STAR DELTA Connection of a Motor

10/22/2015 7:15 AM

I have a Crompton Parkinson motor NEMA 18.5 Kw, 60Hz, 3 Ph,,460V/Star // 230V Star. It is coupled to a water service pump. it has got 12 leads in the terminal box. Since our system voltage is 460, I connected the motor in Y fashion and running it. it got burnt two times already. The rewinder tells me to connect this motor in 460V delta. as this is not capable of running in STAR 460V. But Name plate of the motor clearly indicates 230 V Delat and 460 V Star. I don't know what to do. can anybody suggest me on what connection I have to run this motor

Register to Reply
Pathfinder Tags: star delta
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#1

Re: STAR DELTA connection of a motor

10/22/2015 7:25 AM

The motor rewinder has told you how to connect it.

If he has rewound it then what makes you think that anyone here would know more than him about how it should be properly connected. It may no longer be wound the same as the original name plate suggests.

I am guessing that since it has burnt out twice already that you are not taking his advice, so you would be unwise to take that of anyone who does not know the motor as intimately as the person who wound it.

Register to Reply
Active Contributor

Join Date: Apr 2010
Posts: 16
#2
In reply to #1

Re: STAR DELTA connection of a motor

10/22/2015 9:07 AM

But The manufacturer is giving the information that motor is to be connected in Y for 460V power.

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#3
In reply to #2

Re: STAR DELTA connection of a motor

10/22/2015 9:59 AM

If the motor rewinder you are referencing to performed a rewind on the motor in question and is telling you to connect the motor in DELTA I would ask why they altered the winding from OEM specifications.

If permission was not given to the rewinder allowing alteration of the motor winding and you need the motor to be dual voltage as per OEM design, I would return the motor to the rewinder and demand the motor be returned to OEM specifications or find a different motor rewinding shop that is willing to do so.

One alternative would be to get the motor winding detail report and a statement of warranty from the rewinder before applying voltage to the motor so that the rewinder is responsible for any/all motor damage. Make sure to get a hardcopy motor connection diagram from the rewinder illustrating details on their directions for making motor connections as this may be a simple misunderstanding and/or confusion.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#4

Re: STAR DELTA Connection of a Motor

10/22/2015 10:21 AM

I guess if you DIDN"T listen the first two times then the third times the CHARM!

Like this one!

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#5

Re: STAR DELTA Connection of a Motor

10/22/2015 12:58 PM

You may be reading the OEM name plate wrong. I have never seen a 230V delta - 460V Wye wound motor before. Not saying such a beast could not exist, just that I have never seen one.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
Canada - Member - New Member

Join Date: Jul 2013
Location: Canada but south of 49
Posts: 895
Good Answers: 20
#16
In reply to #5

Re: STAR DELTA Connection of a Motor

10/23/2015 8:18 AM

Good point. Recheck the name plate. I recently-just last week- changed out a 3 phase motor and having delta in my shop installed the jumpers accordingly based on the wiring configuration in the connection box. Gave me problems of overheating and tripped overload. A closer look at the name plate and delta was the symbol they used for 460 volt 3ph and the Y was for 600 3ph not for the power supply type. Reconfigured the jumpers and voila, no more problems.

__________________
Never stop learning
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: STAR DELTA Connection of a Motor

10/22/2015 1:53 PM

Yes. Crompton Parkinson can and they can do it over the telephone too.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#7

Re: STAR DELTA Connection of a Motor

10/22/2015 4:59 PM

I agree with North of 60 #5. I don't understand 460V/Star // 230V Star. If it's 460V star it would be 460/√3 = 265V delta, or if 460V delta, 460*√3 = 796V star.

If the motor has been rewound as the original, from the nameplate it's most likely 460V/Star is correct, but not certain.

Has it been rewound because it failed in some way? Is it a new installation or has it run OK in the past?

I think you should get the rewinder on site to witness and agree the connection, and take responsibility. And bring his multimeter to check he's happy with the supply voltage!

Maybe there's something wrong with the way the 12 leads are connected to the 6 studs in the terminal box. If so it's down to the rewinder to put it right.

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#8

Re: STAR DELTA Connection of a Motor

10/22/2015 5:56 PM

The numbers 460 star and 230 delta don't match. They should be in ratio of sqrt 3 with each other.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#9

Re: STAR DELTA Connection of a Motor

10/22/2015 10:42 PM

Give us the comlplete nameplate data of the motor.

__________________
pnaban
Register to Reply
Participant

Join Date: Oct 2015
Location: new delhi india
Posts: 3
#10

Re: STAR DELTA Connection of a Motor

10/22/2015 10:47 PM

there are 12 leads. that means, each phase has two windings. these can be connected in series or parallel. in parallel, the machine will work on 230v star. in series, it will work on 460V star.

__________________
Mr SHAM SUNDER GOEL
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#12
In reply to #10

Re: STAR DELTA Connection of a Motor

10/22/2015 11:00 PM

Normally 6 wires are enough for star-delta. 12wires are needed only for dual voltage(220 and 380V)motors like british motors made by GEC. 9 wires are used in US motors. Give us the nameplate data.

__________________
pnaban
Register to Reply
Participant

Join Date: Oct 2015
Location: new delhi india
Posts: 3
#13
In reply to #12

Re: STAR DELTA Connection of a Motor

10/22/2015 11:14 PM

it is already given by original questioner.

__________________
Mr SHAM SUNDER GOEL
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#14
In reply to #13

Re: STAR DELTA Connection of a Motor

10/22/2015 11:33 PM

460 star should work on 230 delta. First run in 460 star check current as per nameplate,if ok connect in delta in 230. If it doesn't work winder has changed something claim damages from him. Name plate should give current rating in 460 as well as 230 star and delta,that's why I asked for it.

__________________
pnaban
Register to Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#11

Re: STAR DELTA Connection of a Motor

10/22/2015 10:54 PM

There is, as the others have said, no way that can be a 460Y/240Delta motor. Impossible by the laws of physics. But here is what I think happened. Compton is an English company. The motor originally would have been wound as a 415Y/240VDelta 50Hz motor, which is how THEY do a dual voltage arrangement.

You can USE s 415V 50Hz motor over here as a 480V 60Hz motor. The V/Hz ratio is close enough so that you will get full torque and not saturate. But you CANNOT use that motor at 240V 60Hz, because the V/Hz ratio is too low and the motor would have insufficient torque, increased slip and pull more current, overloading. So it's likely that at some point after it arrived in this country, someone tried to use it at 240V and smoked it. That lead to it being rewound.

When the U.S. Based rewinder got hold of it, he rewound it to OUR dual voltage standards so that this would not happen again. A dual voltage motor here is NOT done as Y/Delta, it is two sets of windings that you connect in series or parallel. Whether that configuration is Y or Delta is the choice of the rewinder, based on slot geometry, magnet wire size, etc etc. it makes no difference to the user, but you DO have to know.

So most likely the rewinder did know, but you ignored him and second guessed him by what you read on the nameplate. Usually the rewinder would change the nameplate information. If he didn't, fault him for that.

But do as he says.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#15

Re: STAR DELTA Connection of a Motor

10/23/2015 12:28 AM

The Brook Crompton handbook shows a 12 wire "Dahlander connected" pole change dual speed motor. Get the connections mixed up and you're in big trouble.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#17

Re: STAR DELTA Connection of a Motor

10/23/2015 10:41 AM

http://apps.motorboss.com/connections/390880.pdf

Here is a link to clear up the apparent confusion on 12 lead dual voltage Y motor connections.

Please note there are numerous motor connection illustrations available at the motorboss.com website that pretty much cover all standard motor winding types and connections.

From the limited information you provided it appears to me that you have a Y-Y wound motor which the 390880 connection diagram and information should match.

Note:

When the Y-Y motor is connected for high voltage the windings are connected in a Y+Y series configuration which allows maximum winding impedance.

When connected for lower voltage operation the windings are connected in a parallel Y/Y which allows half of motor winding maximum impedance.

It is possible and very easy to connect the motor wrongly.

Motor horsepower/power (P) is a function of current (I) squared multiplied by impedance/resistance (R) or (Z).

The Volts-per-Hertz ratio factor determines developed motor torque and horsepower especially at lower voltage applications.

In the USA at 60HZ the volts-per-hertz ratio for a 460V motor is: 7.6666

For the same motor operated at 50HZ and 460V the ratio is: 9.2

As you can see it is possible to have a 17% loss of power when operating a 50HZ motor at 60HZ.

It may well be that the motor application power requirements are above 83% due to energy efficiency design concerns.

If so, the 50HZ motor is suffering HP loss and high current loading because it cannot produce enough HP to satisfy the application requirements. (This would account for the high incidence of motor failure you are experiencing.)

I suggest you determine the process application motor requirements then purchase a 60HZ, 460V high quality motor that exceeds those requirements by at least 10% to account for occasional operational and mechanical overloading instead of rewinding the existing motor.

Good luck and stay safe.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#18

Re: STAR DELTA Connection of a Motor

10/23/2015 8:25 PM

Your original post has a discrepancy, one place you say 460 star/230 star and another you say 460 star/230 delta. I'm surprised you didn't just tell the rewinder to make the winding interconnections and you just make the final connections. Have you checked the current draw unloaded and under load? Are the overloads sized properly for the motor? And lastly, maybe the motor is over-loaded. If the motor was sized for the pump at 50 Hz and it's running at 60 that would cause a sizable increase in power demand. And if this is a centrifugal pump and it is running at significantly higher flow than design, the power requirement could be also increased.

Register to Reply
Register to Reply 18 comments