Calculating I Beam Size

09/07/2015 1:14 AM

Hi all

I need to design a Ibeam for for a 14.4kN point load, located at 2m at the end of the beam. The beam is 2m long and is fixed at the other end. Using 350WA SANS 1431 steel. Please help me selecting the correct beam.

Regards

Stiaan

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Calculating I beam size

09/07/2015 2:14 AM

Huh? The beam is 2m long, and the load is 2m from the end of the beam? In other words, the load is at the fixed end of the beam? In that case, it is a simple shear problem. You'll need a Capt Moosie or a Codemaster to deal with such complexity.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#3
In reply to #1

Re: Calculating I beam size

09/07/2015 5:08 AM

No no the other end... no the other, other end

I can see we are going to have no end of trouble with this

Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#4
In reply to #1

Re: Calculating I beam size

09/07/2015 5:10 AM

Thanks for that!

I think he means a cantilever.

I might have a look when I get a minute, depending on the answers to IdeaSmith's #2.

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#18
In reply to #4

Re: Calculating I beam size

09/08/2015 11:05 AM

Or was it a cavalier?

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#9
In reply to #1

Re: Calculating I beam size

09/07/2015 12:05 PM

Not, "from", 'at'.

munger, you said, " Did do research but time is limited"

There is never enough time to do it right the first time, but always enough time to do it over.

Register to Reply
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#2

Re: Calculating I beam size

09/07/2015 2:24 AM

Sounds like homework!

Why would you have to design this and ask in an engineering forum how to do this?

What sort of safety do you want to apply?

Any dynamic loads anticipated?

Or is it a static load?

Whats the tensile strength of the steel?

Did you do a research?

Start here! https://en.wikipedia.org/wiki/I-beam

__________________
Common Sense Dictates
Register to Reply
Participant

Join Date: Sep 2015
Posts: 2
#5
In reply to #2

Re: Calculating I beam size

09/07/2015 5:20 AM

Hi IdeaSmith

1. Not homework, wish I was still in school though...

2. I don't get much exposure with design but need this for a rigging job

3. Safety factor of about 1.2 would be sufficient

4. No

5. Only static loads (oh and yes it is a cantilever)

6. Tensile strength = 480MPa

7. Did do research but time is limited to get solution at the moment and lost my notes from university

Cheers

Register to Reply
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#6
In reply to #5

Re: Calculating I beam size

09/07/2015 5:41 AM

The internet replaces your notes from university me thinks.

There was plenty of information in my links provided.

I will not do the calculation for you. Sorry but I think it will be better if you do it if you are in charge for the rigging service.

Take a higher safety factor just in case!

http://www.brighthubengineering.com/machine-design/40491-how-to-select-a-correctly-size-steel-i-beam/

Good luck!

__________________
Common Sense Dictates
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#8
In reply to #5

Re: Calculating I beam size

09/07/2015 8:30 AM

480MPa sounds like a typical UTS for structural steel. You would need a safety factor much higher than 1.2 to get a safe working stress.

But unsurprisingly, it's limited by deflection rather than stress. The biggest I-beam I have data on to hand, 203 x 102, gives stress 130MPa, which is OK, but deflection 8.5mm, or 1/236 x beam length, a bit near the knuckle.

UB 203 x 133 x 30kg/m gives stress 106MPa, and deflection 6.8mm, or 1/295 x beam length, still a fair bit of deflection, could be acceptable, it's up to you.

But you should swat up on beam theory and make sure you're happy before going ahead!

__________________
Give masochists a fair crack of the whip
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#10
In reply to #8

Re: Calculating I beam size

09/07/2015 12:46 PM

I should have said "swot" up!

__________________
Give masochists a fair crack of the whip
Register to Reply
Power-User

Join Date: Jun 2009
Location: Australia
Posts: 277
Good Answers: 45
#12
In reply to #5

Re: Calculating I beam size

09/07/2015 11:36 PM

I shudder when I hear, "don't know how, it is just a rigging exercise" - to me this means, "someone could get killed".

