Worst-Case Scenario for Asymmetrical Current

11/10/2015 8:31 PM

Hi All,

According to the attached graph, asymmetrical current is highest when symmetrical current is at around -.85pu. Could this also be worst case scenario when the symmetrical current is at around 1pu?

Thanks!

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Worst case scenario for asymmetrical current

11/10/2015 10:46 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#2

Re: Worst-Case Scenario for Asymmetrical Current

11/11/2015 5:18 AM

You need to talk with your 1st level professor. There is something you are missing. Really.

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#3

Re: Worst-Case Scenario for Asymmetrical Current

11/11/2015 7:04 AM

Looking at the graph, the DC current is maximum at the origin and the symmetrical current at this time is ~-0.85. I cannot understand your statement about assymetric current curve on the graph. Please clarify.

Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#4

Re: Worst-Case Scenario for Asymmetrical Current

11/11/2015 10:16 AM

Looking at the graph you provided, the symmetrical current is at maximum peak value of 1 p.u. at approximately the 0.385 cycles time period and the asymmetrical current waveforms are at maximum peak value of 1.25 p.u. at approximately the 0.375 cycles time period.

The time period you have indicated with the green arrow at .5 cycles indicates the symmetrical current maximum value is at 0.87 p.u. and the asymmetrical current value is at approximately 1.1 p.u..

The graph clearly illustrates both symmetrical and asymmetrical current values peaked well before the 0.5 cycles time period and have begun to decrease rapidly.

These facts render your argument incorrect.

The next time period wherein the symmetrical and asymmetrical current reach maximum values is in the negative voltage region time period of 0.75-0.85 cycles however the maximum value for both are less than 1 p.u.

You very much need to review interpretation of graphs and master the procedure if you want to be successful in this field of study.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Reply
Participant

Join Date: Nov 2015
Posts: 2
#5
In reply to #4

Re: Worst-Case Scenario for Asymmetrical Current

11/11/2015 1:53 PM

Thank you all for your help. We know, Asymmetrical Current = Symmetrical Current + DC offset. Now the higher the value of Symmetrical Current, the higher the value of Asymmetrical current. When we do arc flash study, we try to assume the worst case scenario for asymmetrical current, which happens to be at voltage zero and symmetrical current at negative peak (according to multiple souces). My questioin is, why don't we consider the very next peak when the voltage is zero but the symmetrical current is at it's positive peak? Shouldn't we get a higher asymmetrical current for the latter case?

I think I am overlooking something. If someone can please point out what, I'd be grateful.

Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#8
In reply to #5

Re: Worst-Case Scenario for Asymmetrical Current

11/12/2015 9:05 AM

Dear Sadia27,

I guess you are the person who made the "Original Post" question as "Anonymous", so welcome to CR4.

I have a feeling that when you look at the graph, your mind tells you the "DC current" is asymmetric.

Well, it is, since it is positive polarity only - the other curves are cyclic and swing positive and negative!

Confusingly, the actual current (from the mathematical transient solution, it is the sum of the steady-state sinusoid and the exponential current which is positive only - on your example graph) is labelled "Asymmetric current".

There are some, often used, habits of "use of words" here which can be confusing.

One is that DC is often used to describe a current or voltage of one polarity, even if it has complicated changes of magnitude - to contrast it with alternating values which look "sinusoid" in power engineering (speech or music waveforms rarely do).

Another is that waveforms which look like a distorted "sine wave" with one half cycle different to the other are often called "asymmetric" (a wave can have identical positive and negative shapes - symmetric, even though it has the appearance of a distorted sine wave).

I guess these uses of words have become a habit in power engineering because the voltage and current are supposed to be sinusoidal at 50 or 60 Hz and trouble results when they are not.

One example, needing the kind of analysis you have posted, is the effect on breakers of the DC current which can occur, depending on the point in the voltage wave at which the contacts close [or a short circuit fault occurs].

Another is that, in the early days of AC power, difficulty was found in parallel operation or even connection of generators of different size and design, which led to the specification of very close to sinusoidal waveforms for generators rather than the distorted outputs causing the trouble. If you wonder how they managed to determine waveform without ultra-violet chart recorders or oscilloscopes, I can tell you (because I have an ancient textbook that told me!).

Thinking of your words in this post "worst case scenario....at zero voltage and symmetrical current at negative peak", I wonder if you are thinking the DC component and the symmetrical component can be independently chosen.

This is not true, they both come from the mathematical solution.

Thinking fundamentally, the initial current in a newly closed circuit must always be zero - and in a mostly inductive circuit it can only increase at a limited rate. So it is essential that at time zero the theoretical DC current and symmetric sinusoid have equal and opposite magnitudes.

Note that the symmetrical current is at its peak at voltage zero only for an inductor with no resistance, your graphical example is for low L/R values applying to normal loads of high power factor - the DC component is negligible by the second half cycle.

