Is it safe to use a 15hp VFD TO drive a 15 HP induction motor, inverter duty?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Jul 2007
Location: Toronto
Posts: 14
#1

Re: VFD

07/27/2007 11:39 PM

What is your load cycle? How much is maximum and average loading on your motor? What are over load chances? What is application?

Reply
Anonymous Poster
#2
In reply to #1

Re: VFD

07/27/2007 11:53 PM

Motor is used as a mixer to mix 200 gallons of paint

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: VFD

07/28/2007 3:32 AM

Just out of curiosity, why would you think they would put a label that says "15HP" if it was not intended to be used on a 15HP motor?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Anonymous Poster
#4

Re: VFD

07/28/2007 9:13 AM

Its safe but not advisable. You need to give the VSD an allowance of 15 to 25% above the rating of the drive (Motor) so that when your motor is running at FL it will not be straining( lack of a better terminology) the VSD.

But if you your load diversity, and the motor will not be running at FL all the time, you can you the same rating of VSD as that of Motor for economical reasons.

To get the best performance always refer to the manufacturer manuals.

Hope this helps.

Reply
Anonymous Poster
#7
In reply to #4

Re: VFD

07/28/2007 11:31 PM

Sometimes I am so happy that I work for a VFD manufacturer. Statements such as this mean I get to sell needlessly oversized VFds!

Reply
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#9
In reply to #7

Re: VFD

07/28/2007 11:51 PM

yup

depending on the # of starts & Stops, ventilation of the VFD [ambient temp], other than allan bradley most brands will run @ 125% of FLA [full load amps].

Reply
Associate

Join Date: Jun 2007
Location: Dubai, U.A.E.
Posts: 25
#13
In reply to #4

Re: VFD

07/29/2007 4:47 AM

"safe"? "advisable"?

If it's safe, then why in the world will it not be advisable?

Reply
Anonymous Poster
#5

Re: VFD

07/28/2007 10:16 AM

Thanks to all

Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#6

Re: VFD

07/28/2007 11:30 AM

The motor is used in driving a mixer.So how many cycles per hour.The motor will start accelerate ,run at full speed ,coast to stop.If this is correct u need the time for each portion and arrive at the rating .However a 20% margin should be safe .

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply
Anonymous Poster
#8

Re: VFD

07/28/2007 11:49 PM

YES

Reply
Guru

Join Date: Apr 2007
Location: Hyderabad, India
Posts: 596
Good Answers: 12
#10

Re: VFD

07/29/2007 12:45 AM

yes, without any hesitation.

__________________
Subramanyam
Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#11

Re: VFD

07/29/2007 2:40 AM

All (North American) VFD's rated 15HP will run 15 HP motors. That is why they are name plated 15HP.

If you look at the specs you will discover there is usually a short term overload capability, that can be as high as 150% for 1 minute. Others will be 125% for 1 minute, 150% for x seconds etc. You are playing with the I^2xT thermal capacity of the devices.

The other thing to note is if the 15HP VFD is the same frame size as a higher HP unit, or is it the largest HP for that frame? Checking the spare parts list will also give an indication to what the reserve capacity of the drive is.

Reply
Associate

Join Date: Jun 2007
Location: Dubai, U.A.E.
Posts: 25
#12
In reply to #11

Re: VFD

07/29/2007 4:45 AM

I agree.

I certainly will not buy any VFD without this capability.

Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#16
In reply to #11

Re: VFD

07/30/2007 9:43 PM

Good thoughts, regarding VFD frame sizes. Usually the catalog numbers will indicate the frame sizes, if not, then the specification pages will tell you the physical dimensions, so you can see what ratings are in a single frame size.

One possible case where it won't drive that motor is if the motor's nameplate amps is above the VFD's nameplate amps, which can happen at times.

One caution about using the same VFD size as the motor size--if the ambient temperature is high, then the VFD's electronics will have a derated life span. Under these circumstances oversizing the VFD can avoid this shortened life span, but checking with the manufacturer's engineering people would be good.

JMM

Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#14

Re: VFD

07/29/2007 6:04 AM

Should be-if somebody capable designed the Inverter Circuit.

Stand near the drive.Try all speeds-while keeping Overload Trip Circuits tuned to 80%

Reply
Associate

Join Date: Jun 2007
Location: Lexington, Kentucky, USA
Posts: 33
#15

Re: VFD

07/30/2007 7:46 AM

Yes, there is no problem.

__________________
"A designer knows he has achieved perfection not when there is nothing left to add, but when there is nothing left to take away." Antoine de, Sant-Exupery
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#17

Re: VFD

10/07/2009 10:32 AM

Please keep a watch on the ampere loading of the VSD and the overload withstand capability of the VSD as well.

Reply
Reply to Forum Thread 17 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (5); electricalexpert65 (1); Ezekiel49 (2); Garthh (1); GW (1); hareshptl (1); jmueller (1); JRaef (1); kvsubramanyam (1); MrRoboto (1); MUKULMAHANT (1); nesubra (1)

Previous in Forum: Replacement of Stolen Earthing Copper Tape.   Next in Forum: starter design
You might be interested in: Induction Heaters, AC Motors, DC to AC Converter Chips

Advertisement