Open Circuit in Electric Floor Heating Wire

09/15/2015 8:10 PM

Hello you all, me again, with a simple (stupid) question for some of you...

I have installed a floor heating wire in an apartment on the second floor. Few months later I decided to remodel the one below it. I warned everyone involved in the project to stay away from the 2nd floor planks, to avoid damaging the wire by screwing underneath it, but...

As some of you might guess I do not want to tear down the "brand new floor" so which instrument should be use to find the breakage location. Please, do not mention about those device telling the distance of a broken wire, I have used them in the past with out any success at all and, any way I do not remember exactly how the cable was run (never thought about a picture back then).

Somewhere there is a (hope just one) 240 volts "switch" open in the floor, I can measure approximately 50 volts to ground, if I am kneeling on the floor.

So I am sure that I am not the first one with that type of problem, I hope a specialist will read this message.

__________________
Just for fun!
Register to Reply
Pathfinder Tags: Electric field sensor
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#1

Re: Open circuit in electric floor heating wire :(

09/15/2015 8:22 PM
Register to Reply
Commentator

Join Date: Dec 2010
Location: Montreal
Posts: 75
#37
In reply to #1

Re: Open circuit in electric floor heating wire :(

09/15/2015 11:24 PM

listen to me the f...cki ....g clown never re[ply

__________________
Just for fun!
Register to Reply Off Topic (Score 7)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#2

Re: Open circuit in electric floor heating wire :(

09/15/2015 8:24 PM
Register to Reply
Commentator

Join Date: Dec 2010
Location: Montreal
Posts: 75
#5
In reply to #2

Re: Open circuit in electric floor heating wire :(

09/15/2015 8:34 PM

I have tried one of those but it is not accurate enough, there is potential on all the 200 sq ft floor.

thanks for reading

__________________
Just for fun!
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#8
In reply to #5

Re: Open circuit in electric floor heating wire :(

09/15/2015 8:44 PM
Register to Reply
Commentator

Join Date: Dec 2010
Location: Montreal
Posts: 75
#9
In reply to #8

Re: Open circuit in electric floor heating wire :(

09/15/2015 8:48 PM

You must have a lot of time to waste

__________________
Just for fun!
Register to Reply Off Topic (Score 3)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#10
In reply to #9

Re: Open circuit in electric floor heating wire :(

09/15/2015 8:53 PM

if you're detecting leaking voltage ANYWHERE you need to remove the circuit from service and tear the floor out

Register to Reply
Commentator

Join Date: Dec 2010
Location: Montreal
Posts: 75
#11
In reply to #10

Re: Open circuit in electric floor heating wire :(

09/15/2015 8:59 PM

Yes, but because "ceramic"is not a good conductor, the source should not be detectable by means of electric field...

__________________
Just for fun!
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#12
In reply to #11

Re: Open circuit in electric floor heating wire :(

09/15/2015 9:03 PM

water is a lousy conductor but impurities can make conduct well enough to kill, I'm off this thread

Register to Reply
Commentator

Join Date: Dec 2010
Location: Montreal
Posts: 75
#13
In reply to #12

Re: Open circuit in electric floor heating wire :(

09/15/2015 9:05 PM

Yeah! you were useless anyway

__________________
Just for fun!
Register to Reply Off Topic (Score 4)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#36
In reply to #9

Re: Open circuit in electric floor heating wire :(

09/15/2015 11:22 PM

Many here have a lot of time to waste. Including apparently, you.

I recommend that you seek professional help.

You should also seek the help of a qualified electrician to solve your floor heating wire problem.

[Edit] after reading your #35, I believe that you are not going to get much help here.

I can see why.

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: Open circuit in electric floor heating wire :(

09/15/2015 8:24 PM

Can you at least narrow down where the worked-in areas you think the damage may have occurred?

If you have put a screw or nail through the wire perhaps you have a potentially live metal fastening you can get a reading off using a proximity-based voltage (field) detector or a multimeter set on voltage.

