Hello everyone, I work with a power transmission company. The p.u impedance of the power transformers on the system is between 9.0 and 14%. What is normally considered when determining the PU impedance of a transformer to be installed on a system? Regards
Re: Power Transformers
05/30/2016 4:18 PM
""The percentage impedance of a transformer is the voltage drop on full load due to the winding resistance and leakage reactance expressed as a percentage of the rated voltage."
"It is also the percentage of the normal terminal voltage at one side required to circulate full-load current under short circuit conditions on other side." The impedance of a transformer has a major effect on system fault levels. It determines the maximum value of current that will flow under fault conditions.It is easy to calculate the maximum current that a transformer can deliver under symmetrical fault conditions.
By way of example, consider a 2 MVA transformer with an impedance of 5%. The maximum fault level available on the secondary side is: 2 MVA x 100/5 = 40 MVA and from this figure, the equivalent primary and secondary fault currents can be calculated.
A transformer with a lower impedance will lead to a higher fault level (and vice versa).
The figure calculated above is a maximum. In practice, the actual fault level will be reduced by the source impedance, the impedance of cables and overhead lines between the transformer and the fault, and the fault impedance itself."
https://www.quora.com/Why-is-the-transformer-impedance-given-in-percentage
The operating parameters of a transformer must be known to determine the ability to handle the load and where to set safety device settings...
Good Answers: 445
05/30/2016 7:35 PM
There are many power system studies that go into choosing the appropriate impedance for a transmission transformer. There are regulatory, operational, steady-state, dynamic, and transient considerations that are necessary to ensure the safe and reliable performance of the grid; the transformer's parameters must meet all of them.
In no particular order of importance: load-flow, transient/dynamic stability, voltage drop/profile, BIL, short-circuit, fault contingency, overload capacity/capability, system security, protective relaying, regulatory/grid codes, etc., etc. There are many others, it is definitely not a random choice.
Good Answers: 42
06/01/2016 2:41 AM
In my opinion, what you defined as p.u. it has to be short-circuit rated voltage[uk% IEC standard] or Zk% [IEEE standard] .This series of values could be for medium voltage [6 to 35 kV] and high voltage 110-220 KV transformer primary voltage.
P.u. it is referred to a base apparent power usually [Sbase]10 KVA up to 100 MVA and a voltage base[VLLbase]-usually
the System [or transformer] rated voltage.
Zbase=VLLbase^2/Sbase the base impedance in ohm
Let's say you have a 110 KV 40 MVA transformer 10% zk%. Actually, the short-circuit impedance of the transformer will be:
Zxfr=110^2/40*10/100=30.25 ohm
Let's say Sbase=100 MVA and VLLbase=110 KV Zbase=110^2/100=121 ohm.
Zp.u.=30.25/121=0.25
Julius
06/01/2016 4:44 PM
Z (p.u.) - doesn't that stand for power utilization impedance at maximum load? I don't know, but I am here to learn.
Good Answers: 445
06/01/2016 9:38 PM
Not quite. Per Unit (pu) is a scaling system that makes it easier for power engineers to perform calculations despite differences in the relative ratings of the equipment, especially transformers because of the transformation ratio.
A complete introduction to the per unit system is more cut and paste than the CR4 editor system can handle, but there are plenty of tutorials on the web.
06/02/2016 9:48 AM
Thanks for foreword to the introduction.