Replacement of Stolen Earthing Copper Tape.

07/27/2007 3:29 PM

Hi Everyone

The earthing copper tape inside our ring main substations in being stolen. Anytime we replace them they get stolen again. I'm looking for another solution such as copper clad steel wire or copper clad aluminium wire which are worthless for thievs but I dont know how successfull I'm going to be with that. my questions are:

1) Is it true that grounding copper tape can be replaced by copper clad steel wire?

2) Any suggested manufacturers?

B. Regards

Register to Reply
Pathfinder Tags: earth ground substation
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jan 2007
Location: Sitting directly behind my keyboard in Albuquerque - USA
Posts: 592
Good Answers: 19
#1

Re: Replacement of Stolen Earthing Copper Tape.

07/27/2007 11:24 PM

One night swap 'em out for a phase. End of problem.

__________________
If it eats, it's going to be trouble!
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#2
In reply to #1

Re: Replacement of Stolen Earthing Copper Tape.

07/28/2007 12:17 AM

Earthing can be done in GI also.Since GI is cost effective pilferage will not take place in GI.Only thing is cross section of GI will be different for GI and it should carry the fault current.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Active Contributor

Join Date: Apr 2007
Posts: 19
#3

Re: Replacement of Stolen Earthing Copper Tape.

07/28/2007 12:28 AM

Hi There Enq.alasad, Im no expert on this matter but I know that in QLD in the land of OZ copper coated steel rods are commonly used as earthing rods, usually 1800mm long.

I would guess that different soil types would detirmine the type of earthing rod?

coben

Register to Reply
Commentator

Join Date: Apr 2005
Location: Phoenix, AZ
Posts: 82
Good Answers: 3
#4

Re: Replacement of Stolen Earthing Copper Tape.

07/28/2007 1:54 AM

The problem with the scenario of getting the tape stolen and replacing it with something else is the symptom, not the solution. The solution is to make the area where the tape is unaccessable. Anything short of that, you are kidding yourself.

I guess it depends on your location, but here, copper tape is not held in high regard and/or skirts code.

Register to Reply
Anonymous Poster
#5

Re: Replacement of Stolen Earthing Copper Tape.

07/28/2007 5:38 AM

Copper coated steel rods are permitted for drivng earth electrodes into the ground subject to accaetabe resistance values - in the UK copper coated steel is not permitted as an earthing earthing conductor although it is permitted as a bonding conductor.

Ultimately it depends on the acceptable standards of you own individual country.

Register to Reply
Power-User

Join Date: Jun 2006
Location: Boston Massachusetts U.S.A.
Posts: 398
Good Answers: 4
#6
In reply to #5

Re: Replacement of Stolen Earthing Copper Tape.

07/28/2007 10:33 AM

I like the idea of a deterrent energizing the door would be fun .Maybe an electric fence voltage .

__________________
Lighten up
Register to Reply
Member
United States - Member - Old Member

Join Date: Jul 2007
Location: San Antonio, TX
Posts: 7
#7

Re: Replacement of Stolen Earthing Copper Tape.

07/28/2007 3:46 PM

Electrical substations are not my area of expertise so might I suggest a different tact?

Install a miniature, covert video camera, digital recorder (supercircuits.com) and catch the thieves.

__________________
Hello ? Is this the person to whom I'm speaking ? (phone humor)
Register to Reply
Member

Join Date: Jul 2007
Posts: 8
#8

Re: Replacement of Stolen Earthing Copper Tape.

07/28/2007 7:56 PM

Im talking about 2000 substations out of 10000 substations were stollen.. I have thought about the fence or the camera but we are talking here about huge quantity. Whenever we catch agroup of thievs we find another group of thievs...and so on.

Register to Reply
Power-User

Join Date: Jan 2007
Location: Johannesburg, South Africa
Posts: 230
Good Answers: 16
#9
In reply to #8

Re: Replacement of Stolen Earthing Copper Tape.

07/31/2007 2:58 AM

We have a similar problem in South Africa. Anything copper gets stolen. We use composite bonding conductors, which consists of copper strands surrounded/interwoven by steel strands. It is currently too much hassle to separate the two, as scrap dealers only take pure copper. We are also looking at remote monitoring, but the remote locations and distance from security forces remains a problem - these guys are quick.

In the HV yard of substations. we use flat steel bar of about 5 times the size of the copper rods previously used. Our bosses are not too happy, but I reckon to at least have some protection guaranteed than perfect protection guaranteed to be stolen.

And like Eng.alasad, there are an infinite supply of desperate people to take over from the guys that are caught. We have replaced all our copper overhead cables (electrified railways) in my area with ACSR (Aluminium COnductor - Steel Re-inforced), as these pose the same challenge to the thieves. Now they are stealing the 3kV DC feeder cables....... We are now encasing it in concrete. That gets chopped up too, so now we are reinforcing the concrete. We'll see what's next.

Register to Reply
Anonymous Poster
#10
In reply to #9

Re: Replacement of Stolen Earthing Copper Tape.

07/31/2007 3:57 AM

I was under the impression that the copper stealing was prevailing only in our place, it looks from the response, this is common internationally.

Register to Reply
Associate

Join Date: May 2007
Location: Somewhere in Texas
Posts: 29
Good Answers: 2
#11

Re: Replacement of Stolen Earthing Copper Tape.

08/01/2007 1:49 PM

I build substations for one of the major US electrical utilities. We have a major problem with copper theft. Have tried many methods to minimize thefts.

1. Copperweld conductors- from the grounding/earthing point of the structure to the copper grid underground.

2. Attemts at disguising or hiding the copper from sight. i.e. painting, shrouding, and covering with concrete covers.

We have yet to be able to stop the intrusions. The only ones we catch are the ones that mistakenly cut the neutrals from the transformers. They get stopped rather quickly and permanently.

Illigetimi non carborundum

__________________
Illegitimi non Carborundum.
Register to Reply
Anonymous Poster
#12

Re: Replacement of Stolen Earthing Copper Tape.

08/01/2007 9:04 PM

Try embeding the tape in a porous cinder concrete.

It will be effective and hard to remove.

Register to Reply
Power-User

Join Date: Oct 2006
Posts: 139
#13

Re: Replacement of Stolen Earthing Copper Tape.

08/02/2007 5:56 PM

Suggested manufacturer Copperhead wire www.copperheadwire.com represented by UPSCO Moravia NY Dan Pajak 315/497-1070.

Register to Reply