__________________
jack of all trades
Register to Reply
Commentator

Join Date: Dec 2010
Location: Montreal
Posts: 75
#6
In reply to #3

Re: Open circuit in electric floor heating wire :(

09/15/2015 8:40 PM

HI,

Unfortunately, the work on the first floor cover the full space of the above kitchen floor, I have tried the "proxy" sensor, as I mentioned to another "subscriber" with a high impedance multimeter I can read about 50 Vac (dry day).

__________________
Just for fun!
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4

Re: Open circuit in electric floor heating wire :(

09/15/2015 8:27 PM

I would just pull a new wire.....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Commentator

Join Date: Dec 2010
Location: Montreal
Posts: 75
#7
In reply to #4

Re: Open circuit in electric floor heating wire :(

09/15/2015 8:44 PM

That is the last thing an electrician troubleshouter would say...

__________________
Just for fun!
Register to Reply Score 2 for Off Topic
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#16
In reply to #7

Re: Open circuit in electric floor heating wire :(

09/15/2015 10:07 PM

No, a licensed electrician should immediately remove any and all wiring not installed by another licensed professional, regardless of it working today. Their license and your lives are hanging on their approval.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#22
In reply to #7

Re: Open circuit in electric floor heating wire :(

09/15/2015 10:40 PM

Well I worked as a troubleshooter for 30 years+, and if you can't find the problem without destroying the floor, then you disconnect the circuit and run a new one, possibly using an alternative route.....You obviously don't have any idea what you're talking about...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
4
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#23
In reply to #22

Re: Open circuit in electric floor heating wire :(

09/15/2015 10:44 PM

I disagree, he initially said he had a "stupid question". that was spot on

Register to Reply Good Answer (Score 4)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#14

Re: Open Circuit in Electric Floor Heating Wire

09/15/2015 9:34 PM

How many parallel and series circuits are there in this network?

Montreal is a rare name for a location but it is conceivable that the electric power for your floor heater is not 120 VAC, 60 HZ, earthed, split phase power regardless of your location. Do you know what it is?

Does a fuse blow or only one region not get hot?

"I can measure approximately 50 volts to ground, if I am kneeling on the floor." Between what and what nodes with what kind of a load and with what phase angle for the current? An expert would know what I'm asking.

Speaking of current, what magnitude and phase angle do you have on each side of your broken leg with an unknown load? How does this change when one flips the split phase wiring? (Sorry for asking a question based on a pending answer.)

When you ask your under-skilled friends to do unsupervised skilled craftsmen work do you at least buy the pizza and beer afterwards regardless?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Commentator

Join Date: Dec 2010
Location: Montreal
Posts: 75
#18
In reply to #14

Re: Open Circuit in Electric Floor Heating Wire

09/15/2015 10:17 PM

Hi Redfred, First of all, the contractor hired was professional, they did a lot of work in hard condition. They have sometime to do things a little risky to make there invoice on the right side of the customer, so I am not here to judge them. My discussion is aiming electrical troubleshooting.

Montreal is in Quebec, Canada. Unlike USA our domestic power supply is a split 240 Vac (not 220, that how we "push it" to NY). The system i am talking about is hooked on the opposed "phases or hots" of the line, 240. There is no junction in the wire, small urban apartment. As mentioned in the title, the circuit is open, no short circuit and current draw is none.

If I am touching one probe of my Fluke279 and the other one on the copper water pipe, while kneeling on the floor, today the meter read ~50 Vac. At this point there is no load or I am the load, the thermostat is by passed. Now when you are talking about phase angle, I do not know what you are talking about because as far as i understand we are talking about purely resistive load.

I hope this will help you to help me, because so far you are the best reply.

Thanks, Pierre

__________________
Just for fun!
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#38
In reply to #18

Re: Open Circuit in Electric Floor Heating Wire

09/16/2015 8:59 AM

I'm glad to hear you hired a professional for these installations. I suspect one of these professionals did a shoddy job. From your troubleshooting description it is obvious you should hire another professional to troubleshoot this problem.

