33kV and 415V Cable Separation

05/26/2016 10:32 PM

Hi all, I have a situation where I may use an existing cable trough carrying 33kV trefoil arranged cables, to put a run of 4Cx150 cable for LV supply to a ss building. the 33kv cable is laid in trefoil clamps on the bottom of the trough and the LV cable is clamped to the wall of the trough. The maximum horizontal (angled) distance i can obtain is 385mm between the two different voltage class cables. The parallel run is about 900 meters.

I happened to take some advice and I am told since the MV is screened cable and LV is armoured cable the separation of 300mm is sufficient.

But I am not able to find a standard which states this to be correct.

request your suggestions on this.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: 33kV and 415V cable separation

05/26/2016 11:46 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: 33kV and 415V cable separation

05/26/2016 11:49 PM

It will depend upon where the installation is located and your relationship with the AHJ (Authority Having Jurisdiction). In some cases the AHJ will demand a "suitable barrier" between the two different voltage class cables. As a sidenote I do hope that you've derated the ampacity of both cables to accommodate the expected temperature rise in that confined space, especially if the trough cover is exposed to direct sunlight in a high ambient temperature area and/or poor thermal conductivity soil.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#12
In reply to #2

Re: 33kV and 415V cable separation

05/28/2016 9:36 AM

The ampacity of cable in channel and tunnel it is a very interesting issue, indeed. See-for instance:

From: Power Cables and Their Application, 3rd Edition Part 1 by Lothar Heinhold/Reimer Stubbe (Editors)[Siemens Akt.]

https://books.google.co.il/books/about/Power_cables_and_their_application.html?id=JOBSAAAAMAAJ&redir_esc=y

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#13
In reply to #12

Re: 33kV and 415V cable separation

05/28/2016 9:46 AM

They are many other publications like these:

Power cables in tunnels by Birron M. Weedy

http://ieeexplore.ieee.org/xpl/login.jsp?tp=&arnumber=4075071&url=http%3A%2F%2Fieeexplore.ieee.org%2Fiel5%2F10669%2F4075027%2F04075071.pdf%3Farnumber%3D4075071

TOWARDS A MORE FLEXIBLE RATING METHOD FOR CABLES IN TUNNELS

http://eprints.soton.ac.uk/267553/1/TOWARDS_A_MORE_FLEXIBLE_RATING_METHOD_FOR_CABLES_IN_TUNNELS_final.pdf

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#14
In reply to #13

Re: 33kV and 415V cable separation

05/30/2016 12:26 AM

In my opinion, according to an approximate calculation-if no ventilation is provided and the ambient air-initial-it was 30oC a derating up to 75% of recommended in IEC 60364-5-52 [for low-voltage cable XLPE insulated in free air] and IEC 60502-2 for medium voltage cable.

__________________
Julius
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: 33kV and 415V cable separation

05/27/2016 12:14 AM

What standard are you working to currently as it varies from standard to standard and country to country?

__________________
jack of all trades
Register to Reply
Member

Join Date: May 2015
Posts: 6
#4
In reply to #3

Re: 33kV and 415V cable separation

05/27/2016 1:18 AM

This is for a project in Malaysia. The client has some space constraints and so considering taking both LV and MV together. project adopts IEE and IEC. Thanks.

Register to Reply
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: 33kV and 415V cable separation

05/27/2016 3:13 AM

Standards are, in themselves, not mandatory - they simply advocate best practice; if a standard is followed to the letter then there cannot be any come-back. If there is a Client-based requirement to follow them then so be it, and if need be the trough dimensions would need to be altered or an alternative route found for the LV cable.

However, if a standard cannot be followed to the letter because of Client constraints then it becomes a point for discussion and agreement on the permitted deviation from that standard before work commences. It is a technical discussion, which needs to be recorded, and the record needs to be held by the contracting organisation's Project Manager in case there is any query in the future.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
Member

Join Date: May 2015
Posts: 6
#6
In reply to #5

Re: 33kV and 415V cable separation

05/27/2016 3:42 AM

Thanks for your reply! I completely agree with you, but should not there be a way to find if the separation introduced here cancels out every possibilities of mutual induction even in the case of an fault in mv cable.

I asked many seniors and their comment was they could know it with experience.

Experience matters for sure. But how this practice started because I am not able to find any detail on separation of MV and LV cables that does not mention about physical barriers or to put it in different conduits.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #6

Re: 33kV and 415V cable separation

05/27/2016 4:04 AM

The Client's standards, agreed in the contract, must prevail. However, it may be that this particular instance is not covered by the agreed standards, or it may be that an applicable standard has not been agreed, or it may be that a standard for this application does not exist. Therefore the best course of action is the technical discussion with the Client, as previously suggested, for commercial protection if nothing else.

