Previous in Forum: Location of Snubber or Pulsation Dampener   Next in Forum: Custody Meter - Bi-Directional Prover Loop Recalibration
Flame Detector
02/27/2016 12:42 AM
Dear,
I want to check the orientation for the flame detectors which are installed in my gas plant. Hope without gps device i can't check that. For this purpose which device i need to use?
Thanks.
Re: Flame detector
02/27/2016 1:31 AM
X3301 from Det-tronics, or any of thousands others you can find by searching.
Re: Flame detector
02/27/2016 11:04 AM
you can if sensors are wireless or ethernet connected with corresponding IP set. MIT researchers even plot using electromagnetic field.
Re: Flame detector
02/27/2016 11:22 AM
A magnetic compass, a level, and a protractor.
Good Answers: 125
Re: Flame detector
02/27/2016 2:07 PM
Flame detectors have a cone of vision. The device is most sensitive directly on axis, and becomes less sensitive as you move off axis.
A rule of thumb is 50% sensitivity at 45 degrees off axis.
Therefore, if the detector is placed in a ceiling corner and rotated down and out 45 degrees, the whole plant is covered.
The data sheet for the device will describe effective distance, which varies by the intensity of ultraviolet or infrared radiation the device is designed to detect.
lyn (1); Mr. small (1); Tornado (1); WJMFIRE (1)