Good Luck.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Canada - Member - New Member

Join Date: Jul 2013
Location: Canada but south of 49
Posts: 895
Good Answers: 20
#49
In reply to #38

Re: Open Circuit in Electric Floor Heating Wire

09/17/2015 8:24 AM

Was there any "warranty" on the installation(material and labour) by the original installer?? If he was a "professional" he should guarantee his work.

__________________
Never stop learning
Register to Reply
Guru

Join Date: Sep 2007
Location: East Texas
Posts: 1439
Good Answers: 31
#15

Re: Open Circuit in Electric Floor Heating Wire

09/15/2015 9:48 PM

Sounds like you may be needing a fire suppression system.

Given your success at running wire I'd probably have a professional install it.

__________________
"The greater danger for most of us lies not in setting our aim too high and falling short; but in setting our aim too low, and achieving our mark." -- Michelangelo
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#17
In reply to #15

Re: Open Circuit in Electric Floor Heating Wire

09/15/2015 10:08 PM

Touche`

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Commentator

Join Date: Dec 2010
Location: Montreal
Posts: 75
#21
In reply to #17

Re: Open Circuit in Electric Floor Heating Wire

09/15/2015 10:27 PM

I knew, this is not my first rodeo...

__________________
Just for fun!
Register to Reply
Commentator

Join Date: Dec 2010
Location: Montreal
Posts: 75
#19
In reply to #15

Re: Open Circuit in Electric Floor Heating Wire

09/15/2015 10:24 PM

ok

__________________
Just for fun!
Register to Reply
Commentator

Join Date: Dec 2010
Location: Montreal
Posts: 75
#20
In reply to #15

Re: Open Circuit in Electric Floor Heating Wire

09/15/2015 10:24 PM

idiot

__________________
Just for fun!
Register to Reply Off Topic (Score 9)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#28
In reply to #20

Re: Open Circuit in Electric Floor Heating Wire

09/15/2015 10:54 PM

I think I'm getting the picture now....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Off Topic
Commentator

Join Date: Dec 2010
Location: Montreal
Posts: 75
#31
In reply to #28

Re: Open Circuit in Electric Floor Heating Wire

09/15/2015 10:58 PM

Don"t you have anything else to guerk about

__________________
Just for fun!
Register to Reply Score 1 for Off Topic
Commentator

Join Date: Dec 2010
Location: Montreal
Posts: 75
#34
In reply to #28

Re: Open Circuit in Electric Floor Heating Wire

09/15/2015 11:07 PM

Please do not waste your time with me any more.

__________________
Just for fun!
Register to Reply Score 1 for Good Answer
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#40
In reply to #28

Re: Open Circuit in Electric Floor Heating Wire

09/16/2015 10:20 AM

That guy lives down at the corner of Whitney and Boulder Highway. I've seen him. You should see him strip #0000 wire!

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
Commentator

Join Date: Dec 2010
Location: Montreal
Posts: 75
#35
In reply to #15

Re: Open Circuit in Electric Floor Heating Wire

09/15/2015 11:09 PM

ok if your reply is not professional, then do not do it, a*****e

__________________
Just for fun!
Register to Reply Off Topic (Score 6)
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#51
In reply to #35

Re: Open Circuit in Electric Floor Heating Wire

09/17/2015 10:03 AM

On CR4 good answers come from good questions. Bad or misleading answers come from bad or demeaning questions/postings. This situation is worthless to pursue yourself. I do a lot of electrical design, trouble shooting and installation. I don't do brain or heart surgery, are you out of your skills range? What you have posted so far strongly suggests it. Hire a licensed electrician who has the knowledge to do this. On a cost basis he can do it much quicker and cheaper. He also will not leave the possibility of a structure fire due to incomplete trouble shooting or inexperienced installation . I've been a volunteer firefighter for many years and have put out quite a few structure fires started by bad electrical trouble shooting. One was fatal. Very often we can not put water on an electrical fire until the power company pulls the pole fuses. ETA for them is always "one hour". The structure is just a basement by then. Few fire depts lose the basement! If you want to see a real fire ask the county/state trading academy to demonstrate the "flashover" simulator. 600-1,200 deg F, helmet scorched, hugging the floor, flames crawling over your head, come out and they cool you off with a fire hose, and many more conditions. I love to train in it with $8,000 or more at 70 lbs of gear on. Do you want a family member or yourself to have to escape under these conditions? Keep on persistently doing this and they probably will. Things done wrong----Example.....when testing a line that may or does have capacitance voltage DON'T use a DMM. It pulls very little current to discharge the capacitance of the wires. Use a good old analog multi-meter from radio shack. They draw current, although very little, and will discharge the voltage to actual readings. Same reason DMM have so many readings when not connected to anything.. $5 radio shack is better than a $200 Fluke! Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply Off Topic (Score 4)
3
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#61
In reply to #51

Re: Open Circuit in Electric Floor Heating Wire

09/18/2015 8:42 PM

Whoever thought that electrical fires are OT should realize the OP is "Playing With Fire".

Tried to show him the importance of giving clear questions to get clear answers. Are we mind readers? Not me, only my wife can do that.

Electrical fires are sometimes caused by the same exact situation the OP is describing. Don't think it was too gory to describe what the potential results are Residential Building Electrical Fires, (2009-2011), FEMA, USFA, published 2014:

An estimated 25,900 residential building electrical fires were reported to fire departments within the United States each year. These fires caused an estimated 280 deaths, 1,125 injuries and $1.1 billion in property loss.

■■Residential building electrical fires resulted in greater dollar loss per fire than residential building nonelectrical fires.

■■Residential building electrical fires occurred most often in one- and two-family dwellings (84 percent).

■■Residential building electrical fires occurred most often in the colder months of January and December (at 11 percent each month).

■■In 79 percent of residential building electrical fires, the fire spread beyond the object where the fire started.

■■The leading items most often first ignited in residential building electrical fires were electrical wire, cable insulation (30 percent) and structural member or framing (19 percent).

■■The leading factors contributing to the ignition of residential building electrical fires were other electrical failure, malfunction (41 percent), unspecified short-circuit arc (25 percent), and short-circuit arc from defective, worn insulation (12 percent).

http://www.usfa.fema.gov/downloads/pdf/statistics/v14i13.pdf

If that's not incentive to have a licensed electrician do this and do it right what is? A death of a loved one or a law suit steered by a hungry lawyer (shark).

If you want to see if it is a live circuit or capacitance voltage put some sort of load on it. Use an analog VOM not a DMM. The small load of the VOM will see through the stray pick ups. DMM is only going to confuse you or give an erroneous reading.

What is the best thing for the OP to do? Run away from this potential disaster and get a licensed electrician in fast to fix it! His way, with even all the good answers provided to him, is a disaster waiting to happen

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply Good Answer (Score 3)
7
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#24

Re: Open Circuit in Electric Floor Heating Wire

09/15/2015 10:44 PM

The voltage that you're picking up is capacitive coupling between the live leg and your high impedance DMM probe, and it doesn't tell you much except that there's an AC source somewhere in the area.

I would use an electronic circuit tracer, the two piece type that you use to find which breaker protects a circuit. It feeds a low frequency signal onto the conductor, you then use the receiver to pickup the signal, once you've located the heater wire you then trace it to the point where the signal disappears and you'll know where the break is.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 7)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#25
In reply to #24

Re: Open Circuit in Electric Floor Heating Wire

09/15/2015 10:47 PM

a pinger

Register to Reply
Commentator

Join Date: Dec 2010
Location: Montreal
Posts: 75
#29
In reply to #24

Re: Open Circuit in Electric Floor Heating Wire

09/15/2015 10:56 PM

I know, there was someone...

__________________
Just for fun!
Register to Reply
Commentator

Join Date: Dec 2010
Location: Montreal
Posts: 75
#54
In reply to #24

Re: Open Circuit in Electric Floor Heating Wire

09/17/2015 10:58 AM

Hello, Thank you,

You are right I think this will work. I will try that as soon as I am back from work, one month.

__________________
Just for fun!
Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#26

Re: Open Circuit in Electric Floor Heating Wire

09/15/2015 10:48 PM

Consider using an ultrasonic cable tracer such as made by Cabac and others. You can often hire these devices from electrical suppliers or hire shops.

Disconnect both ends of the element from the other wiring and connect the tone generator.

Use the probe to trace where the wiring is routed, the signal will cease at the break point. Repeat the test from the other end to confirm the result.

They are generally pretty accurate.

Consider also that since a break has already occurred there may be other issues with the element, and any repairs may not fully expunge the problem.

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#27
In reply to #26

Re: Open Circuit in Electric Floor Heating Wire

09/15/2015 10:51 PM

I really don't like this guy, I was never going to save him, unfortunately both you and Ram gave him the shortcut

Register to Reply
Commentator

Join Date: Dec 2010
Location: Montreal
Posts: 75
#32
In reply to #27

Re: Open Circuit in Electric Floor Heating Wire

09/15/2015 11:00 PM

Yeah forget me

__________________
Just for fun!
Register to Reply
Commentator

Join Date: Dec 2010
Location: Montreal
Posts: 75
#33
In reply to #27

Re: Open Circuit in Electric Floor Heating Wire

09/15/2015 11:03 PM

you are suppose to be out, keep it this way.

__________________
Just for fun!
Register to Reply Score 2 for Off Topic
Commentator

Join Date: Dec 2010
Location: Montreal
Posts: 75
#53
In reply to #26

Re: Open Circuit in Electric Floor Heating Wire

09/17/2015 10:51 AM

Thank you, I like the idea.

The more I think about it, the more I like it. I understand your consideration but at least if I can point the location of the "break", I will tear down that tile and go from there. I will reply to your comment to let to know the result. However I am going at sea to work for a month so do not hold your breath.

Thanks' again.

__________________
Just for fun!
Register to Reply
Commentator

Join Date: Dec 2010
Location: Montreal
Posts: 75
#55
In reply to #26

Re: Open Circuit in Electric Floor Heating Wire

09/17/2015 11:02 AM

Hi Spade,

A tracer Is going to be worth to try, but i am feeling good about the success.

Thank again for the time, and professionalism.

__________________
Just for fun!
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#30

Re: Open Circuit in Electric Floor Heating Wire

09/15/2015 10:58 PM

In addition, I design and sell similar systems now (yea, really a jack of all trades), and although I have no experience fixing an installed under floor system that has developed a fault, I got to ask - is there a case where you can go back and get compensation from the company's insurance provider that screwed up your underfloor heating and just replace the whole lot?

Also it sounds like you now have a potentially serious safety concern so until the fault can be fixed you should probably tag and lockout the heating circuit if you have not already done so.

Got access to a thermal camera or thermocouple temperature meter, or is the floor heating too uniform that the variations in temperature would be too small to measure to narrow down the area of the suspected failure?

__________________
jack of all trades
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Dec 2010
Location: Montreal
Posts: 75
#56
In reply to #30

Re: Open Circuit in Electric Floor Heating Wire

09/17/2015 11:10 AM

Hi, Well I hope this is going to be a first time for you. I have to do something to fix it because that is what man does, right...

Insurance reclaim would be good if I had cought right then when it happen, but now I presume the fight between insurances co. ( mine and the contractor) will be tough and painfull.

Also for your safety concern, the power supply is securely isolated.

Thank you for you time.

