Electric Heaters Insulation Resistance

06/03/2016 11:53 AM

We have storage calorifier ( electric tubular immersion heater - indirect type installed in 2000L water tank.) Used for water heating on ship. This provides hot water to people staying on ships & for utilities. Total heater capacity is 90 kw(440V) built with group of tube bundles - 13 nos each @ 7kw. They are arranged in 3 groups ( 35kw, 28kw & 28kw). While commissioning on site we noticed Insulation resistance is between 0Mega Ohm to 0.1Mega ohm. We are trying to improve the the IR value by supplying 24V dc supply through the coil. So far it has improved upto 0.1Mohm. With this the manufacturer has advised to go ahead with starting. Heater is running with normal current of 35Amps.( group of heaters -4 nos 28kw). The heaters are being started after 3 months of storage on site.

These coils are nichrome element inside incolloy sheathing with magnesium oxide powder(MGO) as electric insulator ( and conductor of heat). 1)Is it normal to have such low values of insulation. 2) Have seen info on internet with brands like Hubble heaters - they do confirm IR value some time can be very low & becomes issue for commissioning as end user is reluctant to power up with such low IR.

Anant

Register to Reply
Pathfinder Tags: CALORIFIER
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Electric Heaters Insulation Resistance

06/03/2016 12:43 PM

I would call that unacceptably low.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Electric Heaters Insulation Resistance

06/03/2016 1:00 PM

I would run it for a while then recheck....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3

Re: Electric Heaters Insulation Resistance

06/03/2016 1:13 PM

From a manufacturer's instructions:

"...The refractory material used in heating elements may absorb some moisture during transit, periods of storage, or when subjected to a humid environment. This moisture absorption results in a cold insulation resistance of less than twenty (20) megohms. If this heater has been subjected to the above condition, each heating element must be checked for insulation resistance before energizing. A low megohm condition can be corrected by removing the terminal hardware and baking the element in an oven at 350°F -700°F for several hours or until the proper megohm reading is obtained..." There's more info if you read through the whole thing.

I don't know how large your vessel is, but most marine electrical systems are ungrounded to minimize corrosion/electrolysis problems (the vessel is the earthing conductor, not the neutral/return conductor). If this is the case then the there shouldn't be too much current flow from the elements to the sheath; however, IF (notice that it's a big "if") there's a fault anywhere else you could have problems. Proceed at your own risk and peril.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#4

Re: Electric Heaters Insulation Resistance

06/03/2016 1:15 PM

I'd ask the manufacturer to put his hand on the heater wall or pipe when you power it up.

Register to Reply
Member

Join Date: Jun 2016
Posts: 5
#5

Re: Electric Heaters Insulation Resistance

06/03/2016 9:56 PM

Ramconsult

Thanks for comments. We have powered up 2 heaters & warming up 3rd with low volt dc supply to improve insulation. Have overcurrent protection which should trip. You are right there is no earth leakage at the moment - & may be risky with 2nd fault. Will monitor while running & see if there is improvement. Anyway it is uncomfortable situation. Like to state the manufacturer here is Sandvik with their Kanthal range of heaters.

Anant

Register to Reply
Member

Join Date: Jun 2016
Posts: 5
#6

Re: Electric Heaters Insulation Resistance

06/04/2016 11:20 AM

We did lamp heating at terminal box of heater. For two heaters the IR improved from 0.1Mohm to 0.6 Mohm. third heater it is 0.12 Mega ohm. Since there was good improvement with lamp heating( 20 mins) I understand the moisture is usually at the terminal end. This is the reason probably we had slow improvement with dc current injection into coils. For immersion heaters this MGO powder being hygroscopic is an issue. Will do final check on monday. Hope to recover to min 10Megaohm.

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#8
In reply to #6

Re: Electric Heaters Insulation Resistance

06/06/2016 3:54 PM

Consider ensuring the ends are unsealed (if possible) to allow the moisture somewhere to escape during heating. Also if the humidity is high or room temperature fluctuates consider adding heaters to heat the surrounding air to speed up the drying out process.

Unfortunately there is really no quick way to dry these elements out, so take your time before powering up with full supply voltage.

__________________
jack of all trades
Register to Reply
Member

Join Date: Jun 2016
Posts: 7
Good Answers: 1
#7

Re: Electric Heaters Insulation Resistance

06/05/2016 2:30 AM

If you connect a heater of 0.1 Mohm earth resistance then current drawn to earth will be Iph/R i.e. 250/100000=0.0025A i.e. 2.5 mA which is a very safe amount. You can use the heater with a ROCB/ELCB of 30 mA leakage current very safely.

Register to Reply
Member

Join Date: Jun 2016
Posts: 5
#9

Re: Electric Heaters Insulation Resistance

06/21/2016 11:11 AM

Hi all,

Would like to provide further feedback. After 2 weeks of running the IR value improved between 1.7mohm to 7 Mohm. We have 3 heaters whose starting sequence is based on load. Since at present the load is not much heaters run 2 hrs per day.

