MCB Selection

10/21/2015 3:57 PM

How cal i calculate the value of MCB, if i have full load amp, kw and voltage

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#1

Re: MCB selction

10/21/2015 4:20 PM

You need to specify what you mean by MCB. In IEC-land a MCB is a miniature circuit breaker, in other places this acronym has a different meaning.

You will also need to know the prospective short-circuit current of the supply that you are planning to connect your breaker to.

__________________
paulusgnome
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: MCB Selection

10/21/2015 4:44 PM

You need to understand what a MCB does and is intended to do.

You obviously do not!

Google "MCB function".

Then Google "electrical codes".

Until you have some inkling of what you are doing, you are a danger to society.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: MCB Selection

10/21/2015 5:59 PM

As always, using the electrical code applicable to the jurisdiction in which the installation is to be made. In the UK, for example, it would fall under BS7671. The consequences of not doing so include invoking a measure of unpopularity with the facility's fire insurers and the relatives of the individuals that get killed.

Remember the circuit protective device is there to protect the WIRING.

If in doubt, consult a qualified Electrician.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: MCB Selection

10/21/2015 11:56 PM

This is not about just a formula; there are further questions: Is the load inductive (e.g., motor), resistive (e.g., heater), or capacitive? There are different factors for each. Is the load continuous? There may be a factor for that, also. As already mentioned, this depends on the local regulations. (Apologies for lack of paragraphs; I am temporarily saddled with a crummy browser.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Member

Join Date: Oct 2015
Posts: 6
#5

Re: MCB Selection

10/22/2015 4:13 AM

This is for a my new project in USA, It is a power panel-

As it is an up gradation of a chemical plant-

EQUIPMENT
CAUSTIC PUMPS
PLC PANELS
INSTRUMENTS
DAMPERS
UHF FILTER DRIVE
HOIST
RECYCLE FAN
ID FAN
Heater

These are the equipments i have to power up. So i have to calculate the circuit breakers.

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #5

Re: MCB Selection

10/22/2015 1:47 PM

Definitely - consult a qualified Electrician without further delay!

It doesn't matter what the loads are as it is the wiring that the MCB is supposed to be protecting.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster #1
#18
In reply to #5

Re: MCB Selection

10/30/2015 9:59 AM

I hope this is a college project. Otherwise get out of the job before you kill someone!

Register to Reply Off Topic (Score 5)
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#6

Re: MCB Selection

10/22/2015 10:32 AM

Selected Molded Case Breaker (MCB) values are dependent on the following:

1. Location/position of MCB in electrical system.

2. Rated current of the circuit conductors being protected.

3. Expected maximum current inrush of the circuit.

4. Speed of circuit interruption required to protect the equipment being serviced by the MCB.

5. Ambient environment conditions. (mean temperature, humidity, chemicals,?)

6. Type of system voltage (AC or DC).

7. Physical limitations of the applications.

These and all other requirements are identified in the local code documentation specific to the area/location.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Score 1 for Good Answer
Member

Join Date: Oct 2015
Posts: 6
#7
In reply to #6

Re: MCB Selection

10/22/2015 10:49 AM

Can anyone share the equation for the selection on circuit breaker, Disconnect switch and Fuse

Register to Reply Off Topic (Score 6)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #7

Re: MCB Selection

10/22/2015 1:49 PM

Anyone who uses BS7671, such as a qualified Electrician, can. And it's not so much a formula, more a protocol.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#10
In reply to #7

Re: MCB Selection

10/22/2015 1:54 PM

Not really. As mentioned both earlier and later, it is not just a formula.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Member

Join Date: Oct 2015
Posts: 6
#11
In reply to #10

Re: MCB Selection

10/24/2015 5:24 AM

Thanks Expert.

Can you give me a solution for this.

suppose I have these 2 equipment with you in your project, what will be rating of circuit breaker you chose for its efficient operation.

HOIST3460VAC3.831
RECYCLE FAN3460VAC231
Register to Reply Off Topic (Score 7)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#12
In reply to #11

Re: MCB Selection

10/24/2015 10:14 AM

You don't understand English do you?

Circuit breakers have nothing to do with efficiency!

Use a search engine to research breakers and READ THE CODE BOOK!

Don't be so stubborn!

Do your own work!

Register to Reply
Member

Join Date: Oct 2015
Posts: 6
#13
In reply to #11

Re: MCB Selection

10/24/2015 11:16 AM

Sorry Expert i did not ask about Efficiency. Check my recent post only..

I will check the CODE BOOK ok

Thanks alot

Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#14
In reply to #13

Re: MCB Selection

10/24/2015 12:45 PM

"rating of circuit breaker you chose for its efficient operation."

Register to Reply Off Topic (Score 5)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#15
In reply to #11

Re: MCB Selection

10/24/2015 10:57 PM

Not unless you explain the numbers in the table. Moreover, breakers are not chosen on the basis of "efficient operation".

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Member

Join Date: Oct 2015
Posts: 6
#16
In reply to #15

Re: MCB Selection

10/25/2015 5:07 AM

Experts i am very new in this component selection. Therefore i am totally confused.

I know only thing that i need to use circuit breakers for the above systems also mentioned the information i have with me.

Now i am using search engine to study.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#17
In reply to #16

Re: MCB Selection

10/29/2015 9:05 AM

You need to first follow local codes, but that is not your only problem.

Being that you said this is going to be installed in the USA, the information you need can be found in reading and understanding the National Electric Code (NEC), available from the NFPA (National Fire Protection Agency) as document NFPA-70. In addition, if this is an assembled system as an industrial control panel, the NEC will require that it bear an approval label from a Nationally Recognized Yesting Laboratory (NRTL), a list of which can be attaind from the government office called OSHA (Occupational Safety and Health Administration). The most well known NRTL is UL, and in fact the other NRTLs use the test standards of UL anyway. What you need from UL is a "UL-508" listing. It is very expensive to have UL test a one-off panel, it is far far more effective to hire what's referred to as a "UL-508 shop", who can design and build your panel to meet UL requirements, then apply the necessary label to it. By doing that, you are assured not only of the panel being acceptable to UL, but it will be default meet all NEC requirements. There are thousands of UL-508 shops in the US and Canada, but there are also some spread out across the world. You can go to UL.com to get a list.

Both the NEC and UL-508 contain the rules for the proper selection of MCCBs.

And just for semantic clarity, MCB means "Main Circuit Breaker" over here, not "Molded Circuit Breaker", which would be confusing. So we use MCCB for Molded CASE Circuit Breaker. MCB elsewhere in the world means Miniature Circuit Breaker. the use of OEC style Mini CBs is fraught with issues and pitfalls over here when it comes to UL listings, so I would highly recommend using MCCBs unless you know and understand ALL aspects of the site installation and power system requirements.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Register to Reply 18 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); JRaef (1); juju (5); lyn (3); Paulusgnome (1); PWSlack (3); SHOCKHISCAN (1); Tornado (3)

Previous in Forum: 380v to 480v Transformer   Next in Forum: Lighting Arrester and Lightining Rod

Advertisement