__________________
Just for fun!
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#39

Re: Open Circuit in Electric Floor Heating Wire

09/16/2015 10:12 AM

A TDC (Time Domain Controller) test device if used properly will tell identify the location. It will tell the distance from where the tester is connected to the fault but you must know the layout of the circuit in order to pinpoint the location in reference to the floor area.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#41
In reply to #39

Re: Open Circuit in Electric Floor Heating Wire

09/16/2015 10:25 AM

Time Domain Reflectometery (TDR) will only work accurately with known transmission line cabling. On top of that, knowing that the break is 40 feet away from one point and 10 feet away from another point is useless information if one does not know how the wire is laid under the ceramics.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#43
In reply to #41

Re: Open Circuit in Electric Floor Heating Wire

09/16/2015 10:32 AM

Let him find his own "the f...cki ....g br[ak"

Register to Reply Off Topic (Score 10)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#44
In reply to #43

Re: Open Circuit in Electric Floor Heating Wire

09/16/2015 10:41 AM

even when you attempt to prevent someone from killing themselves or other people who encounter their "craftsmanship" it can be thankless to even try.

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#52
In reply to #41

Re: Open Circuit in Electric Floor Heating Wire

09/17/2015 10:21 AM

A time-domain reflectometer (TDR) is an electronic instrument that uses time-domain reflectometry to characterize and locate faults in metallic cables (for example, twisted pair wire or coaxial cable). It can also be used to locate discontinuities in a connector, printed circuit board, or any other electrical path.

  • Time-domain reflectometer - Wikipedia, the free encyclopediahttps://en.wikipedia.org/wiki/Time-domain_reflectometerWikipedia
    • Thanks for correcting my terminology.
    • We use TDR test devices not only for identifying distance(s)-to-fault(s) in all types of metal conductors but also in our fiber-optic communications cables.
    • They are very accurate.
    • I agree with you in that a TDR tester is useless if the location and layout of the conductor in question is unknown.
__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#42

Re: Open Circuit in Electric Floor Heating Wire

09/16/2015 10:32 AM

Did YOU personally install the heaters on the second floor?

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#45

Re: Open Circuit in Electric Floor Heating Wire

09/16/2015 1:14 PM

Good grief! Have you informed your fire and liability insurance company about this?

__________________
Good moaning!
Register to Reply
Commentator

Join Date: Nov 2008
Posts: 80
Good Answers: 4
#46

Re: Open Circuit in Electric Floor Heating Wire

09/16/2015 11:55 PM

Harbor Freight in the US sells a cable tracker. . I have used one many a time to trace wires in the wall or underground. battery operated. you connect one lead to the conductor and the other lead to the casing and turn it on. It injects a signal down the wire. You trace the signal with a probe. One problem you may have is that the conductors may be very close together and it may be hard to exactly pinpoint the spot, but you should come close. My son has used one to find hidden junction boxes left by the previous owner. Someone should sell something similar in Montreal.

Bonne chance

Before all you naysayers get going, I have over 40 years in the electrical trade, both construction and maintenance, worked 600 V hot bare handed, buttspliced 15 KV cables, worked on 250KV SF6 buss systems

Register to Reply
Commentator

Join Date: Dec 2010
Location: Montreal
Posts: 75
#57
In reply to #46

Re: Open Circuit in Electric Floor Heating Wire

09/17/2015 11:18 AM

Thank you... F...k them any way

__________________
Just for fun!
Register to Reply Off Topic (Score 10)
Power-User

Join Date: Jun 2011
Posts: 336
Good Answers: 18
#47

Re: Open Circuit in Electric Floor Heating Wire

09/17/2015 2:45 AM

A fox and hound would probably work, if you have a discerning ear!

http://www.amazon.com/Triplett-3399-Generator-Adjustable-Sensitivity/dp/B001ULPREW

__________________
If at first you don't succeed, skydiving is not for you!
Register to Reply
Commentator

Join Date: Dec 2010
Location: Montreal
Posts: 75
#59
In reply to #47

Re: Open Circuit in Electric Floor Heating Wire

09/17/2015 11:25 AM

Thanks,, I will try that

__________________
Just for fun!
Register to Reply
Guru

Join Date: Sep 2008
Location: Where the sun sets on OZ
Posts: 1381
Good Answers: 28
#48

Re: Open Circuit in Electric Floor Heating Wire

09/17/2015 6:36 AM

I am not sure that finding the break will help you as you still cannot repair it without ripping up a part of the floor. Once repaired can you be sure that another screw has not cut into a hot wire without breaking it? The screw is now hot. Now what do you do?

