Circuit Breaker/Isolator

02/18/2016 12:46 AM

With regards to Mining and Industries-When can a 3 Phase Circuit Breaker be used as an isolator.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Circuit Breaker/Isolator

02/18/2016 1:24 AM

To what end?

As far as I know, it's not something you would get away with under UK M&Q regs. But it's 10 years since I had anything to do with M&Q

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Mar 2011
Location: oz
Posts: 252
Good Answers: 10
#2
In reply to #1

Re: Circuit Breaker/Isolator

02/18/2016 1:33 AM

Oops-missed the main point. This is when isolating the equipment for maintenance works.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4
In reply to #2

Re: Circuit Breaker/Isolator

02/18/2016 7:25 AM

If the circuit breaker can be isolated from the busbars and circuit, IE racked out of the service position and locked, it would be acceptable.

I've worked on many MV systems where this is the only method of isolation.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Circuit Breaker/Isolator

02/18/2016 6:51 AM
  • Only when it is permitted by the electrical codes applicable to the country of installation, and
  • Only when its use in this way is covered by the Authorised Person raising a Permit To Work to cover the maintenance activity.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: Circuit Breaker/Isolator

02/18/2016 3:54 PM

Some circuit breakers are rated for switching duty, meaning they can be manually operated repeatedly. If code permits (and requirements such as sight/distance are met), then it could be allowed. Please consult local authorities.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: Circuit Breaker/Isolator

02/18/2016 7:03 PM

Vacuum circuit breakers, if not provided with a rack-out system (i.e. Metal Enclosed Switch Gear), are NOT considered safe isolation for maintenance purposes. Air circuit breakers are, but hardly anyone uses ACBs on MV equipment any more.

If you are referring to Low Voltage (600V and below), then Molded case Circuit Breakers (MCCBs) are considered safe circuit isolation for service work, as long as they are provided with locking mechanisms.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Dec 2010
Location: North West England
Posts: 1170
Good Answers: 153
#7

Re: Circuit Breaker/Isolator

02/19/2016 4:52 AM

MCBs in particular, if they have a lock out facility fitted, will usually only accept small shackle locks. You need to check that any lock that fits the MCB is also compatible with the safety enforcement standards in place at the mine of factory where you are working. Mines in the UK have regulations on the type of lock that can be used.

Register to Reply
Participant

Join Date: Feb 2016
Posts: 1
#8

Re: Circuit Breaker/Isolator

02/21/2016 9:01 AM

Just wondering why do you want to use a circuit breaker for this???

Regardless of the atmosphere it is installed in you should use a disconnect switch for lock-out of equipment, (much cheaper also).

Depending on what state you are working in the installation codes vary, consult a local lic electrician for this. They would be able to tell you what NEMA rating you would need to satisfy the local inspectors and also to be safe.