<unsubscribes>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#8

Re: 33kV and 415V cable separation

05/27/2016 5:42 AM

Given the separation I wouldn't have a problem with the proposal. But once one LV cable is installed the chances are that more will follow, that needs to be kept under control.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#9

Re: 33kV and 415V cable separation

05/27/2016 9:45 AM

I agree with PWSlack.See what U.K. Gov. states:

Specification 034 Electrical Installations prepared by Defence Estates (DE) an agency of the Ministry of Defence [U.K.].

https://www.gov.uk/government/uploads/system/uploads/attachment_data/file/33549/spec34.pdf

TABLE 6A Section Six - Cable Installation MINIMUM SPACING OF CABLES

If we could consider the trough as cable tray:

NEC 2014 art. 392.20 Cable and Conductor Installation.

(B) Cables Rated Over 600 Volts. Cables rated over 600 volts and those rated 600 volts or less installed in the same cable tray shall comply with either of the following:

(1) The cables rated over 600 volts are Type MC.

(2) The cables rated over 600 volts are separated from the cables rated 600 volts or less by a solid fixed barrier of a material compatible with the cable tray.

As one could see, no distance is required if the medium voltage cable is MC type.

__________________
Julius
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#10
In reply to #9

Re: 33kV and 415V cable separation

05/27/2016 3:03 PM

That standard while not stating minimum distance if Type MC rated cables are present, does absolutely mention a solid fixed barrier of compatible material. I read that to mean, no, do not put both (sets of) cables in that tray, do separate voltage classes by having essentially two completely separate trays.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#11
In reply to #10

Re: 33kV and 415V cable separation

05/28/2016 1:00 AM

You are right. Our practice is to segregate the cables as per

IEEE Std 525-1992, IEEE Guide for the Design and Installation of of Cable Systems in Substations

[I have not the 2007 edition with me. However, it seems to me the meaning of sentences remains the same]

4.2 Segregation. 4.2.1 High-voltage power cables

a) Installation of high-voltage cables in raceways that are separated from low-voltage power and control cables and from instrumentation cables. Installation of different voltage classes of high-voltage power cables in separate raceways is also suggested.

b) Utilization of armored shielded cables (separate raceways are still suggested).

However, separate raceways is not compulsory, in my opinion.

One has to test the high voltage cable shield and armor grounding often.

__________________
Julius
Register to Reply
Member

Join Date: May 2015
Posts: 6
#15

Re: 33kV and 415V Cable Separation

05/30/2016 1:54 AM

Thank you very much for the input and support friends.

I was so very unsure of this arrangement and I have proposed to my client to have a separate trough/trench for LV cable and not to take it along with MV cables.

I certainly did not understand why some of my colleagues and seniors told this arrangement is possible. But I preferred to have those cables separately, at least that is what IEE 525 says.

May be, as I was told by my seniors, after quite a while I would come to know things by experience and not by standards, but till then.........

Thank you all for the knowledge shared!

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#16

Re: 33kV and 415V Cable Separation

05/30/2016 8:59 AM

In my opinion, usually, the induced voltage, even in the case of short-circuit phase-to-earth or phase-to-ground-to-phase is low.

The distance-or separation-function it is to avoid fire damage from one to another-usually low voltage is less important, but medium voltage cable presents an elevated hazard of fire [the standard recommends the higher voltage in uppermost level since the fire gets up]. Once, the order was upside-down and I saw 6 stacks of cables bursting in a fire starting from a exploded junction box of a medium voltage cable located on the lowermost tray.

__________________
Julius
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#17
In reply to #16

Re: 33kV and 415V Cable Separation

05/31/2016 8:36 AM

Yes, perhaps induced voltage is low, but can you imagine sensitive instrumentation wire openly in the same tunnel/channel with HV cable, and the HV system trip transient that results inducing a signal in the instrumentation wire that fries all that equipment?

If not fries it, then maybe it just messes up some seriously important data streams.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#18
In reply to #17

Re: 33kV and 415V Cable Separation

05/31/2016 4:57 PM

Actually it's a life and equipment safety issue, the goal being to prevent any connection between the high voltage circuit (via direct contact or during an arcing fault) and the low voltage circuit, plus isolating any ensuing fire spread.

Although equipment protection, signal integrity, overheating, and/or induced voltage, etc. issues are a consideration, those are design constraints usually covered in the engineering specifications documentation. Life safety is usually covered by independent standards; i.e., the AHJ doesn't care if the machine doesn't work properly, he just wants to be sure that nobody will die while using it (properly).

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Register to Reply 18 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (6); anup2mohan (3); jack of all trades (1); James Stewart (2); PWSlack (2); RAMConsult (2); SolarEagle (1); TonyS (1)

Previous in Forum: Can VAN DE GRAAFFF Be Used to Charge Batteries?   Next in Forum: Changing Transformer Primary Winding

Advertisement