01/27/2016 2:24 AM
Hello,
We have a 13.8 kV, 50MW alternator, which will be connected to GCB through Bus Duct.
Is there any specification / rule of thumb which decides the clearance / distance between line cubical of Generator & GCB ?
Would 3 meters distance be OK ?
Please share your experience
Thanks & Regards
Re: Clearance between Generator and GCB
01/27/2016 4:58 AM
This sort of thing tends to depend on local or regional regulations. You didn't specify your locale, and not too many of us may just so happen to have a copy of your local rules, anyway.
Good Answers: 444
Re: Clearance Between Generator and GCB
01/27/2016 12:04 PM
1. No specs, just half way between generator and transformer
2. Sure, but is it half way?
3. My experience is that anyone that would design a multimillion dollar generator/transformer installation based upon information from anonymous strangers on the web should definitely be fired ASAP.
01/27/2016 5:31 PM
<...GCB...>?
Good Answers: 444
01/27/2016 7:45 PM
Generator Circuit Breaker, usually only found on smaller machines since the interrupting current capacities are very high as are the short circuit duties and mechanical withstand forces.
02/03/2016 1:23 AM
There is no thumb rule, the clearance is dependent upon the voltage level and the standards of clearance depends onthe country. For 13.58kV 3 meters clearance is sufficient.