Heater

08/31/2015 3:09 PM

I agree with your comment.

When I was a General building Contractor, I would not short cut anything and if the electrical baseboard specified 347 VAC then I would feed it 347 VAC not 220 VAC or 240 VAC because I know the inspector would most likely red tag that item and possibly shut me down until it was rectified and the proper voltage applied!

Also, if there was an issue with the heater and it fried or caused a fire, I'm not going to put my company or insurance on the line for a rookie short cut!

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
3
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#12

Re: 240V Residential Circuit into 347 Baseboard Heater

08/28/2015 10:30 AM

Radiant heating element only or forced air?

Programmable thermostat? Or standard bimetallic element type?

If it is just a radiant heating element type with a standard non-programmable bimetallic thermostat it will work just fine but the heat output will be reduced proportionately and the temperature recovery time curve will be longer for the house or room to reach setpoint.

Much of the equipment sold today is designed to operate at a very broad voltage range and either has multiple voltage tap connections or utilize automatic voltage sensing.

There is usually a minimum & maximum voltage rating stamped or labeled on the equipment at or near the connection box as well as a recommended operating voltage.

Using the equipment at rated voltage or at a lesser value within stated acceptable design limits does not pose a safety risk to occupants or to the equipment.

A call to the manufacturer technical support group should answer any questions you have.

My 30+ year old home up North has 240/347 VAC radiant baseboard heaters and they operate well on the 220VAC supplied by the local power company.

In fact their operating life has been/is dramatically extended due to the lower applied voltage and lower operating current. (All original equipment that came with the house and no heater or thermostat replacements in my 20 + years of ownership.)

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Good Answer (Score 3)
Power-User
Ireland - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: Aug 2007
Location: Northern Ireland
Posts: 197
Good Answers: 17
#20
In reply to #12

Re: 240V Residential Circuit into 347 Baseboard Heater

09/10/2015 8:08 AM

Phew just what I was going to write saved me the time and typing so GA :-)

__________________
I love deadlines; I love the whooshing sound they make as they pass by. - Douglas Adams
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#14

Re: 240V Residential Circuit into 347 Baseboard Heater

08/28/2015 8:28 PM

Resistance heating is just about the resistance. There is no "347V heater" except that the RATING of watts and resultant BTUs of heat is based on applying 347V. You can apply any voltage to is BELOW that value, as long as you accept that it will NOT produce the same amount of heat. Ohm's Law: P (watts) = V2/R . So if you have a heater rated for 1000W at 347V, that means R = V2/P, so 120.409 ohms. If you reduce the voltage to 240V, R is still 120.409ohms, so then P = 487.37w. That's the "roughly half" mentioned earlier.

There is absolutely NOTHING unsafe about this, it is done ALL THE TIME. One major reason in the heating element world is to reduce the watt density of a heater element, meaning if I have an element that must fit in a specific spot, but puts out too much heat and will scorch the product being heated, I use a higher voltage rating on the heater so that the watts / square inch is lower and thereby the surface temperature is lower. The watts and total heat is lower as well of course, so it takes longer for the product to heat up, but it doesn't scorch it. Pasteurizing milk is a prime example of this..

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#18

Re: 240V Residential Circuit into 347 Baseboard Heater

08/31/2015 4:41 PM

Whether right or wrong... the electrical safety system in place in North America (at least in Canada and the USA), consists of 3 parts.

1) The installation codes...

2) The product standards...

3) The 3rd party product certifiers...

The premise is that when, equipment that is certified to the correct product standard by a registered and qualified 3rd party certifier is installed by a trained and qualified installer to the adopted installation code, an inherently safe installation is the result.

This system has served NA very well for many many years and is IMHO the best system for regulating electrical safety in the world. When one component of the three is missing... all bets are off.

Doing less than this enters into the realm of risk management.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Register to Reply 20 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: