Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73

Pesky "Overvoltage" Warnings in Servo Drive

11/16/2015 11:05 AM

I had a problem with a number of servo drives shutting down due to "Over Voltage" warnings that I finally solved. As it turns out, there are several ways to approach the issue but I only tried two methods before I was successful. While investigating, I realized that the servo drives could not measure the incoming AC voltage, it could only measure the captured DC voltage. Then it calculated the apparent AC voltage and freaked out. I was apparently capturing enough peak energy to raise the DC voltage above the maximum threshold for operation.

The first approach involved the installation of Line Reactors and in some cases, it worked. Unfortunately, I still had shutdowns after midnight even though the incoming AC was within its 10% tolerance level. Input voltage was 3 phase, 480 V, 60 Hz. The shutdowns were infrequent, but very annoying.

Since I couldn't adjust the software settings for the supply voltage any higher, I finally realized that the next logical step was to reduce the voltage rather than trace down all of the existing or future harmonic contributors on the same substation.

I considered resetting the taps on the substation but it would have been an expensive and risky approach since other equipment might be negatively affected by the reduced supply voltage. I also knew that I had some harmonics loose in the substation but I wasn't about to spend the money it would have taken to squash the harmonics.

Finally, I bought step-down transformers that were rated to operate as autotransformer's. By feeding the AC supply to all coils in series, I could take off a reduced voltage on the primary coils (also in series) and I've not had any other problems since. My only question was whether or not I skipped an approach that would have saved me some money.

I had 10 Servo Drives on the same substation, so it took 30 transformers to solve the problem at about $95 per transformer. Total cost (not including labor) was about $950.

My question is this: Could I have done something less expensive and had as good of a result? I think the answer is NO.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Pesky "Overvoltage" warnings in Servo Drive

11/16/2015 11:30 AM

I've had servo drive over-voltage problems due to regeneration with high deceleration values. The higher the AC in, the higher the DC bus voltage and the narrower the margin before over-voltage gets triggered. Have you got that covered?

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Good Answer (Score 2)
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#2
In reply to #1

Re: Pesky "Overvoltage" warnings in Servo Drive

11/16/2015 12:03 PM

In my application, the motors (about 1200W) and inertia were very small and fortunately regeneration was not the issue. That being said, I'd have to say that I have not got that covered in this case. I'll tuck that away in my list of things to consider! Thanks for your reply!

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Pesky "Overvoltage" Warnings in Servo Drive

11/16/2015 2:13 PM

Could it have been possible to power these motors from a single buck/boost transformer, or did locations dictate the multiple transformers?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#4

Re: Pesky "Overvoltage" Warnings in Servo Drive

11/16/2015 11:24 PM

To me it sounds like a good fix.

If you had used a single large transformer, there might have been some reactions between units.

There is no single point of failure with each having its own transformer. A good move.

Do keep an eye on cooling, its winter now, but think "summer" as well.....

It sounds like a cheap and good fix to me!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#5

Re: Pesky "Overvoltage" Warnings in Servo Drive

11/17/2015 9:07 AM

Excellent cost effective solution. Great job!

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Andy Germany (1); JohnDG (1); NotUrOrdinaryJoe (1); SHOCKHISCAN (1); Tornado (1)

Previous in Forum: Smart Phone Apps Wanted!   Next in Forum: Voip - Quality or Junk?

Advertisement