Can you get access to the heads of the screws? You would probably have already checked their potential if you could.

Few months later I decided to remodel the one below it. I warned everyone involved in the project to stay away from the 2nd floor planks, to avoid damaging the wire by screwing underneath it, but...

I can't believe anybody would screw into floorboards in the first place, let alone use screws long enough that they could poke through the boards. Floorboards typically don't support loads without sagging. It is the floor joist that supports cabinetry etc. It is for this reason alone that the job done by the remodelers was bad work. Here in Oz there are licensing bodies that would like to be informed about this type of tradie so that they could drum them out of business. Grounds for compensation!

Jim

__________________
Where's the KaBoom? There should be a KaBoom!
Register to Reply
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#50
In reply to #48

Re: Open Circuit in Electric Floor Heating Wire

09/17/2015 9:15 AM

Jimrat,

When I purchased my first custom built house in Nevada, I was touring the house with the Superintendent and I noticed that the electrical installers had drilled some routing holes very close to the inside portion of the framing stud.

I asked the Superintendent if they were going to install nailer plates to protect the wires and he replied "WE DON'T NEED THEM, THEY DON'T USE THE LONG DRYWALL NAILS" very confidently.

Fast forward about 4 months. I have the cable TV installers at the house and they have a direct short on the CATV wire in my sons room. I call the Superintendent and politely explain the situation and they send out a tech to look at the issue. He traces the wires to an area in the garage where the bulk of those wires were routed through the studs. After cutting out a small section of drywall he found the issue.

The drywall installers had used 2" long nails instead of 1-5/8" and they pierced the CATV wire so dead center that it had severed the center solid copper conductor in half. I told the tech to stop work and I called the Superintendent to come look at the issue. He said he was too busy and I replied then I guess your tech is going to sit here at my house until you show up. Let's just say that he was there in 10 minutes and was truly unhappy when I took him to task on the use of "THE LONG DRYWALL NAILS".

I guess the moral of the story is to never trust a contractors word unless you've worked with them before. They will lie to you more than a 3 year old in the cookie jar!

P.S. Then they never came back to repair the section of drywall they cut out. The Superintendent stopped taking or returning my calls. What an ass!

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
Commentator

Join Date: Dec 2010
Location: Montreal
Posts: 75
#58
In reply to #50

Re: Open Circuit in Electric Floor Heating Wire

09/17/2015 11:24 AM

Hi, sorry for you story.

__________________
Just for fun!
Register to Reply
Power-User

Join Date: Nov 2011
Location: New Hampshire
Posts: 406
Good Answers: 3
#60
In reply to #50

Re: Open Circuit in Electric Floor Heating Wire

09/18/2015 7:46 PM

Your story is why the NEC in the U.S. states you will cover the wire with the proper plate to fend off the contractor doing what should not be done.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#62
In reply to #60

Re: Open Circuit in Electric Floor Heating Wire

09/18/2015 9:23 PM

"...the NEC in the U.S. states you will cover the wire with the proper plat...", this would imply that the entire heating cable be protected both top and bottom for its entire length. Please provide the NEC Chapter and Paragraph that states this requirement.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Register to Reply 62 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Crabtree (1); Fredski (9); Gavilan (1); jack of all trades (2); JIMRAT (1); Kevin LaPaire (1); lyn (2); Munster (1); old salt (2); Original_Macgyver (3); RAMConsult (2); redfred (5); SHOCKHISCAN (2); SolarEagle (3); spades (1); SWB123 (1); TripppleP (24); vtbgiraud (1)

Previous in Forum: Shaft Power / Absorbed Power   Next in Forum: Motors

Advertisement