It looks like you do not understand what you are doing if you think a safety factor of 1.2 is likely to be enough. I was a design engineer in years gone by and don't recall ever using a factor that low.

Just one question to alert you to a potential risk, and one that even the odd professional has got caught on - "is there a possibility of a torsional mode/stability failure, and or how is this to be avoided" ?

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#13
In reply to #12

Re: Calculating I beam size

09/07/2015 11:44 PM

I see this calculation:

Length of beam x load x span x safety factor x torsional load : then a miracle happens = answer.

Register to Reply
Anonymous Poster #1
#14
In reply to #12

Re: Calculating I beam size

09/08/2015 3:33 AM

A well-considered response. Always nice to learn something from another's thought processes..thanks!

Register to Reply
Guru
Technical Fields - Project Managers & Project Engineers - New Member

Join Date: Oct 2013
Location: Texas.Baytown
Posts: 697
Good Answers: 26
#15
In reply to #5

Re: Calculating I beam size

09/08/2015 7:18 AM

Safety factor of about 1.2 would be sufficientI always go for a minimum of 2. Even then its iffy. As load is applied repetitively the contact area is work hardned and yield/tensile values change. We have had this problem with crane hooks.

__________________
If you want to know how well a broom works you do not ask the guy selling the broom or the guy who designed the broom, you ask the guy using the broom.
Register to Reply
Power-User

Join Date: Sep 2015
Posts: 482
#7

Re: Calculating I beam size

09/07/2015 7:11 AM

I think, you must pass the licensure exam first, even if design of prototype involve only you riding on it. Dangerous stuff when life is at risk (your dog's, your neighbor's, your wife's, your children's life)

I suggest you must reflect on this first.

__________________
The doctor said "just one post or reply aday in CR4, take it or leave it". I said, "what does that mean?"
Register to Reply Score 2 for Off Topic
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#11

Re: Calculating I Beam Size

09/07/2015 7:09 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru
Canada - Member - New Member

Join Date: Jul 2013
Location: Canada but south of 49
Posts: 895
Good Answers: 20
#17
In reply to #11

Re: Calculating I Beam Size

09/08/2015 9:07 AM

Yes, I keep forgetting all the forumulae are available online these days. Call me old fashioned, but I would refer to my CISC or AISC handbook of steel construction. Have to make sure you know if it is guided or unguided.

__________________
Never stop learning
Register to Reply
Power-User

Join Date: Jun 2009
Location: Australia
Posts: 277
Good Answers: 45
#19
In reply to #11

Re: Calculating I Beam Size

09/08/2015 7:53 PM

The above is correct in simple terms, but there is a mode of failure not provided for in the formula, and a trap for the naive - that of the section twisting (and typically moving laterally) to bend around the minor axis - torsional stability failure. Regrettably, for that reason, the answer should not be rated GA.

Register to Reply Score 1 for Good Answer
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#20
In reply to #19

Re: Calculating I Beam Size

09/08/2015 7:56 PM

Exactly correct. The failure mode is directly linked to high stress in the compression flange, and the laterally unsupported length of the section between lateral bracing mechanisms.

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#21
In reply to #11

Re: Calculating I Beam Size

09/09/2015 12:33 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#16

Re: Calculating I Beam Size

09/08/2015 7:49 AM

Nope, I'm not touching this one. Pay me to figure it out for you.

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Register to Reply
Register to Reply 21 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Brave Sir Robin (1); CaptMoosie (2); Codemaster (3); IdeaSmith (2); Kevin LaPaire (1); Legolaz (1); lyn (2); munger (1); SolarEagle (2); texasron (1); Tornado (1); TrevorM (2); user-deleted-1105 (1)

Previous in Forum: Linear Roller Bearings   Next in Forum: Generator Over Frequency Shut Down?

Advertisement