I am facing a problem which one can never think off !
In one of the machine, there is installation of Mitsubishi make 110 V AC 50 Hz coil.
One day there was failure of this contactor and I replaced this contactor with Schneider make contactor of same to same rating.
But machine not started because as soon as contactor pick ups, machine generates error code.
I could not understand the reason , finally I have replace the same with Mitsubishi make.
Only differance I observed that, coil resistance (with multimeter) :
Mitsubishi = 75 Ohms ; Schneider = 120 Ohms.
Again I have taken the trial with FINDER make relay but again same problem observed becasue Finder relay coil was 1.2 Kohms
Now, It is concluded that, the coil from where it is operated (PLC) is checking the impedance of the coil...but how it is possbile ?
And if want to measure impedance of original coil, what is the procedure ?
Pls help me out.