Different Transformers Voltage

05/23/2016 2:04 PM

Please what will happen in the low voltage side if some difference in voltage line before feeders say one transformer 400v and the other 395 or little less or there is allowable voltage difference voltage? As shown in attach sketch.

Also what is the best connection after transformers in the same bus bar or separate bus bar?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Different transformers voltage

05/23/2016 2:12 PM

There will be circulating currents between the generators, and the voltage on the bus between the generators will be uniform except for minute variation from length and resistance.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Different Transformers Voltage

05/24/2016 3:14 AM

...and in a properly designed and installed system, once the circulation currents rise to intolerable levels, (a) circuit protective device(s) will operate, disconnecting the relevant piece(s) of equipment from the supply and preventing the equipment and its cabling from incurring damage.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Different Transformers Voltage

05/24/2016 5:07 AM

Why do you want to run mismatched transformers in parallel? Beside the probable circulating currents have you considered the maximum prospective fault current on the 400V board?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#4

Re: Different Transformers Voltage

05/24/2016 6:13 AM

draw the circle diagrams and see the result . . . .

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5

Re: Different Transformers Voltage

05/24/2016 7:08 PM

It's much simpler than circle diagrams, it's just the loop impedance with the difference in voltage applied across it. Basically you take the voltage difference (5 volts) and divide by the sum of the transformer impedances (not provided by OP but let's use X=0.1j), then 5.0/0.1j= 50 Amps. It may not seem like a lot until we consider that it gets added to the current in one of the windings, plus the extra losses are I^2 R, and 2,500 times any resistance can be a lot of kWhrs over the course of a year.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#6

Re: Different Transformers Voltage

05/25/2016 4:12 AM

In my opinion, the generators-connected both with the 11 kV Busbar are synchronized-same frequency same voltage []

The problem is on 0.4 kV side and here it could be a difference leading to a circulating current between the two transformers.

IEC 60076-1 Table 1 - Tolerances, it states:

2. Voltage ratio at no load on principal tapping for a specified first pair of windings:

The lower of the following values:

a) ±0,5 % of declared ratio

b) ±1/10 of the actual percentage impedance on the principal tapping.

Let's say we are speaking about 11/0.4 = 27.5 [minimum 0.995, maximum 1.005] = 27.6375 to 27.3625 [11/27.6375 to 11/27.3625=0.39801 to 0.40201 that means maximum 4 V difference is allowable in order not to damage the transformers.