Changing Transformer Primary Winding

05/27/2016 12:10 AM

Dear Experts

We have 1600KVA, 6KV/0.525KV, Dry type Transformer laying in our Store, it was being used when we had utility connection of 6KV, now the new utility connection is 11KV. Is it feasible to rewind only Primary Winding of this transformer and convert it to 11KV/0.525KV 1600KVA transformer, What I am looking for is does the transformer core has anything to do with the Voltage level as we are not making any change in core. Any other draw back we will face after this alteration. Will the new Primary voltage (11KV) result in core saturation?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Changing Transformer Primary Winding

05/27/2016 12:31 AM

In a word, no.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Associate

Join Date: May 2016
Posts: 53
#9
In reply to #1

Re: Changing Transformer Primary Winding

05/29/2016 12:07 AM

agree.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Changing Transformer Primary Winding

05/27/2016 3:03 AM

The installation needs a new transformer, and circuit protection equipment, suited to the higher supply voltage - <...experts...> a simple telephone call to the transformer manufacturer, where the expertise lies, would have confirmed that.

The stored transformer may have some residual value on the second-hand equipment market, which can be used to offset the purchase of the replacement.

As the utility cables are likely to need replacement too, it may be worth investigating the replacement of other nearby transformers to see whether some system rationalisation and the displacement of other equipment could add to the purchase value offset. If in doubt consult a qualified Electrical Engineer locally.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Changing Transformer Primary Winding

05/27/2016 5:18 AM

As JR said "no".

Sell the old transformer and use the funds towards the new transformer. There is a good market for 2nd user electrical equipment due to recession.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#4

Re: Changing Transformer Primary Winding

05/27/2016 1:08 PM

Theoretically you could use the actual core if you would keep the same voltage per turn.

But you have to consider the coil dimensions as number of turns increases and the insulation also. You have to stick the new bobbins in the same space. In my opinion if the transformer rated power would be 100-200 kVA it could very difficult. But, it seems to me, for 1600 kVA no major change in overall dimensions will be required.

In any way you have to order the new windings from a special manufacturer-like Siemens, ABB and others.

As TonyS said, may be it will be better to buy a new transformer.

Still, I think, you need a "tailor made" transformer since 525 V rated it is not a standard one, in my opinion.

__________________
Julius
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#5

Re: Changing Transformer Primary Winding

05/27/2016 2:53 PM

NO. Trade the old XFMR in for new rating one, that has already been designed for that service, tested, and quality-controlled seven ways from Sunday.

Never do that.

You would have had to basically gut the thing, and start over with both windings, then you still not be sure the case is sufficiently isolated for safety, much less the requirement for new bushings.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#6

Re: Changing Transformer Primary Winding

05/27/2016 6:49 PM

Yes, you can rewind it for different voltages and no the core is not a concern. It's size and design is only affected by frequency and overall working capacity.

Regardless of your primary to secondary voltage ratios the core is still a 1600KVA unit.

Register to Reply
Power-User

Join Date: Jul 2014
Posts: 113
Good Answers: 4
#7

Re: Changing Transformer Primary Winding

05/27/2016 10:26 PM

After you finish winding the primary, you have to impregnate it. And this you cannot do.

Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#11
In reply to #7

Re: Changing Transformer Primary Winding

05/31/2016 8:25 AM

I have never witnessed a transformer impregnation...I was just wondering about the gestation period...

Final warning: Kids! Do not try this at home! Don't even try this at work!

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#12
In reply to #11

Re: Changing Transformer Primary Winding

05/31/2016 9:09 AM

In the 60's while involved in transformer mfg, the transformers after coming off the winder section, they are oven-dried before being soaked into tubs filled with liquid electrical insulating varnish... They're left soaking, immersed until all air occupied spaces has been completely eliminated.. with no more air bubbles observed after certain elapsed time...

At this point they are considered to be already impregnated!

__________________
vsar
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#13
In reply to #12

Re: Changing Transformer Primary Winding

05/31/2016 10:34 AM

But, but, but....when do the little baby transformers come out?

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#14
In reply to #13

Re: Changing Transformer Primary Winding

05/31/2016 3:49 PM

Over certain period of time after expelling any trapped air ...like burping babies! they'll be more comfy, when bubbling stops....

__________________
vsar
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#15
In reply to #14

Re: Changing Transformer Primary Winding

05/31/2016 4:00 PM

Yes sir, that's your baby! No sir, I don't mean maybe! Yes sir, that's your baby now!

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#16
In reply to #15

Re: Changing Transformer Primary Winding

05/31/2016 4:10 PM

Love that too!! �� ����

__________________
vsar
Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#8

Re: Changing Transformer Primary Winding

05/28/2016 7:13 AM

Theoretically YES since the voltage desired is about double of the original, while the corresponding AWG size of the copper magnet wire will be smaller to maintain the KVA rated capacity of the device!

The BH characteristics of the core ued is another factor that needs considerations, since efficiency of the device may be affected...in the power conversion processes! It is one of the main factor in determining the proper turn per volt ratio in the design of that device!

Similar to the earlier advice given, it is NOT advisable to rewind! Given that you have to asked this question, led me to believe that you do not have or lacked the expertise needed to safely implement your plan!

__________________
vsar
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#10

Re: Changing Transformer Primary Winding

05/29/2016 3:49 PM

Possibly, but may introduce many possible problems (such as clearances, de-rating, etc).

Talk with a professional transformer rewinding company as they should be of help and hopefully advise if it is possible or not in your particular application. It may not even be economically viable compared to purchasing a new transformer.

Do NOT attempt this by yourself or let someone who isn't properly trained rewind the transformer.

__________________
jack of all trades
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#17

Re: Changing Transformer Primary Winding

06/10/2016 6:27 AM

A possible cheaper and quicker to fiinalise alternative would be to add an aproximately 2:1 step down transformer, up front, to bring the higher voltage down to the requirements of the original transformer....

Never touch a running machine!

What say the experts here?

__________________
"What others say about you reveals more about them, than it does you." Anon.