pls house how can I service my humming electric contractors. because am not comfortable with the noise

Reply
User-tagged by 1 user
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#1

Re: Humming Contactors

09/17/2015 6:24 AM

Try teaching them the words.

Seriously though, there could be a number of reasons such as dirt between the pole faces, pole faces misaligned and not coming together accurately, loose laminations, low voltage, coil too loose on stem, lost shading ring, DC contactor being used on AC, etc.

Reply Good Answer (Score 3)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#2

Re: Humming Contactors

09/17/2015 7:47 AM

I don't help ANONS

Reply
Guru

Join Date: Sep 2012
Location: Iowa, USA
Posts: 577
Good Answers: 50
#3

Re: Humming Contactors

09/17/2015 10:31 AM

As Spades indicates, something is causing an air gap in the closed magnetic circuit.

Disassemble the contactors, most likely rust corrosion on pole faces. Sand both faces clean (on a flat surface) and the buzzing will stop. Also check that the shaded pole winding is intact.

You can't put paint on the faces as this will create an air gap. I'm not not aware of a conformal coating that will inhibit corrosion and keep the air gap minimized. Someone here may know of this.

I'm assuming these are located in an area where humidity can cause this corrosion. It does not take much.

__________________
ignator -
Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#5
In reply to #3

Re: Humming Contactors

09/18/2015 8:55 PM

First disconnect and lock-out/tag-out the supply source(s).

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#4

Re: Humming Contactors

09/17/2015 11:57 AM

Many good manufacturers spray a fine mist of anticorrosive oil which percolates by capillary action between laminations and helps reduce magnetostictive noise. It also oozes onto the surface and forms a very fine (5 microns or so) layer which does not interfere with the normal operation of the magnet. If I recall, the name of the chemical is Tectyl 472.

The best way to reduce (even eliminate) noise is to use a DC coil. Many elevator/escalator operating contactors use DC coils with a built-in rectifier since the incoming coil supply is AC.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#6

Re: Humming Contactors

09/19/2015 3:04 PM

You do not write if only some contactors hum more than others or all hum objectionably. Many contactor coils are AC powered. This is simple and reliable but inherently produces 100Hz or 120 Hz mechanical vibration and noise.

Basically, the smaller the air gap in the iron path, the greater the inductance and the smaller the current and noise (current and noise will increase with coil voltage). But there is a minimum gap to avoid lock-on due to remanent magnetism while the coil is de-energised.

"Spades"has given reasons why some may be more noisy than others.

You might be afflicted by a particularly noisy contactor design or panelling which resonates at the vibrating frequency. A microphone and amplifier with level meter might track down a particularly noisy item. Resilient rubber mountings (for each contactor) might work or stiffening a panel to move "off resonance - but these are difficult beyond the design/construction stage.

Modern panels close to personnel would use DC contactors where noise could be an irritation. This is not a feature of lowest cost design. But you might [on questioning the contactor maker] find that the coils on your contactors can be "field-changed" for DC coils with built-in diode bridges - the shading turn by the gap, needed for AC, will slow DC pick-up and drop-out and need to be removed.

If your contactors are fed from a common supply, such as a control transformer, it could be that the normal voltage "out" is at the top end or above the contactor coil specified band - you might be able to use a higher voltage transfo primary tap (also cuts transfo noise). Control transfos may be oversized for a small number of contactors and be cheap [with poor regulation and high voltage on small loads]. N.B. It is possible your primary supply voltage is high, which would affect motor efficiency, flux and noise as well as contactors.

If you suffer low supply frequency, this increases magnetising current and noise but nothing can be done about that!

Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#7

Re: Humming Contactors

09/25/2015 12:34 AM

Basically the contactor laminated E- core surface properly worn out or dirt accumulated on the surface of the laminated E -core. This cause the closing gap point between the upper laminated E -core and the lower laminated E -core are not properly closed and during energize the contactor the gap cause the humming sound.

The only best thing to do is to replace the contactor.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Reply to Forum Thread 7 comments