You are correct to wonder if a later half cycle might be worse than the first, but since the peaks of the sinusoid are always the same magnitude and the total current only increased by the exponential which always falls with time, I think you will agree the first half cycle current peak is always greatest.

I suggest you investigate the currents when energising transformer primaries or short circuiting generators at their terminals. In both these cases the L/R time constant for the DC current is much longer than for usual loads and several cycles can be very offset by the DC component.

67model

Reply Score 1 for Good Answer
Participant

Join Date: Nov 2015
Posts: 2
#12
In reply to #8

Re: Worst-Case Scenario for Asymmetrical Current

11/12/2015 2:16 PM

Thank you 67model for taking the time to explain. I greatly appreciate your help!

Reply Off Topic (Score 5)
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9913
Good Answers: 1141
#6

Re: Worst-Case Scenario for Asymmetrical Current

11/11/2015 2:02 PM

If you apply AC voltage to an inductor, after steady state is achieved, the current will lag the voltage by 90 degrees (symmetrical current). On startup, the current is initially in phase as shown (asymmetrical current), and the difference is a "dc current" as shown. It's not "at the same time" as the symmetrical current. One is shown on startup and the other is steady state in relationship to the voltage waveform.

Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#7

Re: Worst-Case Scenario for Asymmetrical Current

11/12/2015 1:43 AM

Another homework question because the OP slept in class. No thanks!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#9
In reply to #7

Re: Worst-Case Scenario for Asymmetrical Current

11/12/2015 11:05 AM

This does indeed sound like a student's question, but sleeping in class is not the only reason for seeking outside help. I still remember, from well over 50 years ago, a professor saying: "And therefore, obviously, ,,,". Whatever it was that followed, was NOT obvious to me, and I was too meek and/or stupid to speak up and say so. If the internet had existed then, I would have definitely have looked there for assistance.

If this were really homework, some value would have to be calculated. As I see it, the student is simply seeking help understanding a concept, and I see no problem with that! At 75, I'm definitely a student when it comes to large reactive loads on AC circuits, so I was/am looking at the thread, hoping to add a bit more knowledge to my level of understanding.

I still don't know what the vertical axis "p.u." stands for.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Reply Score 1 for Good Answer
2
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#10
In reply to #9

Re: Worst-Case Scenario for Asymmetrical Current

11/12/2015 12:17 PM

dkwarner,

p.u. stands for "per unit". It is power system engineer's jargon brought on by analysing systems with dozens of generators, transformers and loads. To simplify the system simulation model, everything is transposed to one voltage level (if possible) and multiples of a convenient unit easy to set on a simulation rig (could be real scaled generators, inductors, resistors, capacitors) or analog computer e.g. Rated current, voltage of biggest generator are both scaled to 1.0 (and thus its rated power is 1.0 VA corresponding to an actual "base value" of e.g. 100 MVA) and all other values are scaled to same units. When the simulation results come out, it is easy to see that an 0.1 pu rated transfo at 2 p.u. current is getting 20 x rated current etc.

In this example, 1 p.u. seems to be the peak voltage or current of the symmetrical (steady state, settled) component. Since a sine wave has a basic peak value of 1, e.g. V = sin(wt), this is simplest unit to use.

67model

Reply Good Answer (Score 2)
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#11
In reply to #10

Re: Worst-Case Scenario for Asymmetrical Current

11/12/2015 12:24 PM

Thanks! After reading that three times, it is starting to make sense!

Dick

__________________
Teaching is a great experience, but there is no better teacher than experience.
Reply
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#13

Re: Worst-Case Scenario for Asymmetrical Current

11/12/2015 4:27 PM

No. The graph looks the way it does because of the initial conditions at the initiation of the fault, moving to the right simply shows how the current changes as time goes by. What you are proposing is picking and choosing where on the graph and/or which component of the current to use as "the" current for your study, when in fact the fault is defined as occurring at t=0, you can't then move the fault to have it occur later in time.

Please note that although three lines are plotted on this graph, in reality only one current exists, namely the Asymmetric Current, which is simply the superposition of the normal current waveform with the exponentially declining DC offset. Also note that the graph shows that the magnitude of the current will always reach its maximum value within the first half cycle.

A little history might help. Remember that the study of AC power systems started early in the 20th centuries long before there were computers, and computations were done using differential equations, graphs, log tables, nomographs, and mechanical calculators. In order to simplify the work when repetitive calculations were needed, a few people developed techniques that could be applied by anyone that was facing a similar problem, without the need to use the higher math that went into the original solution.

Differential equations are needed for a rigorous solution to this problem, when used, there will be a constant in the form of an exponential that is part of the solution that gets added to the sinusoidal portion of the solution. This constant was named the "DC offset" because it accurately described what was being observed and was easy for the engineers to identify with, not because DC was somehow injected into an AC circuit.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply Good Answer (Score 2)
Reply to Forum Thread 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (3); Andy Germany (1); dkwarner (2); Mikerho (1); RAMConsult (1); Rixter (1); Sadia27 (2); SHOCKHISCAN (1); SolarEagle (1)