Generator Over Frequency Shut Down?

09/07/2015 2:57 AM

Our generator can run for 40 to 50 minutes, then shut down, when i check the fault log its says, Generator Over Frequency. i have serviced it twice in 6 months and cannot stop the problem. the Hz are suppose to be 50Hz but its shoots up to 56Hz then shuts down.

What could be causing problem?

Register to Reply
Pathfinder Tags: Generator Over frequency
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Generator Over frequency shut down?

09/07/2015 3:52 AM

One way would be if there is a sudden drop of load, with slow response from the generator's governor.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Sep 2015
Posts: 482
#2

Re: Generator Over frequency shut down?

09/07/2015 6:41 AM

Do you have any troubleshooting manuals for the genset that you can refer to? Is it possible to contact manufacturer for after sales technical support? I mean, that's the fastest and the safest way to go to solve your problem. First step.

If you have the feeling you be able to provide solutions faster than asking the tech support, you may wish to.

Tornado's comment is also worth to try.

Others might have inputs, similar solutions to problem like yours, just hold on a little while.

__________________
The doctor said "just one post or reply aday in CR4, take it or leave it". I said, "what does that mean?"
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9912
Good Answers: 1141
#3

Re: Generator Over frequency shut down?

09/07/2015 7:38 AM

Check your frequency meter when it starts up and periodically until it shuts down. That will let you know if the governor is drifting or if it is a sudden load change as Tornado has suggested.

Register to Reply
Participant

Join Date: Sep 2015
Posts: 2
#9
In reply to #3

Re: Generator Over frequency shut down?

09/08/2015 1:24 AM

it is a gradual increase and then shut down.

and also its not a constant increase it, it goes up then down then up ........and so on until its shuts down.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#11
In reply to #9

Re: Generator Over frequency shut down?

09/08/2015 4:10 AM

Hunting due to insufficient damping in the feedback caused by ......can't tell from here.

Do you have manuals for the machine?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#4

Re: Generator Over frequency Shut Down?

09/07/2015 10:17 AM

Old issue? Or; New issue?

Is the generator having the issue when stopped under load or unloaded condition?

Or both?

Old Issue:

Consult the IOM and the generator drawings.

Most likely you are getting the alarm(s) because of the generator shut down logic.

Many control systems remove power and signal inputs to all auxiliary equipment as soon as the stop signal is initiated. (This includes interrupting the feedback signal to the frequency monitoring and control circuits.)

This allows the operator to know the status of all alarm(s) functionality.

New Issue:

Possible governor component failure or governor needing calibration and tuning.

Possible frequency meter component failure or needing calibration.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5

Re: Generator Over frequency Shut Down?

09/07/2015 11:12 AM

What: type of prime mover, governor, control system, how old, initiated the actual trip, rate does the frequency rise, type of loading, was being done when the trip occurred, did the factory say, etc., etc.?

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#6

Re: Generator Over frequency Shut Down?

09/07/2015 11:28 AM

...." Loss of an interconnection, while exporting power (relative to system total generation) will cause system frequency to rise. Automatic generation control (AGC) is used to maintain scheduled frequency and interchange power flows. Control systems in power plants detect changes in the network-wide frequency and adjust mechanical power input to generators back to their target frequency. This counteracting usually takes a few tens of seconds due to the large rotating masses involved. Temporary frequency changes are an unavoidable consequence of changing demand. Exceptional or rapidly changing mains frequency is often a sign that an electricity distribution network is operating near its capacity limits, dramatic examples of which can sometimes be observed shortly before major outages. Frequency protective relays on the power system network sense the decline of frequency and automatically initiate load shedding or tripping of interconnection lines, to preserve the operation of at least part of the network. Small frequency deviations (i.e.- 0.5 Hz on a 50 Hz or 60 Hz network) will result in automatic load shedding or other control actions to restore system frequency. Smaller power systems, not extensively interconnected with many generators and loads, will not maintain frequency with the same degree of accuracy. "...

http://physics.stackexchange.com/questions/2641/how-does-load-affect-frequency-on-the-power-grid

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7

Re: Generator Over frequency Shut Down?

09/07/2015 5:27 PM

Of all people, Murphy oughta know what could go wrong.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#8

Re: Generator Over frequency Shut Down?

09/08/2015 12:20 AM

You do know Musany, that in order to be assisted, you have to answer some reasonable questions.

Are you there?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#10

Re: Generator Over frequency Shut Down?

09/08/2015 2:01 AM

Dear Mr.musany,

One possible cause could be severe earth fault occurring in a definite interval, as a result, the load is cut-off and the Engine Speed shoots up and stop the engine. When the frequency goes up the governor should regulate the speed (which does not happen in your case. ) and engine should not stop.

Pl. check for earth fault and check.calibrate the governor.

A similar situation was faced by us some time back and earth fault was the source of the problem, but engine did not stop.

DHAYANANDHAN.S

Register to Reply
Participant

Join Date: Jan 2018
Posts: 1
#12

Re: Generator Over Frequency Shut Down?

01/21/2018 11:06 AM

??

Register to Reply
Participant

Join Date: Feb 2019
Posts: 2
#13

Re: Generator Over Frequency Shut Down?

02/22/2019 10:26 AM

I would like to ask if your machine is running in droop or isochronous mode. To me if it is a stand alone it should have no droop. Check your speed sensor maybe dirty or intermittent signal, check gap settings, resistance, voltage output. Just remember it all starts with com from the speed sensor to controller to gov that if all is set correct and in nick condition. I f i was given more info on the machine i would be more precise

Good luck

Register to Reply