Generator Reverse Power

06/04/2016 10:59 AM

100MW Generator, having static excitation system, got tripped on reverse power protection, while excitation switched ON and voltage building to rated voltage, Prior to synchronization to grid. Can any one share possible causes of reverse power with this condition

Register to Reply
Pathfinder Tags: reverse power
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Generator reverse power

06/04/2016 5:04 PM

Something is backwards.

Look on page 231.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: Generator reverse power

06/04/2016 7:15 PM

I think you already have your answer. "Prior to synchronization to grid."

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5
In reply to #2

Re: Generator reverse power

06/04/2016 9:31 PM

That's the puzzle rather than the answer.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#10
In reply to #5

Re: Generator reverse power

06/05/2016 7:41 AM

The puzzle is why the generator was connected to the grid prior to synchronization?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#11
In reply to #10

Re: Generator reverse power

06/05/2016 8:17 AM

It didn't read to me that it had been connected to the grid yet, but that might be an interpretation.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#3

Re: Generator reverse power

06/04/2016 8:13 PM

Has some maintenance just been performed on this generator? If yes, then that is where you should start looking for your problem.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4

Re: Generator reverse power

06/04/2016 8:57 PM

Perhaps, after you share with us exactly what was going on; things like the rating and type of the unit, how it was being synchronized, buttons pushed, the type of protective relaying and flags dropped, what "prior to synchronization" means exactly, etc., etc.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#6

Re: Generator reverse power

06/04/2016 11:20 PM

LINK

try this for an answer.....

__________________
The square root of nothing is what you make it!
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#7

Re: Generator reverse power

06/04/2016 11:26 PM

Sounds like you have something wired backwards....or start-up sequence wrong....when was the last time maintenance was performed on the static exciter system? These static exciter systems are high maintenance...

http://control.com/thread/1232026413

http://hydropower.ornl.gov/docs/HAP/ElecExciterBestPractice.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Member

Join Date: Jun 2016
Posts: 7
Good Answers: 1
#8

Re: Generator reverse power

06/05/2016 2:08 AM

Reverse power occures due to frequency mismatch of your system with grid. Frequecy of your system depends on fuel supply to your engine. The reverse power only can occure due to problem in your fuel system. Fuel system problem may be from choaked filter/strainer, Fuel control valve and related fuel control system or insufficient fuel supply.

Register to Reply Score 2 for Off Topic
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#9

Re: Generator reverse power

06/05/2016 7:03 AM

Right..

It would seem that the link I placed in an earlier reply has not been looked at, so to quote from that link

"Reverse power generally describes a condition where the prime mover of a generator is not supplying sufficient torque to keep the generator rotor spinning at the same frequency as the grid to which the generator is connected. In other words, the generator has actually become a motor and is drawing current from the grid to which is connected and is supplying torque to the prime mover which is supposed to be supplying torque to the generator.

During synchronization, it might be possible to have the synchroscope rotating in the Slow direction (anti-clockwise) and then close the breaker. Under this condition, the generator would then be drawing a small amount of current from the grid instead of supplying a small amount of current to the grid (which occurs when the breaker is closed with the synchroscope rotates in the Fast (clockwise) direction).

I have seen some prime mover control systems (and exciter regulator control systems and synchronizers) that try to increase load slightly as soon as the generator breaker is closed. On a couple of sites, after a maintenance outage, I have seen the output of the control mis-connected to the control valve and cause the load to actually decrease instead of increase and cause the generator to trip on reverse power. One case was a paper mill that had a DC motor on the steam control valve actuator and the motor leads were reversed."

__________________
The square root of nothing is what you make it!
Register to Reply
Member

Join Date: Jun 2016
Posts: 7
Good Answers: 1
#12
In reply to #9

Re: Generator reverse power

06/05/2016 9:32 AM

If you are asking reverse power during synchronization then it normally happens when synchroscope needle is moving from negative direction and crossing zero and you closed the breaker. Always do the synchronization in positive direction by looking the trends of the needle movement.

Register to Reply
Participant

Join Date: Jun 2016
Posts: 2
#13

Re: Generator reverse power

06/05/2016 10:36 AM

Dear All

few more details are here

1) "Prior to synchronization" means the generator did not connected to grid, and the generator is getting tripped on reverse power before synchronization to grid

2) The generator is getting tripped on reverse power while terminal voltage reaching to rated 15KV from 0KV

3) There is no issues from prime mover side and fuel

4) ABB make REG 316 is the protection relay

5) Generator & AVR make: SIEMENS

6) Reverse power setting is -2.6MW, 2sec, as per events list the relay got operated at -5.2MW for first time and -4.0MW at second time

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#14
In reply to #13

Re: Generator reverse power

06/05/2016 11:15 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Member

Join Date: Jun 2016
Posts: 7
Good Answers: 1
#15
In reply to #13

Re: Generator reverse power

06/05/2016 1:04 PM

Reverse power can not occur before synchronization------ basic of electrical engineering.

Your REG 316 is malfunctioning. Try to switch of the power for few seconds and switched it on, check for its function, if ok no problem , otherwise call vendor for reprogram or replacement.

Register to Reply
Active Contributor

Join Date: Jun 2015
Posts: 15
#17
In reply to #13

Re: Generator reverse power

06/06/2016 1:28 PM

Sounds like protection relay is not configured correctly or operating correctly. Reverse power should only occur when connected to another source.

Register to Reply
Participant

Join Date: Jun 2016
Posts: 3
Good Answers: 1
#19
In reply to #13

Re: Generator reverse power

06/17/2016 5:03 AM

please check your MW transducer, it should be giving 0 MW before synchronizing to grid.

Register to Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#16

Re: Generator Reverse Power

06/06/2016 10:10 AM

Alex, I'd like Generators for $800 please.

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#18

Re: Generator Reverse Power

06/06/2016 2:04 PM

If your generator protection is tripping on reverse power with the generator not yet synchronized / connected to the bus, then you could have one or more of several problems:

1. The relay is wired to the CT and/or VT inputs imcorrectly. It would help if you could post a schematic of the relay connections to the instrument transformers and generator bus. Where are the CTs and are they of proper ratio, phasing, and polarity? Same with VTs?

2. The relay is programmed incorrectly. Is this reverse power setting correct, per the device coordination study?

3. The relay is operating incorrectly, and sensing something it shouldn't. Was the relay bench tested to verify that it operates at the proper setpoints for appropriate voltage and current inputs?

A consideration ifor the ABB REG316 (or other numerical, multifunction relay) is when should a particular function be enabled. I would suggest that the reverse power function should be disabled while the generator is not yet synced to the bus, because that function is not relevant yet. Reverse power protection is actually only relevant when the generator is connected to the bus. Other protection functions are used to protect the gen wirings before this point. In looking at schematics for older style, electromechanical reverse power relays (such as the GE ICW51), they usually put a Normally Open contact (52a) of the generator circuit breaker in series with the relay's reverse power trip output, so that the trip could only operate after the breaker is closed and the generator synced to the bus.

__________________
To get the right answers, first you need to ask the right questions.