Need Detail on European Plug Configurations for Small Appliances

09/02/2015 12:08 PM

Guys... I need to understand the wiring of standard European small applicance receptacles.

The voltage is 250V at 50Hz, correct?

How many pins in a standard receptacle and how are they refered to?

As to the conductors that delivers power to a device and returns it back to the source, what do you call them? A hot and a neutral?

Is the neutral bonded to the case of an appliance inside that appliance?

You use a bonding conductor, correct? Do you call it a bond or a ground conductor?

Is the bonding conductor bonded to the case of an appliance inside that appliance?

How exactly does your RCDs work, what conductors do they monitor and how?

How different is it, from a configuration perspective, from one country or area of Europe to another?

Thanks folks.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Need detail on European plug configurations for small appliances

09/02/2015 12:25 PM

Wiki gives a country by country reference guide that is very handy....

https://en.wikipedia.org/wiki/Mains_electricity_by_country

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 3)
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#2
In reply to #1

Re: Need detail on European plug configurations for small appliances

09/02/2015 12:32 PM

Thanks... I have seen that before.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Need detail on European plug configurations for small appliances

09/02/2015 12:39 PM

Various Thomas Glover handbooks might be helpful, even if not fully comprehensive.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
3
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Need detail on European plug configurations for small appliances

09/02/2015 1:04 PM

A1) The standard in the UK is around 230V with a tolerance so that appliances in the UK and Eire can be used in Continental Europe at 220V, and vice-versa. See A2 below.

Mains-operated shavers can be plugged into a special socket in the bathroom in the UK, which is transformer-isolated from Earth, of low power capability, and use a 2-pin plug similar to those used in the Americas; many such sockets have dual 115V/230V capability.

A2)See #1 above.

A3) usually 3: Live, Neutral and Earth. 2-pin plugs can be used for double-insulated appliances in some parts of Continental Europe, see #1 above, and for electric shavers, which use only the Live and Neutral.

A4) see A3 above.

A5) Never. The case of an appliance is bonded to the Earth conductor. However, in the case of an appliance that bears the square-within-a-square symbol, some cases are double-insulated by the manufacturer and as such do not need an Earth connection whether metallic or otherwise; such appliances will use a 2-core flex.

A6) An Earth conductor.

A7) Yes, though see A5 above.

A8) Live and Neutral, tripping if the imbalance exceeds the unit's trip rating current.

A9) See #1 above.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 3)
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#5
In reply to #4

Re: Need detail on European plug configurations for small appliances

09/02/2015 2:23 PM

Excellent tks. The neutral at the house supply is bonded to the "earth" conductor?

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: Need detail on European plug configurations for small appliances

09/02/2015 2:42 PM

Not in a TT system, a TN-S system or an IT system (IT is not usually found in houses in the UK - more common in hospitals).

There is an excellent article in Wikipedia on earthing systems: https://en.wikipedia.org/wiki/Earthing_system

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#7
In reply to #6

Re: Need detail on European plug configurations for small appliances

09/02/2015 3:13 PM

So in your TT system, the only point the neutral is bonded to earth is at the supply. Thanks PW... appreciated.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#8
In reply to #5

Re: Need detail on European plug configurations for small appliances

09/02/2015 6:40 PM

Please (just for my sense of fairness) give PW the GA he deserves. With thanks in anticipation.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Off Topic (Score 4)
Guru
United Kingdom - Member - Old New Member

Join Date: Jul 2005
Location: South east U.K.
Posts: 3695
Good Answers: 93
#9

Re: Need Detail on European Plug Configurations for Small Appliances

09/03/2015 4:21 AM

This interactive chart my help.

__________________
I didn't have a really important life, but at least it's been funny (Lemmy Kilminster 1945-2015)
Register to Reply Score 1 for Good Answer
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#10

Re: Need Detail on European Plug Configurations for Small Appliances

09/03/2015 6:27 AM

The voltage is 250V at 50Hz, correct? I usually measure between 220 - 230.

How many pins in a standard receptacle and how are they refered to? Each country it seems has their own, even the Europlug is modified between countries. Define your country.

As to the conductors that delivers power to a device and returns it back to the source, what do you call them? A hot and a neutral? Phase or live and neutral.

Is the neutral bonded to the case of an appliance inside that appliance? No. That is simply very dangerous, code should never allow it, ever?

You use a bonding conductor, correct? Do you call it a bond or a ground conductor? Ground, earth, Masse, Erde, what language do you want?

Is the bonding conductor bonded to the case of an appliance inside that appliance? Depends if the device to be powered is double insulated or not. If double insulated, no earth required.

How exactly does your RCDs work, what conductors do they monitor and how? God knows why you need to know this, but they compare the current in the phase to that in the neutral, if they are not the same, within given tolerances, the breaker drops within a set time limit.It does not need an earth connection as far as I am aware.

How different is it, from a configuration perspective, from one country or area of Europe to another? There are plenty of differences, the UK has the best system of all, each plug has a fuse that needs to be sized for the device at the other end of the cable correctly.

They use ring mains since about 1945.

The plugs do not allow tiny fingers or objects like knives to touch them when live.

The live and the neutral sockets are covered by insulating parts that prevent entry of foreign objects and are only automatically released once the earth pin (always present even if not used as an earth connection!) is inserted and the phase and neutral pins are entering their respective sockets...Brilliant system. Used also in various other countries.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#11
In reply to #10

Re: Need Detail on European Plug Configurations for Small Appliances

09/03/2015 7:38 AM

Boldface, like all-caps, is just another form of shouting.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Off Topic
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#12
In reply to #10

Re: Need Detail on European Plug Configurations for Small Appliances

09/03/2015 10:53 AM

Thanks...

Country... There is no country defined at the moment in the issue I have before me.

Neutral to Case Bonded... Agree fully, I still need to understand European practices.

Language... More interested in the term used as opposed to what language is used.

Bond Conductor to the Case... So it is bonded to the case if not double insulated.

RCD Functions... Because an RCD is being proposed as a way to mitigate a potential harmfull situation. As such, I need to determine it ability to mitigate the hazard.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Power-User
Ireland - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: Aug 2007
Location: Northern Ireland
Posts: 197
Good Answers: 17
#13

Re: Need Detail on European Plug Configurations for Small Appliances

09/03/2015 12:08 PM

I'm going to add a bit more on previous answers, with a nugget of gold at the end for those who persevere :-)

The voltage is 250V at 50Hz, correct?

50 Hz yes but anywhere from 220-240V nominal. Most are nominal 230V. The UK has the highest I have encountered at 230 +10% / -6% = 253V max.

How many pins in a standard receptacle and how are they referred to?

Standard UK receptacle has been described. However 15A 3 x round-pin un-fused are still in use for theatre lighting. 5A 3 x round pin can be used for small standing lamps for example (to prevent people plugging in higher powered appliances).

As to the conductors that delivers power to a device and returns it back to the source, what do you call them? A hot and a neutral?

Live and neutral, which are known as active conductors. In US and Canada you can have 2 hot-legs to give you 240V for large appliances. This is not used in Europe since the voltage is already near that level.

Is the neutral bonded to the case of an appliance inside that appliance?

No not ever no way. As an active conductor, the neutral must never be so connected unless by the supply authority itself.

You use a bonding conductor, correct? Do you call it a bond or a ground conductor?

See below.

Is the bonding conductor bonded to the case of an appliance inside that appliance?

See below.

How exactly does your RCDs work, what conductors do they monitor and how?

See below.

How different is it, from a configuration perspective, from one country or area of Europe to another?

Aha. A huge organisation called Schneider have thought about this. Helpfully they have produced a great tome called the Electrical Installation Guide which you can download free of charge from here:

http://www2.schneider-electric.com/sites/corporate/en/products-services/product-launch/electrical-installation-guide/electrical-installation-guide.page

Also search for their 'Cahiers techniques' which will give even more detailed information on the workings of RCDs (for example).

__________________
I love deadlines; I love the whooshing sound they make as they pass by. - Douglas Adams
Register to Reply Score 1 for Good Answer
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#14
In reply to #13

Re: Need Detail on European Plug Configurations for Small Appliances

09/03/2015 12:20 PM

Thanks...

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#15

Re: Need Detail on European Plug Configurations for Small Appliances

09/07/2015 5:03 PM

A morsel of information. The earth wire that runs to small appliance receptacles [sockets in UK] is defined as a circuit protective conductor [cpc] " a protective conductor connecting exposed-conductive-parts of equipment to the main earthing terminal" while a bonding conductor is "a protective conductor providing equipotential bonding". The words in italics are exactly as the definitions in the "IET Wiring Regulations" British Standard 7671, current edition. Another definition makes "equipment" an abbreviation of "electrical equipment".

Each circuit from a distribution board fuse/breaker has its own cpc, usually called "earth", of course! A bonding conductor is, for example, between the main building earth terminal and the metallic piping for water and fuel gas and is not part of any "circuit".

I appreciate that your using the term "bonding" shows that you have your principles firmly in mind in North America and know that bonding the kit in a building is the essence and a real "ground" only matters outdoors.