However have noticed running heaters record low IR value while standby heaters have higher value. If the starting sequence is changed the heater 1st in line records low IR ( 0.7Mohm) while standby heaters ( 3-4 mohm).

We have checked individual heating element IR value & it varies between 0.5Mohm to 27mohm. ( FYI as stated in 1st post the elements are grouped in delta together to form 3 heater groups of 35 kw, 27.5kw, 27.5kw respectively.

Does above means the heater has manufacturing defect - seals are not good allowing the heater(MGO powder) to breath moisture ?

Appreciate your feedback & comments. Some of the dealers of watlow informed me this is common problem in Singapore & there could also be manufacturing defect.

Unfortunately Manufacturer - Sandvik india has not been supportive & I had to take this to their M.Director today.

Really frustrating as my client says they will not accept heater unless the IR value is 10Mohm atleast.

Thanks in advance

Anant

Register to Reply
Member

Join Date: Jun 2016
Posts: 5
#10

Re: Electric Heaters Insulation Resistance

06/25/2016 10:46 AM

Hi all,

Would like to provide further feedback. After 2 weeks of running the IR value improved between 1.7mohm to 7 Mohm. We have 3 heaters whose starting sequence is based on load. Since at present the load is not much heaters run 2 hrs per day.

However have noticed running heaters record low IR value while standby heaters have higher value. If the starting sequence is changed the heater 1st in line records low IR ( 0.7Mohm) while standby heaters ( 3-4 mohm).

We have checked individual heating element IR value & it varies between 0.5Mohm to 27mohm. ( FYI as stated in 1st post the elements are grouped in delta together to form 3 heater groups of 35 kw, 27.5kw, 27.5kw respectively.

Does above means the heater has manufacturing defect - seals are not good allowing the heater(MGO powder) to breath moisture ?

Appreciate your feedback & comments. Some of the dealers of watlow informed me this is common problem in Singapore & there could also be manufacturing defect.

Unfortunately Manufacturer - Sandvik india has not been supportive & I had to take this to their M.Director today.

Really frustrating as my client says they will not accept heater unless the IR value is 10Mohm atleast.

Thanks in advance

Anant

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#11
In reply to #10

Re: Electric Heaters Insulation Resistance

06/26/2016 3:24 PM

Perhaps there is still moisture sealed in the heater. Try unsealing the ends and running it (along with perhaps dehumidifiers in a sealed room to control air moisture levels) to allow moisture to evaporate out then seal the ends up to prevent moisture being absorbed back in when the heater is off.

If it is anything more perhaps it is a manufacturing defect.

__________________
jack of all trades
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14
In reply to #10

Re: Electric Heaters Insulation Resistance

08/22/2024 5:50 AM

<...Unfortunately Manufacturer...has not been supportive & I had to take this to their M.Director today....>

Exactly the right course of action.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Jan 2017
Posts: 1
#12

Re: Electric Heaters Insulation Resistance

01/08/2017 10:51 AM

Hello Mr.anant

I hope the ussue is resolved by now. If not then . Pls follow this process and you need to have a oven big enough to fit that 90 kw flange heater inside a oven

Mostly your heater size would have been 400 NB ANSI flange with length of the ehater around 1200mm

Soyou will beed a 1.2 meter oven

1. Remove all the terminals nuts of the heater elements ... Mostly this is M4 nuts from terminals

2. Remove the ceramic bush

3. Remove any rtv sealent if it provides and completely cleane it with a pointer and blow compressed air to remove and clear it from any forigh materials. You should see white mgo crust

4. Keep/ place the heater standing position facing the terminals upwards. if possible of other wise horizontal position will also do.

5. In this position place it inside the oven and heate the complete bundle upto 400 deg.C

And maintain it for 2 hours atleast

6. Remove it from oven . If you check the IR value now you will see lower megger values. But as the tube cools down this vales will imporove greately

However dont wait for the heater to cool down as the mgo which is very highly hygroscopic materilal will absorb atmospheric moisture. So when you remove it from the oven. At that temperature with gloves on hands . Do the RTV silicon sealing. We do different kind of sealing as we are manufacturers and have facility . But in site this is whatyou could getbthe best .. a RTV silicon sealing 280deg C grade and sealing should be done properly and see after sealing you reinstall those ceramic bushes on the tube ends

And fasten a small nut tightly. While doing so. You will see som red RTV puffs out on edge of bush and tube.. let it be like that..

Once the heater bundle cools down ... you can check the IR valelues to be improved for sure. And if the process is done correctly

can provide you further assistance if required

Let me know.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13

Re: Electric Heaters Insulation Resistance

03/12/2024 10:52 AM

A1) <...normal...> is irrelevant. Acceptability must be the criterion. The acceptability boundary may be found in local electrical codes.

A2) Open a dialogue with <...Hubble heaters...>. Telephone?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 14 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

anant64 (4); bhaben66 (1); Brave Sir Robin (1); jack of all trades (2); PWSlack (2); RAMConsult (1); satishdave (1); SolarEagle (1); Tornado (1)

Previous in Forum: Adding Temp Control to a Lab Stirrer/Hot Plate   Next in Forum: Generator Reverse Power

Advertisement