Wooden Platform Bonding

01/28/2016 2:29 AM

Dead tank circuit breaker's control cabinet which is bonded to ground grid is high to reach personal and planing to install a wooden platform on finished grade  (before placing insulating gravel) where personal could stand and work in cabinet. Around platform there would be gravel. Should need to install metal grating on top of wooden platform and bonded to ground grid.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Wooden Platform Bonding

01/28/2016 8:00 AM

Is there a chance of step voltage?

You need to do a risk basement based on local conditions. Conditions we know nothing about.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#2

Re: Wooden Platform Bonding

01/28/2016 12:59 PM

What did yout electrical safety department/responsable said about that?

__________________
The time is ......now
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Wooden Platform Bonding

01/28/2016 1:00 PM

Is the wood going to become live, then? How strange.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4

Re: Wooden Platform Bonding

01/28/2016 2:00 PM

Seems strange. Is this a permanent situation or temporary for maintenance/commissioning?

I take it this is outside in some sort of large factory switchyard (or possibly a substation)?

How big/high is the cabinet?

What country is this in, what standards are you working to?

Why not an all metal structure properly bonded back to earth as would be common for outdoor access structures in switch yards or substations? What do your local standards say regarding structures in this situation?

__________________
jack of all trades
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5

Re: Wooden Platform Bonding

01/28/2016 3:06 PM

This is a Darwin Award in the making.

First you want to work on an energized high voltage circuit breaker,

Second you want to build an elevated wooden platform that will potentially reduce the clearance between the bottom of the energized bushings and your personnel,

Third you want to eliminate the insulating properties of the wood and ensure a really good path to ground for your personnel by making them stand on a grounded metal grid instead of the isolation provided by the wood/crushed stone, and

Forth you're ignoring the fact that Anonymous strangers on the web may not be any more qualified to give advice than you are to implement it, and certainly have no culpability when things go wrong.

Hire a firm that specializes in live equipment maintenance, at a minimum you may prevent a blackout if someone's tool slips or they jumper the wrong contacts, and in the best case you may save someone's life.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Active Contributor

Join Date: Feb 2011
Posts: 13
#6
In reply to #5

Re: Wooden Platform Bonding

01/28/2016 5:45 PM

a

Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#7
In reply to #5

Re: Wooden Platform Bonding

01/28/2016 9:13 PM

Usual practice is an earth mat under the switchyard floor to prevent step voltage. If ever you've see cattle killed by simply approaching a fault the reason becomes obvious. When approaching a switch I was taught to do the shuffle, never place one foot fully in front of the other.
Rather than a wooded platform metal would be preferable.

A dead tank breaker isn't going to have HV in the cubical or anywhere near ground level. You'll probably find a load of mechanical/hydraulic/pneumatic stuff.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#8
In reply to #7

Re: Wooden Platform Bonding

01/29/2016 2:57 AM

The National Electric Safety Code (not to be confused with the NEC) allows the use of safety mats as supplemental protection around live equipment:

Section 124.C.4 Mats...may be used at switchboards, switches, or rotating machinery as supplementary protection.

The clearances to live parts needs to be maintained especially if work is being done on a raised platform:

The distances depend upon a table that considers the phase to phase voltage and the BIL of the system, neither of which has been stated. I've been in 500kV switchyards when switching transients caused flashovers between arcing horns so I'm a bit respectful of the vagaries of high voltages. Distance keeps you alive.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.