It is standard practice in Britain for the cpc of a typical 2.5 sq.mm copper socket circuit to be only 1.5 sq.mm.

Register to Reply
2
Power-User
Ireland - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: Aug 2007
Location: Northern Ireland
Posts: 197
Good Answers: 17
#16

Re: Need Detail on European Plug Configurations for Small Appliances

09/16/2015 7:43 AM

Hot off the press. I'm working on a project in France and uncovered another guide from Legrand which describes all sorts of European wiring regulations. Very useful indeed.

http://www.legrand.com/files/fck/File/pdf/Guide-International.pdf

__________________
I love deadlines; I love the whooshing sound they make as they pass by. - Douglas Adams
Register to Reply Good Answer (Score 2)
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#17
In reply to #16

Re: Need Detail on European Plug Configurations for Small Appliances

09/16/2015 9:25 AM

Nice find... thanks.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#18
In reply to #16

Re: Need Detail on European Plug Configurations for Small Appliances

09/16/2015 1:34 PM

Sweet.

But what's that 'Spur Unit' in the IEC/British standards? It looks like it's joining to different circuits together. That doesn't seem safe...

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#19
In reply to #18

Re: Need Detail on European Plug Configurations for Small Appliances

09/16/2015 6:19 PM

The spur unit is just T-ing a spur off from a ring main circuit (the most common method of domestic wiring in the UK). The diagram doesn't make it very clear. Look here: https://en.wikipedia.org/wiki/Ring_circuit

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#20
In reply to #19

Re: Need Detail on European Plug Configurations for Small Appliances

09/17/2015 10:01 AM

Oh, a Ring circuit is a way to carry an amp load with smaller wiring, by running the circuit in a loop from the electrical panel out through the area, and then back to the same point, so the load is shared by two conductors.

Very clever .....

Until a wire breaks or comes loose, or a component gets miswired, then the whole house burns merrily like a Yule Log.

(shakes head) "...mad dogs and Englishmen..."

That's why I love ANSI rules for wiring: every INCH of a wiring circuit must be able to carry the FULL CURRENT the breaker or other circuit protection will allow, with some extra capacity as a safety buffer.

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#21
In reply to #20

Re: Need Detail on European Plug Configurations for Small Appliances

09/19/2015 9:58 AM

Yes, but on a ring main in UK we have two earth returns from each socket! What happens when an earth wire breaks in US?

The ring main was introduced in 1948 to save on copper, which was strategically short then. For 2 x 2.5 square mm wire you get a 32A circuit. The associated BS3613 sockets had shutters over live & neutral socket entries opened by the earth pin and the matching 13 amp plugs all had integral fuses. The better sockets to current standard will not open shutters unless all 3 pins are inserted.

If you have a 2.5 sq.mm Cu wire in a 20A breaker radial circuit with a bad joint is it that much better? It is the bad joints that get really hot and cause trouble [and 115V has twice the current for the same power]. The wires are usually buried in plaster.

Europe uses 230V, which for the same power and % volt drop uses 1/4 the copper of 115V.

Every system has its disadvantages and benefits.

67model

Register to Reply
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#22
In reply to #21

Re: Need Detail on European Plug Configurations for Small Appliances

09/21/2015 9:26 AM

"Yes, but on a ring main in UK we have two earth returns from each socket! What happens when an earth wire breaks in US?"

Two Earth returns for each socket? In the US we call that a Ground Loop and it's generally a Bad Thing to have.

But when you have a single ground line and it breaks, you end up with ungrounded equipment. Which is why it's important to regularly check your building wiring for problems such as that. It's just part of Regular, Preventative Maintenance, which should be done anyway.

Personally, I'm only worried about 'broken grounds' when hooking up audio equipment, since I live in Chicago, and all our wiring, even in residential locations, are contained in metal pipe, and the pipe doubles as the 'ground connection.' a broken hot will touch the inside of the pipe and trip the breaker, a broken neutral may trip the breaker, or it may simply leave the circuit it's part of 'mostly dead' (equipment will not run, although the hot side is still live) or, if the neutral is connected to the Earthing point inside the equipment, cause the equipment to run power down the ground for the brief moment needed to trip the breaker.

(The reason for watching grounds when hooking up audio equipment is to eliminate any 'ground hum,' a 50/60Hz buzz that leaks in when equipment is grounded improperly. Ground Loops are a major source of Ground Hum.)

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply
Register to Reply 22 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (2); adreasler (3); Andy Germany (1); BabyGuinness (2); JohnDG (2); Nigh (1); North of 60 (6); PWSlack (2); SolarEagle (1); Tornado (2)