Setting The Low Flow Cut Off Magmeter

10/28/2015 12:40 PM

Hello all,

We have a issue in our plant. We have aquametro amflo basic magmeters without display.The issue is we can not detect low flows. The issue is we cant access the meter configuration as it has no display. Is there a way we can solve this issue by tweaking the pcb.I cant think of any other way. Kindly help me out.

Register to Reply
Pathfinder Tags: low flow magmeter
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#1

Re: Setting the low flow cut off Magmeter

10/28/2015 2:00 PM

There is one other way,.... and that is to get a MagMeter that falls in the range you require....

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Setting the low flow cut off Magmeter

10/28/2015 2:40 PM

Get an AMFLO Pro Remote from your favorite supplier:

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#3

Re: Setting the low flow cut off Magmeter

10/28/2015 2:47 PM

If you want help in this forum you must include the meter model number and catalogue number.

Does the meter have connections and capability for installing a remote display or connecting to a DCS or HMI?

Does the meter have a communication port?

Is it HART compatible?

If yes; Connect a HART analyzer with a 250 ohm resistor across the terminal per HART protocol and see if you can access the program.

If you do not know the answers to these questions or all of the answers are "no"; then you need to contact the OEM for help.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4

Re: Setting the low flow cut off Magmeter

10/28/2015 2:57 PM

Save everybody some time.

Go to their website Aquametro - AMFLO® MAG Basic , or call tech service and ask them.

Register to Reply
Commentator

Join Date: Aug 2010
Posts: 56
#5
In reply to #4

Re: Setting the low flow cut off Magmeter

10/28/2015 3:22 PM

Here is the link to the manual. It is blind version. It has no display. Supplier doesnt want to help us as he says these meters are obselete and there is no support.I have around 20 nos of these flow meters so it is not feasible for us to change to a different meter.I need to figure a way out

https://www.dropbox.com/s/ayc9nsbphl7qxbe/Amflo%20light.pdf?dl=0

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7
In reply to #5

Re: Setting the low flow cut off Magmeter

10/28/2015 6:52 PM

Where does the 4-20mA output go?

Why can't you use that?

Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#12
In reply to #7

Re: Setting the low flow cut off Magmeter

10/29/2015 8:14 AM

I can answer that.

If the flow is below the working range of the instrument, the 4-20mA, which is no doubt what they are using for readout since the unit has no display, is just going to read 4ma. (actually, it will probably be 3.91 to 3.93mA or so - typical no detection output of a 4-20mA transmitter) That would appear to be the problem facing the OP.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply Score 1 for Good Answer
3
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#11
In reply to #5

Re: Setting the low flow cut off Magmeter

10/29/2015 7:45 AM

If it is not feasible to change, then you are constrained by the limitations of what is in place.

Eventually you will reach a point where the costs/losses caused by the inadequate meters is greater than the cost for appropriate meters and you will then change them over.

There's an old saying about sows ears not becoming silk purses.

__________________
Just an Engineer from the land down under.
Register to Reply Good Answer (Score 3)
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#6

Re: Setting The Low Flow Cut Off Magmeter

10/28/2015 4:51 PM

What flow GPM? GPD? MGPD?

What size pipe?

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Sep 2015
Posts: 482
#8

Re: Setting The Low Flow Cut Off Magmeter

10/28/2015 9:51 PM

Honeywell and Yamatake has a handheld communicator you can use to monitor readings settings and do calibration. The safest way around is to buy replacement, could be parts or the whole unit. If its intgrated to some HMI, i think it would just be alright so long as it serve its purpose reliably. Read manuals.

__________________
The doctor said "just one post or reply aday in CR4, take it or leave it". I said, "what does that mean?"
Register to Reply
2
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#9

Re: Setting The Low Flow Cut Off Magmeter

10/28/2015 11:49 PM

Magnetic flow meters rely on fluid velocity to create a voltage.

This is created by the fluid moving through a magnetic field.

All mag meters have a minimum velocity(flow) below which they will not work.

Perhaps the low flow you are looking for is below the design limits of the meter.

Look at the size of the meter orifice.

Calculate the velocity of the flow through the orifice you are trying to measure,then

look at the specifications of the meter to determine if it is within range.

If it is below the minimum velocity of the meter,field modification of the unit is not

practical.

Make sure the meter is located in a position to guarantee that it stays full of liquid at

all flow rates.

Air in the measuring portion of the meter will give errors or no readings at

all,depending on the magnitude.

A link to a pdf file by the manufacturer is below.

They spec .04 Meters/Second as minimum flow velocity.

http://www.aquametro.com/data/docs/en/3049/aquametro-6850d-amflo-mag-basic.pdf

Good luck.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10

Re: Setting The Low Flow Cut Off Magmeter

10/29/2015 6:46 AM

Most flow devices have a minimum below which they will not register properly, sometimes given as a "turn-down ratio" of actual flow to maximum flow.

  • If the analog is wired to some electronic control system, then invoke some code that says "if the analog signal is below a minimum set point [i.e. the meter minimum point as shown in the User Manual], then overwrite a zero onto the indicated flow register" and "if the valve in the pipeline is closed then overwrite a zero onto the indicated flow register".
  • If the meter won't register the flow as it is too low, then the pipe is too large and the meter is incorrectly selected for the task.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#13

Re: Setting The Low Flow Cut Off Magmeter

10/29/2015 8:58 AM

Once again I ask.............

What flow GPM? GPD? MGPD?

What size pipe?

What is the model number?

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Aug 2010
Posts: 56
#14
In reply to #13

Re: Setting The Low Flow Cut Off Magmeter

10/29/2015 11:16 AM

Flow is in m3/hr.

Pipe size varies. I have around 20 nos of these shitty meters of various sizes from dn 200 to dn 500 .

Low flow cut off varies depending on the dn.

Register to Reply Score 1 for Off Topic
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#15
In reply to #14

Re: Setting The Low Flow Cut Off Magmeter

10/29/2015 11:39 AM

Ok, Your piping is a bit smaller than what I'm used to working with. We had a 1200 mm dia. pipe that was having trouble measuring low flow.

Our solution was to buy a different meter and sensor that was capable of measuring the flow we needed.

I know this really isn't an answer, but you may need to bite the bullet and buy a different meter for your low flow areas.

Good luck

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#16
In reply to #14

Re: Setting The Low Flow Cut Off Magmeter

10/29/2015 3:00 PM

New issue? Or old issue traced back to the original installation?

If a new issues; What changed?

If old issue; Why was it not corrected during commissioning of the equipment?

In all fairness to the meter manufacturer and supplier:

How old are the devices? If they are past expiration date most likely all will fail soon.

How often are the flow tubes pulled out of service for cleaning and bench calibration testing?

Magnetic flow tubes will scale up causing measurement error that will increase with length of in-service time depending on the fluid being measured.

How critical is the accuracy of measurement to the process?

If critical, I see no viable option other than replacing the units with new equipment.

It might be possible to tweak the controls but how would you know if the meter is function correctly? Or if the measurements will be linear with increased flow?

Changing the zero/low cutoff point could well destroy the accuracy of the meter.

It would be best of the failed/bad devices are replaced with new devices that will maintain accuracy throughout the process required operating range.

Anything short of that is a "crap shoot".

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#17
In reply to #14

Re: Setting The Low Flow Cut Off Magmeter

10/30/2015 7:23 AM

Consider the possibility of the process and plant design being <...sh*tty...> and not the meters in themselves.

  • Several readers have asked for flowrate information and said information has still not been forthcoming. There is no point in having large pipe for small flows.
  • What is in the pipe, its temperature and its pressure are pretty fundamental pieces of data that are also still missing.

Help the forum to provide the help needed, otherwise the entire thread is a complete waste of time and space! <...Sh*tty...> questions get <...sh*tty...> answers!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Aug 2010
Posts: 56
#19
In reply to #17

Re: Setting The Low Flow Cut Off Magmeter

11/04/2015 9:31 AM

I am sorry for not answering the questions. Here are the details.

Flow meter make: Aqua Metro MagproDN: 400Flow below 60 m3/hr are not detected.

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#18
In reply to #14

Re: Setting The Low Flow Cut Off Magmeter

10/30/2015 2:34 PM

You might want to consider a different type of flow meter. Perhaps a D/P orifice plate type would work better for your application.

If you aren't happy with the current vendor, call some others and discuss it with them then compare the gathered information.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Commentator

Join Date: Aug 2010
Posts: 56
#20
In reply to #18

Re: Setting The Low Flow Cut Off Magmeter

11/04/2015 9:37 AM

We have 100 other location where we have used magmeters of different brands (Simens MAg 5100W,Badger and Endress Hauser) and we havent any problems with the meters. There is no problem with the design as I have seen other location with the same set up detect the low flow.This is the problem with the aquametro meters. I have tried to contact the Supplier and he doesnt want to offer us help as we have stopped buying there meters. Kindly let me know

Register to Reply
Power-User

Join Date: Mar 2011
Location: oz
Posts: 252
Good Answers: 10
#21

Re: Setting The Low Flow Cut Off Magmeter

11/09/2015 3:22 PM

To increase the velocity you will need to reduce the size of the flow sensor, you will have to calculate the sensor size for the optimum velocity. It does not matter if the rest of the pipework are different sizes. Your flow rate will be the same.

Register to Reply
Register to Reply 21 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

eltech (1); HiTekRedNek (1); Just an Engineer (1); Legolaz (1); lyn (2); Original_Macgyver (3); phoenix911 (1); Phys (1); plckid (4); PWSlack (2); RAMConsult (1); SHOCKHISCAN (3)

Previous in Forum: Electric Control Valve   Next in Forum: Should I fit Y Strainer to Mains Water Supply?

Advertisement