Dear Electrical Engineers,
I am facing an issue in momentarily parallel operation of two similar transformers. Problem is that while checking voltages between R-R, Y-Y and B-B phase of transformers, it is not equal or near to ZERO. Values measured are as follows:
R1-R2 = 244V, R1-Y2 = 493V, R1-B2 = 247V
Y1-R2 = 248V, Y1-Y2 = 243V, Y1-B2 = 493V
B1-R2 = 493V, B1-Y2 = 248V, B1-B2 = 245V,
All possible checks has been done. Kindly suggest the reason for the issue. All other transformers of similar specifications at plant has been checked for parallel operation and are working fine.
Detail of transformers is as follows (Both have same details):
|
Make | Voltamp |
|
Capacity | 2500 KVA |
|
Voltage | 22 / 0.415 KV |
|
Current HV | 65.61 Amp |
|
Current LV | 3478.01 Amp |
|
Phase | 3 |
|
Connection | DeIta / star |
|
Cooling | ONAN |
|
sl.no | IN 4797 / 13 |
|
Vector group | Dyn 11 |
|
Impedance
volt. | 7.89% |