Sizing VFD for Slip Ring Motor

12/18/2015 1:48 AM

Hello,

I need to use VFD for Slip ring motor. How we size VFD for the slip ring motor?

Is VFD sizing is same as squirrel cage induction motor?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Sizing VFD for slip ring motor

12/18/2015 3:49 AM
Register to Reply Score 1 for Off Topic
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#3
In reply to #1

Re: Sizing VFD for slip ring motor

12/18/2015 4:35 AM

I think you will find that link is actually about replacing a slip ring motor with a standard squirrel cage motor and VFD.

While that is not what the OP wanted, it is most likely the best way to go.

If converting a slip ring motor to VFD, you would first need to short the rotor bars, and this would best be done so that the brushes are made redundant, otherwise they will still need to be maintained.

You would also want to be a bit careful of the condition of the motor as VFDs can impose pretty harsh voltage spikes on an old motor's insulation. Possibly a dV/dT filter would reduce the risk here.

As for sizing, I seem to recall that converting a slip ring motor to VFD operation will result in a loss of around 25% starting torque. Perhaps others can confirm or deny this.

Register to Reply
Member

Join Date: Dec 2015
Posts: 6
#4
In reply to #3

Re: Sizing VFD for slip ring motor

12/18/2015 4:43 AM

I have 129 Kw slip ring motor.is it ok to select 132 Kw VFD drive?

Register to Reply Score 2 for Off Topic
Power-User

Join Date: Jan 2015
Location: Johannesburg, South Africa
Posts: 248
Good Answers: 3
#14
In reply to #4

Re: Sizing VFD for slip ring motor

12/19/2015 3:41 PM

NO

__________________
Tragedy for Engineers is thinking they know so much that they can not learn from any body else.
Register to Reply
Member

Join Date: Dec 2015
Posts: 6
#2

Re: Sizing VFD for slip ring motor

12/18/2015 4:09 AM

I have 129 Kw slip ring motor.is it ok to select 132 Kw VFD drive?

Register to Reply Score 2 for Off Topic
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#5
In reply to #2

Re: Sizing VFD for slip ring motor

12/18/2015 5:01 AM

I suggest you ask the VFD manufacturer or supplier.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6
In reply to #2

Re: Sizing VFD for slip ring motor

12/18/2015 8:52 AM
Register to Reply Score 1 for Off Topic
Power-User

Join Date: Jan 2015
Location: Johannesburg, South Africa
Posts: 248
Good Answers: 3
#15
In reply to #2

Re: Sizing VFD for slip ring motor

12/19/2015 3:45 PM

NO, NO Read the advice given, it is not just sizing a VFD, collect the information suggested and get a reputable VFD supplier to advice you and also do the installation for you and the programming.

__________________
Tragedy for Engineers is thinking they know so much that they can not learn from any body else.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#7

Re: Sizing VFD for Slip Ring Motor

12/18/2015 9:22 AM

Shorting the rotor will cause problems starting due to low torque.

You can get VSD's designed for slipring current control.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#8

Re: Sizing VFD for Slip Ring Motor

12/18/2015 10:01 AM

I suggest you contact the VFD manufacturers of your choice and solicit their input.

If you want to ensure best case performance I suggest soliciting input from at least three (3) separate/different VFD field application service groups to obtain good solid information for comparison and decision making.

Some wound rotor motors utilize shorting of the windings during the starting cycle to provide enough torque for the application without overloading the motor.

If the motor you are using has this type of capability then it may be possible to permanently short the windings and remove the slip rings to lower maintenance cost.

If the existing motor and control does not utilize rotor winding shorting during the start cycle then you may have to replace the wound rotor motor with a high efficient squirrel cage motor.

If you are unsure about what type of motor and/or motor control is present, I suggest you contact the original motor manufacturer and get their input and advice.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#9

Re: Sizing VFD for Slip Ring Motor

12/18/2015 10:56 AM

Repeating the same question over and over in the face of reasonable answers is rude. You are essentially saying "You must be too stupid to understand what I am asking so I will say it again and again until you do." You have the answers, now act upon it accordingly.

And because apparently it is YOU that is having a difficult time understanding, here it is again. There is more to this than simply sizing the VFD. Find a supplier you trust and ask THEM what they recommend. Some VFDs can handle this, some cannot. My company makes 4 different VFD product lines. Two of them would have no issues, one would need to be seriously over sized, one of them would not work at all.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#10

Re: Sizing VFD for Slip Ring Motor

12/18/2015 11:28 PM

a few the questions..

Why do you need a VFD, because when you change the impedance connected to the rotor circuit on the slip ring motor, the speed/current and speed/torque curves can be altered of the motor you already have? YES? So why change to a VFD now?

Why do you insist to keeping the original motor? The advice you have asked for and got is sound and practical. Change the motor!

Is the slip ring motor rated for VFD operation? I somehow doubt it!

__________________
The square root of nothing is what you make it!
Register to Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#11
In reply to #10

Re: Sizing VFD for Slip Ring Motor

12/19/2015 7:21 AM

Perhaps TS is going to use the slipring motor as a double fed induction generator...

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#13
In reply to #11

Re: Sizing VFD for Slip Ring Motor

12/19/2015 2:23 PM

perhaps.. but I doubt it!

__________________
The square root of nothing is what you make it!
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#12

Re: Sizing VFD for Slip Ring Motor

12/19/2015 7:52 AM

Dear Mr. Lalinda,

To use the existing motor for VFD application you have to check or arrange the following.

1. One bearing of the motor on coupling side or the the other side, you should have INSULATED BEARING or BEARING INSULATION, to avoid shaft current circulation.

2. Cooling Fan of the motor - when speed reduces the air blown will be reduced and hence a seperate and independent blower is required to keep the motor winding/body temp. with in limit.

3. A dedicated Earthing OF 2.5 TIMES NORMAL TO BE PROVIDED FOR THE VFD which means no other equiment should be connected to this Earthing.

Perhaps you have decided to use the existing slip ring motor for which you have to short the rotor to make it as a squirrel cage rotor.

Pl. note the starting torque will be less than the normal slip ring motor and hence take care of starting.

DHAYANANDHAN.S

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#16

Re: Sizing VFD for Slip Ring Motor

12/19/2015 4:29 PM

<...We...> pick up the phone and <...we...> speak to the VFD manufacturer, who, on being given the motor details, will provide <...we...> with a quotation to supply the right one.

Next!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#17

Re: Sizing VFD for Slip Ring Motor

12/19/2015 9:56 PM

Friends,

In the 1990's, when I worked for a water and wastewater utility we had a number of wound rotor motors (slip ring motors) that were in sewage lift stations with "Flowmatcher" type of controls (slip rings connected to copper bus bars that sat in a tank, in which the level of the salt solution was continuously controlled by the level of sewage in the wet well). They worked well, but the maintenance of all the components was very time consuming. We switched them all to VFD controls as follows:

  1. All VFD's were chosen at a typical 50% oversize (to allow operation at 50-deg C with no loss of expected life).
  2. All slip rings were shorted together and the brushes and brush holders removed.
  3. Line and load reactors were always used (typically 2 or 3%), to protect the motors from dv/dt spikes.
  4. Motor lead lengths were typically 50-feet (16-meters) or less, but never over twice this distance.
  5. Grounding of the rotor shaft through brushes or rings was not done (no one in our area was aware of this topic then). Now, I would use them as a firm rule.

We had no problems. You don't tell us what the application is, so we can only guess. The advice from others is valid--ask the manufacturer to help you in selecting the proper VFD (size and style).

--John M.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#18
In reply to #17

Re: Sizing VFD for Slip Ring Motor

12/22/2015 2:51 PM

Flowmatcher is still around!

I visited them a few years ago, I don't think there was anyone in that company under 60 years old, it was like a retirement home for electrical engineers. They only sell 3 or 4 systems per year now, but I guess it's enough to keep them in business.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Register to Reply 18 comments

"Almost" Good Answers: