We have storage calorifier ( electric tubular immersion heater - indirect type installed in 2000L water tank.) Used for water heating on ship. This provides hot water to people staying on ships & for utilities. Total heater capacity is 90 kw(440V) built with group of tube bundles - 13 nos each @ 7kw. They are arranged in 3 groups ( 35kw, 28kw & 28kw). While commissioning on site we noticed Insulation resistance is between 0Mega Ohm to 0.1Mega ohm. We are trying to improve the the IR value by supplying 24V dc supply through the coil. So far it has improved upto 0.1Mohm. With this the manufacturer has advised to go ahead with starting. Heater is running with normal current of 35Amps.( group of heaters -4 nos 28kw). The heaters are being started after 3 months of storage on site.
These coils are nichrome element inside incolloy sheathing with magnesium oxide powder(MGO) as electric insulator ( and conductor of heat). 1)Is it normal to have such low values of insulation. 2) Have seen info on internet with brands like Hubble heaters - they do confirm IR value some time can be very low & becomes issue for commissioning as end user is reluctant to power up with such low IR.
Anant