Generator

05/05/2016 4:23 AM

Hello everyone

My question is that why we turn off capacitor bank while switching on generator.

& i connected capacitor at load side. i dont turn off them hence that load side capacitor will draw extra current. ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: GENERATOR

05/05/2016 4:40 AM

Google says: a lightly loaded system with capacitance connected can cause over-voltage & leading power factor problems.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Generator

05/05/2016 6:45 AM

Surely that is explained in the organisation's Standard Operating Procedure documents?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: May 2016
Location: Ahmedabad
Posts: 21
#3

Re: Generator

05/05/2016 8:06 AM

Once the total load on isolated generator can be subjected to changes with time a capacitor are connected for pf perfection might suddenly causes the total load to become capacitive. Sometimes the total components have an unsafe effect on the capacitors bank. So, it is highly suggested to control this values of the harmonic.

__________________
Control Panels India
Register to Reply
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#4

Re: Generator

05/06/2016 6:28 AM

Every generator has limited capability to operate under leading power factor load which may be governed by its END ZONE HEATING limits and / or margin on stability. (load angle approaches 90 degree).

If you do not turn off the capacitor bank, the resultant power factor as seen by the generator will depend on amount of load and its power factor.

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#5

Re: Generator

05/06/2016 10:25 AM

I'm thinking that what is happening is due to the voltage regulator cross current compensation.

When a generator is paralleled onto a bus, if the generator voltage is not set equal to the bus voltage, reactive current will flow between the generator and the bus. This reactive current is sensed by the cross current compensation circuit in the voltage regulator which corrects the voltage setting.

The reactive current caused by the capacitor bank would give the same indication to the cross current compensation circuit as an incorrect voltage setting and cause an improper voltage adjustment.

http://esrdc.mit.edu/library/ESRDC_library/VR_parallel.pdf

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#6

Re: Generator

05/07/2016 2:17 AM

Dear Mr.ashitoshchougle,

If the Capacitor BANK is on Line, (while starting the Generator, there will be NO-LOAD on the Generator) the capacitor will be working as load and it will result in HIGHER TERMINAL VOLTAGE and the Power Factor will be LEADING P.F. Pl. refer a Standard Electrical Technology Book for the related VECTOR DIAGRAM.

The higher terminal voltage will cause damage to the equipement. Hence the capacitor bank should not be switched on before loading the Generator, and as when the P.F is to be improved, the capacitor bank should come on-line.

DHAYANANDHAN.S

Register to Reply
Active Contributor

Join Date: May 2016
Location: Ahmedabad
Posts: 21
#7

Re: Generator

05/10/2016 7:41 AM

In some older switchboards there used to be a Hand-Off-Auto switch for power factor correction, problems could arise (did) in one case that I investigated of the switch left on hand. Was concluded this damaged the generator diodes when the stand-by generator started.

__________________
Control Panels India
Register to Reply