Previous in Forum: Allowable Stress Table For SA213-T23   Next in Forum: Hot Water Electric Boiler 600 Gallons Heater Burst
CRAJ
01/14/2016 6:13 AM
What is the value of Alpha in the formula, in Form T- 0240 section 3.3 (fluid) for calculating the mionimum safety distance in hydraulic pressure testing.
Re: CRAJ
01/14/2016 6:42 AM
42
Re: CRAJ
01/14/2016 8:39 AM
Is that 42 parsecs?
Good Answers: 76
Re: CRAJ
01/14/2016 10:11 AM
To better assist us in answering your question, you should provide more information... you know... something like linking the standard you reference:
http://www.wermac.org/others/ndt_pressure_testing_safedistance.html
This way, you're more likely to get a decent answer.
Re: CRAJ
01/14/2016 10:32 AM
GIGO*.
*Garbage in-Garbage out!
Good Answers: 76
Re: CRAJ
01/14/2016 11:02 AM
Looks like this isn't the first time its come up:
http://cr4.globalspec.com/thread/17841/safe-distance-for-pressure-testing
To the OP... contact Loyd's Register and ask them:
http://www.lr.org/en/contact-us/
Re: CRAJ
01/14/2016 12:54 PM
For fluids (3.3) it is :l = 0.15 x internal diameter x ((max workable distance) ^ 0.4) x ((test pressure / (cube root of density))^ 0.6
Register to Reply 6 comments
JavaHead (2); lyn (2); PWSlack (1); SolarEagle (1)