Earthing System for HV Sub-Station 132kV

02/28/2016 1:53 PM

Hi friends.

for learning purpose i want to know , what is best earthing system to earth substation bus bars and other equipments CB, CTs and PT installed outdoor, solidly earthed or low-impedance earthed ?

your opinions and comments awaited,

thanks .

Register to Reply
Pathfinder Tags: 132 earthed earthing Power System
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Earthing System for HV Sub-Station 132kv

02/28/2016 2:00 PM

Yes!

Solidly earthed with a very low impedance connection.

Seriously, consult your local codes and regulations!!!!!!!!!

We don't even know where you are. We hope you do and can do proper research instead of asking unknown strangers.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Earthing System for HV Sub-Station 132kv

02/28/2016 4:23 PM

Surely the organisation has a procedure to follow that determines this? Ye gods...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: Earthing System for HV Sub-Station 132kv

02/28/2016 5:44 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#4

Re: Earthing System for HV Sub-Station 132kV

02/28/2016 9:23 PM

I have a love/hate conundrum with these types of questions that makes me uncertain how to answer them. If one fully understood what one actually asked in this type of a question they would understand that not enough information has been provided to answer such a question. On the other hand if one does not understand what they asking. then they are "poking their nose where it doesn't belong" and neither don't deserve nor will likely understand a concise answer. My, personal conundrum comes into play here because I don't believe either extreme case prompted this question. I therefore don't know which is closer to the truth nor how to answer in a useful manor.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5
In reply to #4

Re: Earthing System for HV Sub-Station 132kV

02/28/2016 10:40 PM

What does the type of house have to do with it?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6
In reply to #5

Re: Earthing System for HV Sub-Station 132kV

02/29/2016 12:38 AM

Perhaps knowing that would help one be a more effective tudor?

Register to Reply Score 1 for Off Topic
Power-User

Join Date: Mar 2014
Posts: 204
Good Answers: 3
#8
In reply to #6

Re: Earthing System for HV Sub-Station 132kV

02/29/2016 4:39 AM

A person is not superior in any way just because they have more than one automobile.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14
In reply to #8

Re: Earthing System for HV Sub-Station 132kV

02/29/2016 4:42 PM

<...A person...they have...>

Grammar Alarm - Arrrrrrrooooooooooooooooooooooooooooooooooogah!

Take one ER Penalty Point. Must try harder.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#9
In reply to #6

Re: Earthing System for HV Sub-Station 132kV

02/29/2016 4:39 AM

The only way I know to earth a tudor coupe is with conductive tires.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Hmmm...

Join Date: Jul 2010
Location: Maryland
Posts: 567
Good Answers: 29
#12
In reply to #9

Re: Earthing System for HV Sub-Station 132kV

02/29/2016 12:11 PM

Sounds pretty high class, a tudor coop! Must be some mighty fine chickens.

Register to Reply Off Topic (Score 5)
Power-User

Join Date: Mar 2014
Posts: 204
Good Answers: 3
#13
In reply to #12

Re: Earthing System for HV Sub-Station 132kV

02/29/2016 3:06 PM

classy manor, classy chickens

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#7

Re: Earthing System for HV Sub-Station 132kV

02/29/2016 3:59 AM

First off I'm not your friend

The safest busbars are dead and solidly connected to earth/ground. Unfortunately they don't transfer any useful power.

Explain what you want to know giving some criteria.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Anonymous Poster #1
#10

Re: Earthing System for HV Sub-Station 132kV

02/29/2016 11:17 AM

Ask for training.

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#11

Re: Earthing System for HV Sub-Station 132kV

02/29/2016 11:37 AM

See: NEC [NFPA 70] art. 250;IEEE 142 [Green Book];IEEE 80/2000;IEC 60364-5-54;BS 7430;DIN-VDE 0141;IS 3043;and other.

__________________
Julius
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Feb 2016
Posts: 16
#15

Re: Earthing System for HV Sub-Station 132kV

03/01/2016 10:29 AM

Sorry guys, to much angry peoples out there....

please tell me , i am confused between solidly earthed or low-impedance earthed ?, then which way i ask about that . and what is the requirement or missing data,, ?

Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#17
In reply to #15

Re: Earthing System for HV Sub-Station 132kV

03/13/2016 2:29 PM

Sorry. I think- now- it is about low-voltage systems. So, in my opinion you can see the followings:

Ground Fault Protection for Solidly Grounded LV Systems

http://apps.geindustrial.com/publibrary/checkout/GET-6533A?TNR=Application%20and%20Technical%7CGET-6533A%7CPDF

Resistance Grounding System Basics

http://apps.geindustrial.com/publibrary/checkout/Resistance-Gro?TNR=White%20Papers|Resistance-Gro|generic

Principles of Power System (By V.K. Mehta & Rohit Mehta). chapter 26 Neutral Grounding

http://202.74.245.22:8080/xmlui/bitstream/handle/123456789/112/Ch-26.pdf?sequence=28

__________________
Julius
Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#16

Re: Earthing System for HV Sub-Station 132kV

03/13/2016 12:32 AM

From IEEE-665/1995:

"The purpose of grounding the neutral is threefold: to limit the fault current flow during phase-to-ground faults, to allow for application of protective relaying to detect these faults, and to limit the transient and temporary overvoltages that may be caused by ground faults on the generator system.

Eight methods of grounding are identified by IEEE Std C37.101-1993:

  1. High Resistance Grounded (Distribution-Transformer Grounded)
  2. High Resistance Grounded (Neutral-Resistor Grounded)
  3. Low Resistance Grounded (Neutral-Resistor Grounded)
  4. Low Inductance Grounded (Neutral-Reactor Grounded)
  5. Resonant Grounded (Ground Fault Neutralizer Grounded)
  6. High Resistance Grounding -Transformer Grounded
  7. Medium Resistance Grounding-Transformer Grounded
  8. UngroundedFor each case, the unit arrangement(s) and the reason for using this method will be given. Advantages and disadvantages of each method are presented in IEEE Std C37.101-1993.IEEE Std C62.92-1987 provides means of estimating, by symmetrical component impedance ratios, the transient and temporary overvoltages that may occur on generator systems having various electrical characteristic classes."
__________________
Julius
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#18

Re: Earthing System for HV Sub-Station 132kV

03/14/2016 4:51 AM

As you can see, you cannot treat seriously any answer. Take it as a Facebook thread where merely has to be funny to be appreciate. The colleagues are interested to hear their own voice not yours.

Let's return to your problem.

First of all something is confusing me:

You are speaking about equipment grounding or system grounding?

I am familiar only with 110 to 400 kV European Systems. There the high voltage System is-technically speaking-solid grounded. I think the resistance grounding is very expensive.

The grid manager will calculate the short-circuit current in any point of the grid and will decide if one transformer neutral will be solid grounded or ungrounded. A grounding isolator is provided and a surge protector is connected with the transformer neutral when this will be ungrounded.

If we are speaking about equipment grounding it has to be connected directly to the grounding grid-no resistance inserted.

__________________
Julius
Register to Reply
Register to Reply 18 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: