Safe Distance Between Gas Pipelines

05/05/2016 7:17 AM

Please let me know the safe distance between gas pipelines and it will be good if there exists a code recommendation. Like, I have checked B31.8, where it says that 6 inches (150 mm) shall be the min. distance between two pipelines

Register to Reply
Pathfinder Tags: Safe distance Gas Pipelines
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Safe distance between gas pipelines

05/05/2016 7:42 AM
  • What gas(es) - re-entry plasma, methane, oxygen, xenon, compressed air?
  • Why are there two pipelines when one would do?
  • Where is the Process Engineer's design in all this?
  • Has the design been through a HazOp study?
  • Pressures?
  • Temperatures?
  • Flowrates?
  • Sizes?
  • Materials of construction?
  • Method of joining?
  • Insulation requirements?
  • Insolation?
  • Etc.

If they are too close together then it may be simply impossible to assemble and disassemble them.

So do help the forum to provide concise answers by providing all the information it needs to gain an accurate insight into the problem.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#2

Re: Safe distance between gas pipelines

05/05/2016 7:53 AM

It will be dependent on how you define the safety. What criteria do you have to include in your assessment? Accidental or arbitrary damage? Process safety? Local access options to attend to damaged pipes? Pipe laying constrains?

I believe that only you can answer that question.

__________________
Common Sense Dictates
Register to Reply
Member

Join Date: May 2016
Posts: 6
#4
In reply to #2

Re: Safe distance between gas pipelines

05/05/2016 11:42 AM

These are natural gas pipelines for Fertilizer plant. I think you all know about the process of manufacturing Fertilizer. That is not important. We have two existing natural gas pipelines of sizes 16 inches and 20 inches. Now we are laying another pipeline of size 24 inches in the same right of way. Design temperature is 80 deg. C and pressure is 53 kg/cm2g. Now I need to know the horizontal inter distance as per code. And I m Section Project Engineering (by the way).

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: Safe distance between gas pipelines

05/05/2016 11:57 AM
  • Laying a single 36in main and removing the undersized ones will obviate the problem.

How close are the undersized ones?

Please explain how the forum is able to come to the rescue, free of charge, of this project when so many questions remain unanswered?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#12
In reply to #5

Re: Safe distance between gas pipelines

05/05/2016 2:17 PM

A 26-inch pipe would more than suffice, if that strategy is adopted.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#13
In reply to #4

Re: Safe distance between gas pipelines

05/05/2016 2:31 PM

I'm a policeman. Why do you think that all of me knows about fertiliser plants?

Absolute nonsense.

__________________
Good moaning!
Register to Reply
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#21
In reply to #4

Re: Safe distance between gas pipelines

05/05/2016 11:41 PM

Make it the same!

__________________
Common Sense Dictates
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Safe distance between gas pipelines

05/05/2016 9:26 AM

The piping or process engineer would know.

Horizontal distance?

Vertical distance?

Parallel?

Perpendicular?

Above ground?

Buried?

There is soooooo much you haven't told the forum.

Are you the ditch digger or the hanger?

Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#6

Re: Safe Distance Between Gas Pipelines

05/05/2016 1:34 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Member

Join Date: May 2016
Posts: 6
#7
In reply to #6

Re: Safe Distance Between Gas Pipelines

05/05/2016 1:50 PM

OK thanks But I need same reference from ASME or API code. I agree with your comment of 500 mm but what does the code says?

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#8
In reply to #7

Re: Safe Distance Between Gas Pipelines

05/05/2016 1:57 PM

The appropriate codes are your responsibility!

As "Section Project Engineering" it IS YOUR JOB to have the appropriate codes to hand at all times!

You are a disgrace to your "profession".

Do they not have a professional code of ethics where you are?

Buy the codes yourself!

Register to Reply Score 1 for Good Answer
Member

Join Date: May 2016
Posts: 6
#9
In reply to #8

Re: Safe Distance Between Gas Pipelines

05/05/2016 1:59 PM

CR4 ADMIN: Deleted Post

Vulgar/Rude/Improper Behavior: This post was deleted because it did not adhere to the behavioral policies of the site. Please review Section 14 of the CR4 Site FAQ and the CR4 Rules of Conduct.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#14
In reply to #9

Re: Safe Distance Between Gas Pipelines

05/05/2016 3:21 PM

Apparently, "maza aya" is some kind of Muslim insult.

If you must resort to childish insults, please translate them into a language that the person you are trying to insult will understand.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#15
In reply to #14

Re: Safe Distance Between Gas Pipelines

05/05/2016 4:04 PM

I think it means 'in fun' in Hindi....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#16
In reply to #15

Re: Safe Distance Between Gas Pipelines

05/05/2016 4:50 PM

खुश Cinco डे मेयो

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#17
In reply to #16

Re: Safe Distance Between Gas Pipelines

05/05/2016 5:33 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#18
In reply to #17

Re: Safe Distance Between Gas Pipelines

05/05/2016 6:03 PM

Register to Reply
Member

Join Date: May 2016
Posts: 6
#20
In reply to #14

Re: Safe Distance Between Gas Pipelines

05/05/2016 8:25 PM

Tu Farid Admi Hy

Register to Reply Score 1 for Off Topic
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#10
In reply to #7

Re: Safe Distance Between Gas Pipelines

05/05/2016 2:01 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Member

Join Date: May 2016
Posts: 6
#11
In reply to #10

Re: Safe Distance Between Gas Pipelines

05/05/2016 2:08 PM

Thanks guru

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#19

Re: Safe Distance Between Gas Pipelines

05/05/2016 6:05 PM

The flow capacity of a pipe is proportional to diameter D2.5; for a bunch of pipes, add up their D2.5, and then take the 0.4 power of the sum to get the D of a single-pipe equivalent.

For a 16- and a 20-inch pipe, a 24-inch single pipe will just barely exceed that.

For a 16-, 20-, and 24-inch pipe, a single 32-inch pipe would suffice. (Or use the next standard size up.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#22

Re: Safe Distance Between Gas Pipelines

05/06/2016 5:29 AM

B31.8 sounds good, then. A copy is not available here. One could always check the reasoning behind the standard with the authors; there is a theory that one can reach anyone on the planet by making only 6 telephone calls to locate that individual.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#23

Re: Safe Distance Between Gas Pipelines

05/06/2016 12:19 PM

The closer they are, the easier they are to take out with a single, precision ordinance.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#24
In reply to #23

Re: Safe Distance Between Gas Pipelines

05/06/2016 12:29 PM

An ordinance is a municipal law; military materiel is ordnance.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#25
In reply to #24

Re: Safe Distance Between Gas Pipelines

05/06/2016 12:47 PM

Damn auto-correct.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#26
In reply to #25

Re: Safe Distance Between Gas Pipelines

05/06/2016 12:54 PM

Yeah, I know, gotta watch that. I wonder why the dictionary is so limited.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Off Topic (Score 5)
Associate

Join Date: May 2014
Posts: 30
#27

Re: Safe Distance Between Gas Pipelines

05/10/2016 6:52 AM
Pipe diameter (mm)Duct width x depth (mm)
without meterwith meter
50300 x 200500 x 400
80400 x 300550 x 400
100500 x 400
150600 x 500

CP 51:2004

Register to Reply Score 1 for Off Topic
Register to Reply 27 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Crabtree (1); IdeaSmith (2); lyn (5); nt (1); Osama Nusrat Ali (5); PWSlack (3); redfred (2); SolarEagle (4); Tornado (4)